Hi all,

Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation.

We've been putting in a new kitchen into an apartment over the last couple of weeks and had a bit of a nightmare with the electrician. The firm is well rated and the guy we initially spoke to about the estimate (the owner I believe) was very knowledgeable but they seem to have quite a few sparks working for them and the straw we drew was pretty short. This specific question is about the light fitting and (lack of) installation, though it was by far the only thing we've had issues with...

The flat was built in the late 1960s and has concrete ceilings and walls made of pure obsidian, so when a rewire was done about 15 years ago (by the local council) it was all trunking and surface mount accessories. The light fitting is a powder coated metal four bar spotlight with the trunking running to it; ugly but not a lot that can be done without installing a suspended ceiling.

The electrician attempted to put the fitting up, running into obstacles at basically every point.
  • After the first fix, turning on the (old) kitchen light would trip the MCB immediately. He fixed it the next morning, explaining that it was "just" a loose cable in the (exposed) knockout box.
  • Instead of installing a junction box at the top of the trunking and running a single cable to the fitting, he ran four cables, needing a very large notch out of the side of the fitting (the notch is fine, we knew the fitting would have to be modified and we can cover it). Judging by the cleanness of the edges, he cut this notch using a hammer. He also notched it in a weird position, meaning that the fitting is about a metre off centre in the room.
  • He bundled the conductors into Wagos but had 3 lives and 4 neutrals each using a single 2 way connector. One of the neutrals pulled out when I just moved the wires.
  • The fitting is sold as Class II, he cut off the connector block inside (though I know people hate these), which I assume makes it Class I and requiring a CPC? There's no earth connector in the fitting and the whole thing is powder coated inside and out so it will be difficult to earth. Also, would Wagos bundled up inside the Class II fitting actually make it Class I anyway even if he hadn't cut that off?
  • When he cut off the connecting box, he mangled the cables. If I didn't know what happened I would assume the insulation and conductors had been chewed by a rat.
  • There was no grommet or protection over the metal cutout. I know this is required for knockout boxes/consumer units, but not sure about stuff like light fitting?
  • He was completely unable to fit the lights. We tried explaining to him that he probably needed to space the mounting plate a bit off the ceiling to give a bit of wiggle room for the fitting to slide over (1960s artexed ceilings with decades of previous light fittings are not known for being euclidean planes) but he explained that that would not help.
He gave up after two and a half hours of standing on his tiptoes and swearing and said it couldn't be fitted but he'd fit a different one for us if we bought one, which was good of him. I've put the fitting up by spacing it from the ceiling a bit, extending the conductors with some inline Wagos and the wires from some 2.5mm flex, and switching out the 2-way connectors for more appropriate ones.

The guy is supposed to be coming back at some point to certify the work, we're going to ask for someone else from the firm to do it (preferably the owner we spoke to before). How much of the above is an actual issue we should highlight when the work is certified and how much is me just being a picky sod?

Thanks!
 
TL;DR
Electrician completely bodged light fitting install (among other things), what should I complain about when this is certified and what should I just get my therapist to help me move on from?
Hi all,

Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation.

We've been putting in a new kitchen into an apartment over the last couple of weeks and had a bit of a nightmare with the electrician. The firm is well rated and the guy we initially spoke to about the estimate (the owner I believe) was very knowledgeable but they seem to have quite a few sparks working for them and the straw we drew was pretty short. This specific question is about the light fitting and (lack of) installation, though it was by far the only thing we've had issues with...

The flat was built in the late 1960s and has concrete ceilings and walls made of pure obsidian, so when a rewire was done about 15 years ago (by the local council) it was all trunking and surface mount accessories. The light fitting is a powder coated metal four bar spotlight with the trunking running to it; ugly but not a lot that can be done without installing a suspended ceiling.

