Search the forum,

Discuss Insulation resistance testing live conductors to earth in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
21
Hello all, I hope you're all keeping well.

I have a question regarding insulation resistance testing.

Whether doing a single circuit IR test or a global IR on an entire installation, I usually try to remove all loads, eg lamps, neons etc, but obviously this isn't always possible. So I generally join both L+N and test to earth. This is to avoid damaging any sensitive equipment by ensuring no potential difference across the load.

But how come I still can get a bad reading on a circuit while testing this way? I don't fully understand. Is it due to certain loads being able to throw up a bad IR reading and others not?

Any help would be greatly appreciated
 
If this is a global reading you need to break it down to individual circuits by disconnecting the neutral conductors and having all protective devices off. What test voltage are you using.
Having something still connected should not matter unless that something itself is faulty.
 
Some older RCD sockets/spurs will give a low IR to E, without apparently being defective. Surge protection (eg extension leads) will give a low IR when tested at 500V (but not at 250), typically about 0.4M ohms. Anything with a functional earth will again give a low IR to E, in my experience this is only likely to be certain RCDs or RCBOs at a downstream CU.
 
There can be a few reasons for low L+N -> E readings:
  • Connected equipment is leaking. By design, or just old/damp
  • SPD are connected (but there you get a big difference between 250V where usually > 10M and 500V where usually < 0.1M)
  • Cable has degraded or is very damp
  • Accessories are damp/dusty
If a global IR is good, as in above a few M, then you know all circuits are similar.

If the global IR gives you cause for concern, say as it is < 1M, then checking individual circuits can at least establish if a low total is due to, say, 10 decent circuits of ~5M leading to ~0.5M, or 9 are > 10M and one is deeply suspect as different at ~0.5M, etc.
 

Reply to Insulation resistance testing live conductors to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
9
Views
519
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
447
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
700
I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top