The electrician attempted to put the fitting up, running into obstacles at basically every point.
  • After the first fix, turning on the (old) kitchen light would trip the MCB immediately. He fixed it the next morning, explaining that it was "just" a loose cable in the (exposed) knockout box.
  • Instead of installing a junction box at the top of the trunking and running a single cable to the fitting, he ran four cables, needing a very large notch out of the side of the fitting (the notch is fine, we knew the fitting would have to be modified and we can cover it). Judging by the cleanness of the edges, he cut this notch using a hammer. He also notched it in a weird position, meaning that the fitting is about a metre off centre in the room.
  • He bundled the conductors into Wagos but had 3 lives and 4 neutrals each using a single 2 way connector. One of the neutrals pulled out when I just moved the wires.
  • The fitting is sold as Class II, he cut off the connector block inside (though I know people hate these), which I assume makes it Class I and requiring a CPC? There's no earth connector in the fitting and the whole thing is powder coated inside and out so it will be difficult to earth. Also, would Wagos bundled up inside the Class II fitting actually make it Class I anyway even if he hadn't cut that off?
  • When he cut off the connecting box, he mangled the cables. If I didn't know what happened I would assume the insulation and conductors had been chewed by a rat.
  • There was no grommet or protection over the metal cutout. I know this is required for knockout boxes/consumer units, but not sure about stuff like light fitting?
  • He was completely unable to fit the lights. We tried explaining to him that he probably needed to space the mounting plate a bit off the ceiling to give a bit of wiggle room for the fitting to slide over (1960s artexed ceilings with decades of previous light fittings are not known for being euclidean planes) but he explained that that would not help.
He gave up after two and a half hours of standing on his tiptoes and swearing and said it couldn't be fitted but he'd fit a different one for us if we bought one, which was good of him. I've put the fitting up by spacing it from the ceiling a bit, extending the conductors with some inline Wagos and the wires from some 2.5mm flex, and switching out the 2-way connectors for more appropriate ones.

The guy is supposed to be coming back at some point to certify the work, we're going to ask for someone else from the firm to do it (preferably the owner we spoke to before). How much of the above is an actual issue we should highlight when the work is certified and how much is me just being a picky sod?

Thanks!

Welcome to the forum. Great first post!

I'd get some photos posted to clarify things. And your therapist's report obviously.
 
Unfortunately I'm not in the property again for a week or so and the only thing I had the foresight to take a picture of was the cable situation:

PXL_20230906_164353185.jpg

The mounting plate is visible at the top of that photo, and there's a barely visible bundle of earths he cropped short just sticking out of the trunking behind everything. The flex in that photo was running to a pendant fitting he put up just so there was some light in the room.

All those cables are now inside the fitting, earth is still not connected because I don't really know what (if anything) to connect it to as there are no exposed metal parts of the housing.
 
The earths are a worry yes. Continuity needs maintaining between all of those.
 
Sorry, I didn't phrase that very well! The earths are connected in a push-in connector, but there's no CPC to the housing.

I guess the main question I'm asking is if a CPC is required with the loose Wagos inside the housing given that the powder coating isn't conductive?
If it's now Class I (and I assume it is), is there any way to make this Class II (e.g. mummifying connectors, or placing them all in an additional enclosure)?
And if there's no other way around it, is there any good way of making a solid earth connection to power coated metal without leaving anything visible on the outside of the fitting (no bolt throughs)?

The fitting is this exact one (not my picture, weirdly it was an example used on a blog post about double insulated fittings).

astro-ascoli.jpg
 
You could insist the owner comes, and explain what a mess his guy has made of this.

Changing a class II to class I is bad enough, but to not attempt to earth the fitting is diabolical.

I’d expect some sort of Heath Robinson… a bit of earth wire with a ring crimp on the end, with the fixing screw tightened up would effectively earth the fitting ( if the main body was then screwed to the bracket)
But he hasn’t even done that.

Plastic joint box external to the fitting, and a 2 core into the (new, replacement) fitting with the class II crappy little connector box intact.
 
But they haven't made it Class I, their failure to install correctly has compromised it's Class II protection. For it to become Class I they would have to certify it as such.
Oh yes… what he did was way off, but he didn’t even attempt to earth it…. And if he had, it would still be wrong… but at least a little safer.
 
Thanks all. The owner is coming out on Friday to review the situation, we have quite a few other issues with the install outside of the light fiasco, so it will be interesting to see what he says.
 
Other issues?

Anything you wish to divulge further?
He damaged the extractor fan when putting it up because he forced it when he couldn't get the clips to line up, the housing is chewed up and the bearing is out, so the whole thing vibrates. He also wired the earth into the switched live terminal for the boost (it's marked T so maybe he thought Terre? No clue).

He left about 1m slack on the flex running from the built-in cooker hood to the isolator, and fed that cable through the 150mm hole cut in the top box for the ducting instead of the hole drilled in the back corner for the cable. Not a massive deal, will take a few minutes to redo but I shouldn't have to.

He unilaterally decided to change a socket position from down the side of the fridge to in a wall cabinet. We explained to him well in advance that there would be a ~100mm gap that might be hard to work in, so maybe do that that socket on the first fix. We also then said we could pull the fridge cabinet out to give him space to work when he came back (we left it attached with only 2 screws because we were pretty sure it was going to need to come out). Apparently his solution was to move a socket meant for a vacuum cleaner into a cupboard at eye height.

And just in general, everything is wonky. Extractor fan, every isolator, almost every socket. Only by a little bit but it's just sloppy.
 
He damaged the extractor fan when putting it up because he forced it when he couldn't get the clips to line up, the housing is chewed up and the bearing is out, so the whole thing vibrates. He also wired the earth into the switched live terminal for the boost (it's marked T so maybe he thought Terre? No clue).

He left about 1m slack on the flex running from the built-in cooker hood to the isolator, and fed that cable through the 150mm hole cut in the top box for the ducting instead of the hole drilled in the back corner for the cable. Not a massive deal, will take a few minutes to redo but I shouldn't have to.

He unilaterally decided to change a socket position from down the side of the fridge to in a wall cabinet. We explained to him well in advance that there would be a ~100mm gap that might be hard to work in, so maybe do that that socket on the first fix. We also then said we could pull the fridge cabinet out to give him space to work when he came back (we left it attached with only 2 screws because we were pretty sure it was going to need to come out). Apparently his solution was to move a socket meant for a vacuum cleaner into a cupboard at eye height.

And just in general, everything is wonky. Extractor fan, every isolator, almost every socket. Only by a little bit but it's just sloppy.
Sounds like you could have accomplished it yourself.

It’s good that you know when it’s not right.

And you also know how bad some sparks are, although maybe compliant the work is just a mess

It’s sometimes very difficult to do a job that you are 100% happy with there is always something.

You usually find that not taking your time and thinking about about stuff ends up taking more time and effort.
 
Last edited:
Changing a class II to class I is bad enough, but to not attempt to earth the fitting is diabolical.

I’d expect some sort of Heath Robinson… a bit of earth wire with a ring crimp on the end, with the fixing screw tightened up would effectively earth the fitting ( if the main body was then screwed to the bracket)
But he hasn’t even done that.
I find with these so called 'class 2' metal light fittings which are basically class 1 fittings with a crappy supposedly double insulated joint box supplied to be a total waste of time, if a typical loop in wiring method is present(which it mostly is) the only way to install the light safely is indeed to ring crimp the CPCs and screw them to the fixing screw of the base bracket, like you said, which at least provides an earthed light fitting

This is my method when dealing with these fittings and sadly the only choice I can think of.

unless you have a single cable entering the light fitting it is impossible to ensure a class 2 double insulated situation is maintained, they are a terrible design and lead mainly to an unearthed class 1 fitting as in the post
 

Reply to Class II fitting modified by Electrician in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
1K
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
958
Hi Family member has moved into this house which is about 110 years old. Bodges everywhere inc the electrics. We are just rennovating it and when...
Replies
14
Views
1K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock