We live in an old stone built ground floor flat, built in the 1880s. Obviously the consumer unit and cabling has been updated a number of times over the years by previous owners. One being the Local Authority who owned the property back in the 1960s -70s.

We have lived here for 25 years and decided to have an electrical inspection carried out by a local Electrician. He is a good honest guy, fully trained and qualified and a member of quite a few registered bodies. His report has shown only a couple of problem areas that should be addressed. Separate circuits for appliances, swapping circuits to the protected side of the consumer unit, updating sockets and light switches. He says although our consumer unit is older and the cabling is older there is no need change it or renew at this time but it is something we should think about for the future. He did have limited knowledge with regard to our particular make/model of consumer unit. (Young guy probably not born when our consumer unit was installed)

Now, our plan is to sell up in the new year and realising that this would be a huge upheaval and at a hefty cost we have decided to not take on the task.
However, we have hit a juncture. Our plumbing is such that we have only ever had an Electric Shower.
We wish to maintain this arrangement but have decided to upgrade the shower to a more powerful 10.5Kw unit as the old 7.5Kw shower has packed in and as you have no doubt guessed, this will involve a cable and MCB upgrade.

Existing arrangement is; distance from consumer unit to shower, 25m. Cabling 6mm², under floor in solemn space and in plaster for the last 1m. 32amp MCB on RCD protected circuit.
Our fuse box is an Merlin Gerin, (photos attached).

My questions are; (bearing in mind we are not changing the consumer unit and only wish to change the cabling and MCB for this one circuit),
Q1, would the Merlin Gerin consumer unit be able to be upgraded with a modern Schneider Acti9 45 amp MCB in place of the Multi9 MCB.
Q2, Are our current Multi9 MCBs a C-curve? I'm not sure if the writing on the current MCBs indicate the Curve type.
Q3, Would the Schneider replacement MCBs need to be a C-Curve or B-Curve type in whichever case?
Q4, Rather than a consumer unit upgrade, could we actually just update all the MCBs in the consumer unit this way?
Q4, Should we upgrade all the MCBs to RCBOs instead. (Assuming there is room in the consumer unit for such an upgrade as I understand they are quite large in comparison).

From my internet of things investigation... I gather that Merlin Gerin are no longer in manufacture and subsequently that the proper replacement for Multi9 would be Schneider Acti9. Would this be the correct information?

Any good advice appreciated for 3 dirty children and a smelly wife... I've always been a clean guy...
 

Attachments

  • Merlin Gerin Consumer Unit (1).JPG
    98.5 KB · Views: 134
  • Merlin Gerin Consumer Unit (2).JPG
    94.3 KB · Views: 136
  • Merlin Gerin Consumer Unit (3).JPG
    89.8 KB · Views: 139
  • Merlin Gerin Consumer Unit (4).JPG
    100.5 KB · Views: 144
Schneider C60H RCBO's will fit that board. Merlin Gerin is now Schneider so only the colours and name changed on their switch gear.

Do not try and get the iC60H range to fit as they will not, only the C60H.

This way you will only need to install a new busbar rather than replace the whole board. I'd go full RCBO.

TBH that board is a very good make and I would be very reluctant to rip it out, unless required all your devices only need to be B type unless you have LED units with high inrush currents and the manufacturers recommend C type or if you have a decent sized welder in the garage.
 
Hi - just my opinion, but why not just replace like for like if you’re moving on?
For the upgrade it sounds like you would need a new cable from the CU to the uprated local isolator and then the new shower. But rather than mess about with the old Consumer Unit I’d probably put in a separate little board - Schneider do a 50A one (as you’ve mentioned them).
 
The odd thing that jumps out at me in the pictures is a relatively new 100a DP isolator which only has the live tail connected through it with the neutral being straight through a SP block. Why would anyone do that ?
 
The odd thing that jumps out at me in the pictures is a relatively new 100a DP isolator which only has the live tail connected through it with the neutral being straight through a SP block. Why would anyone do that ?

It's odd to fit a DP isolator when they are only connecting the line, but not unusual for a DNO to fit a single pole isolator in the line only.
Self connect meters with a built in isolator are single pole, and I've seen single pole isolators fitted in seperate enclosures occasionally.
 
What body the electrician belongs to is irrelevant and side tracking this thread. Posts removed.
Hi I don't understand your comment with regard to side tracking and am I to understand that you have removed my post?
I am a householder not an Electrician. I only mentioned the registered bodies because 100% of the Electricians that I looked up on the internet to do the job for me all advertised that they were registered with some organisation/body or other. Is this not the case for all Electricians? So are you saying that an Electrician registered with one of the following organisations is irrelevant?
BRE Certification Ltd
British Standards Institution
ELECSA Ltd
NAPIT Registration Ltd
NICEIC Group Ltd
SELECT (Scotland)
STROMA
Are there any Electricians you could recommend to me an ordinary family man in the street, not an Electrician, that I should hire to do the job who are not registered with an organisation? How would I know to trust them or their work?
I don't feel like taking a chance where electricity is concerned and would hope that I would get a good fully qualified Electrician. How would I know otherwise?

Thank you.
[automerge]1577216785[/automerge]
 
None of your posts have been removed. I deemed the questioning of the bodies the electrician belongs to as being irrelevant to your issue.
 
Hi Dave OCD, the Isolator was fitted by British Gas when we had a new boiler installed. Can you see a problem with it and should I get them back to make amendments?
Thanks

The odd thing that jumps out at me in the pictures is a relatively new 100a DP isolator which only has the live tail connected through it with the neutral being straight through a SP block. Why would anyone do that ?
[automerge]1577217678[/automerge]
None of your posts have been removed. I deemed the questioning of the bodies the electrician belongs to as being irrelevant to your issue.

Thanks for your reply westward10.

My apologies, I thought that you had removed my thread as you are a moderator and you said Posts Removed...
I was not questioning any bodies or their relevance. I merely mentioned that to highlight that in my opinion the local Electrician I asked to do the job for me had advertised these organisations. As it happens I checked the organisations for his registration and he was indeed an approved contractor and that gave me huge confidence in his abilities. As I said, I have no other way of ascertaining his credentials or reliability? Only a man in the street trying to get the best for my family...

Thanks...
 
Last edited:
You haven't seen the removed posts, they were not pertinent to your question they would have sent it off track. None of your posts are a problem.
 
Hello,
He is a good honest guy, fully trained and qualified and a member of quite a few registered bodies.
He says although our consumer unit is older and the cabling is older there is no need change it or renew at this time but it is something we should think about for the future. He did have limited knowledge with regard to our particular make/model of consumer unit. (Young guy probably not born when our consumer unit was installed)

Existing arrangement is; distance from consumer unit to shower, 25m. Cabling 6mm², under floor in solemn space and in plaster for the last 1m. 32amp MCB on RCD protected circuit.
Our fuse box is an Merlin Gerin, (photos attached).

My questions are; (bearing in mind we are not changing the consumer unit and only wish to change the cabling and MCB for this one circuit),
Q1, would the Merlin Gerin consumer unit be able to be upgraded with a modern Schneider Acti9 45 amp MCB in place of the Multi9 MCB.
Q2, Are our current Multi9 MCBs a C-curve? I'm not sure if the writing on the current MCBs indicate the Curve type.
Q3, Would the Schneider replacement MCBs need to be a C-Curve or B-Curve type in whichever case?
Q4, Rather than a consumer unit upgrade, could we actually just update all the MCBs in the consumer unit this way?
Q4, Should we upgrade all the MCBs to RCBOs instead. (Assuming there is room in the consumer unit for such an upgrade as I understand they are quite large in comparison).

From my internet of things investigation... I gather that Merlin Gerin are no longer in manufacture and subsequently that the proper replacement for Multi9 would be Schneider Acti9. Would this be the correct information?


I would say there is no point replacing that consumer unit, short term or long term, it is a good quality board designed primarily for commercial/industrial use rather than domestic and any modern domestic CU would be a step backwards in my opinion.
The electrician not being familiar with that CU is may be due to them primarily working in the domestic sector rather than commercial or industrial.

Schneider have bought Merlin Gerin but are still manufacturing compatible protective devices. To bring it up to full compliance with current regulations you would need to change the non-RCD ways to RCBO's.
Whilst you can buy new compatible protective devices there is still a massive amount of the older type out there, mostly second hand or some new old stock.

The MCB's you have use an older labelling system than the current B, C, D, the but that says type 2 denotes the tripping curve.
 
I would say there is no point replacing that consumer unit, short term or long term, it is a good quality board designed primarily for commercial/industrial use rather than domestic and any modern domestic CU would be a step backwards in my opinion.
The electrician not being familiar with that CU is may be due to them primarily working in the domestic sector rather than commercial or industrial.

Schneider have bought Merlin Gerin but are still manufacturing compatible protective devices. To bring it up to full compliance with current regulations you would need to change the non-RCD ways to RCBO's.
Whilst you can buy new compatible protective devices there is still a massive amount of the older type out there, mostly second hand or some new old stock.

The MCB's you have use an older labelling system than the current B, C, D, the but that says type 2 denotes the tripping curve.

Thank you for your reply davesparks.

That sounds very good advice to me and I am delighted to hear that the CU is of good quality.
I think I will try to source the original MCBs from the internet and ask my Electrician to do the job for me. He quoted me a very reasonable £250 labour for the original work of running another cable to my kitchen, (both the oven and hob are on the same cable and have a dual outlet plate in the kitchen), he recommends that needs to be changed. Also to swap the cooker circuit to a lower amperage MCB and move it to the RCD protected ways... I guess I would try to source three original MCBs for him to fit. He would no doubt supply everything else, cables, sockets and light switches etc... Should I source a 45amp MCB for the shower and, am I right in thinking that I should get 2 x 30 amp MCBs for both separate oven and hob circuits?

Thank you...
 
He quoted me a very reasonable £250 labour for the original work of running another cable to my kitchen, (both the oven and hob are on the same cable and have a dual outlet plate in the kitchen), he recommends that needs to be changed.

Reasonable? I'd say its very unreasonable to take what sounds like a perfectly compliant and safe installation and carry out unnecessary work.
 
Thanks to all for your replies. Collectively I have had some great advice and gained some good knowledge with regards to my CU and the best course of action to take...
Thanks again and I wish you all a Merry Christmas and all the best for the New Year!
[automerge]1577226951[/automerge]
Reasonable? I'd say its very unreasonable to take what sounds like a perfectly compliant and safe installation and carry out unnecessary work.
No, I will ask him to do only the remedial work. I'm sure he would be asking a lot more for a 4 bedroom, 1 sitting room, 1 bathroom, 1 cloakroom and a kitchen rewire with a new consumer unit. He said half a days labour of £250 for the remedial work and in my experience over the years with various Electricians in Edinburgh, that is a good price.
It will no doubt be extra for the shower that I don't mind paying. It will probably come in around £1000 that would be fine for me...
 
Last edited:
No, I will ask him to do only the remedial work.

That's my point, having the hob and oven on the same circuit is fully compliant with the current regulations. Suggesting that there is any need for them to be on seperate circuits is incorrect and they are ripping you off.
They may not be deliberately ripping you off, it could be through a genuine lack of knowledge of the regulations, but either way it is wrong.

There are far too many electricians who have not properly read and understood the changes in the regulations and are still working to previous editions of the regulations. This is often unintentional and they are just falling back on what they were taught as an apprentice.
 
I briefly spotted an accusation there in a post with regard to doing the job myself!
I wish I could that would save me a fortune... I will ask my Electrician if he will source the original MCBs but I thought I would try to make the whole thing easier... I am a researcher and the IT/internet thing is a breeze for me... I'm not so sure about the person with the doubts/accusations but hey ho! Were all entitled to our opinions right or wrong I suppose...

My wife is a registered childminder with the Care Commission. This is the reason we needed the;

DOMESTIC ELECTRICAL INSTALLATION CONDITION REPORT
Issued in accordance with British Standard BS 7671 - Requirements for Electrical Installations,
...in the first place. Safety first!

Maybe the person with the comments is just a DIYer and that's what they would do.
Also it's our house and our CU and our MCBs so I am entitled to find out as much information about them as possible. Just in case I come across the type of rip-off person who would make such comments as self installation and probably do the job themselves...

Thanks again...
[automerge]1577228091[/automerge]
That's my point, having the hob and oven on the same circuit is fully compliant with the current regulations. Suggesting that there is any need for them to be on seperate circuits is incorrect and they are ripping you off.
They may not be deliberately ripping you off, it could be through a genuine lack of knowledge of the regulations, but either way it is wrong.

There are far too many electricians who have not properly read and understood the changes in the regulations and are still working to previous editions of the regulations. This is often unintentional and they are just falling back on what they were taught as an apprentice.
Interesting, I will get clarification on this from my local authority building services dept...
The guy seems genuine to me and we like him a lot... But you never know! He is young and perhaps has not fully understood the regulations as you say.
Thanks for the great advice...
 
Interesting, I will get clarification on this from my local authority building services dept...
The guy seems genuine to me and we like him a lot... But you never know! He is young and perhaps has not fully understood the regulations as you say.
Thanks for the great advice...

Local authoritys generally don't have a clue about the wiring regulations as it is nothing to do with them.

Unfortunately you have to trust the electrician you hire, or spend a few years learning the trade yourself.

Ask the electrucian to show you the actual regulation which they believe this does not comply with. The book they will show you is BS7671 'The 18th edition IET wiring regulations' (or words to that effect, I can't remember the exact wording but the BS number is right) which is an A4 size book with a blue cover (any other colour is a previous version which is not current).
They may also show you the on site guide which is an A5 size ring bound book with a blue and white cover. This is an official guide to regulations.
 
Local authoritys generally don't have a clue about the wiring regulations as it is nothing to do with them.

Unfortunately you have to trust the electrician you hire, or spend a few years learning the trade yourself.

Ask the electrucian to show you the actual regulation which they believe this does not comply with. The book they will show you is BS7671 'The 18th edition IET wiring regulations' (or words to that effect, I can't remember the exact wording but the BS number is right) which is an A4 size book with a blue cover (any other colour is a previous version which is not current).
They may also show you the on site guide which is an A5 size ring bound book with a blue and white cover. This is an official guide to regulations.
Here is a snapshot of section 7 of the report I may have got my information wrong... What are your thoughts please?
 

Attachments

  • Inspection Report Snapshot.png
    59.6 KB · Views: 101
Those are all C3s and are only recommendations, you should have received a satisfactory report and no remedial works are required.
 
Those are all C3s and are only recommendations, you should have received a satisfactory report and no remedial works are required.
Yes understood , but I would like the house to be 100% goodly as far as Electrical is concerned. I am unsure as to the real-time effect of the recommendations...
What would you recommend?
 
I wouldn't be too worried about any of the defects listed there. Carrying out the work suggested should improve the installation, but nothing is required to be done. The certificate should state the installation is in a satisfactory condition.
 
If you are moving out very soon then why bother with the hassle? Stick with a lower power shower unit.

Thats the best bit of advice you've been given (including the #4 @Wilko, which won't multi post here?). Unless anything is dangerous, and that appears not to be, I wouldn't be doing anything if you are moving soon. Ask an estate agent. I recently moved, and felt inclined to renovate certain things before putting my place on the market, but was advised not to.

The eventual buyer, never mentioned anything. If there are things that need changing or upgrading, that will be reflected in the offer price; people want to put their own mark on the property they are investing in. Which, incidentally IMO, would be replacing that horrible looking CU.

Merry Xmas everyone.
 
Thats the best bit of advice you've been given (including the #4 @Wilko, which won't multi post here?). Unless anything is dangerous, and that appears not to be, I wouldn't be doing anything if you are moving soon. Ask an estate agent. I recently moved, and felt inclined to renovate certain things before putting my place on the market, but was advised not to.

The eventual buyer, never mentioned anything. If there are things that need changing or upgrading, that will be reflected in the offer price; people want to put their own mark on the property they are investing in. Which, incidentally IMO, would be replacing that horrible looking CU.

Merry Xmas everyone.
Hi Midwest, got that... The report did come back as satisfactory.

However, I don't like the idea of passing on possible issues to the next person, call it good karma or something. Call me old fashioned, but my grandparents, who lived through two world wars would never have done that either.

I understand a buyer may rip it all out and that's fair enough. If we were not selling we would commission a full rewire/complete upgrade ourselves and I would insist that the highest quality CU and cabling/fittings etc were used.

As a matter of interest, what would you be replacing the horrible CU with?

Merry Christmas to you and all...

Thanks
 
I would leave well alone also and you are not handing over a poor job TBH and Merlin boards are really good.

You will be hard pushed to find a board of better quality
 
Hi Midwest, got that... The report did come back as satisfactory.

However, I don't like the idea of passing on possible issues to the next person, call it good karma or something. Call me old fashioned, but my grandparents, who lived through two world wars would never have done that either.

I understand a buyer may rip it all out and that's fair enough. If we were not selling we would commission a full rewire/complete upgrade ourselves and I would insist that the highest quality CU and cabling/fittings etc were used.

As a matter of interest, what would you be replacing the horrible CU with?

Merry Christmas to you and all...

Thanks

I suspect your prospective buyer would have their own survey and an EICR etc carried out, but as has been already said, your report doesn’t appear to highlight any dangerous issues. I don‘t know your property, but if I was buying an older property, I would be expecting potentially to have upgrading it’s infrastructure, which would include re-wiring, plumbing & heating etc.

I doubt if my misses looked at your CU would have any concerns, but my electricians head just sees it as plain nasty, no offence meant. Others here would argue differently.

Replace your faulty shower, like for like, and keep your money for your new house, don’t spend it on the old one.
 
Those Merlin boards are solid and will out last a lot of the crap available now. Don't waste your money as you'll probably need it for the unexpected on your next property.
 
Yes that's pretty solid advice from all of you guys... Looking at the CU and considering the hassle and costs I might just take the easy option.

Wait though a plan has presented itself! Looking at the CU again, it occurs to me that it would no doubt be easy for the Electrician to move the 40amp Cooker MCB to the protected ways and then put the shower on that 40 amp MCB circuit. At the same time he could move the cooker circuit onto the 32amp protected ways MCB.

Thus downgrading the MCB for the Cooker circuit and at the same time upgrading the Shower circuit allowing a larger capacity shower to be fitted. This would also be partly in line with his recommendations would it not?

Does that Make sense, would that be possible, would it be in line with the regulations?

Thanks...
 
Here is a snapshot of section 7 of the report I may have got my information wrong... What are your thoughts please?

Number 2 can be solved by fitting RCBO's rather than replacing whe whole DB.

Number 3 and 5 are nonsense, there is no need to replace things just because they are 'dated' this hould not have been recorded as an observation at all unless they have deteriorated through age so that safety is reduced.

Number 4 is nonsense, there is no limit to the number of appliances that can be run from a single circuit.

Number 6 again can be solved by fitting RCBO's to the existing board.
 
Number 2 can be solved by fitting RCBO's rather than replacing whe whole DB.

Number 3 and 5 are nonsense, there is no need to replace things just because they are 'dated' this hould not have been recorded as an observation at all unless they have deteriorated through age so that safety is reduced.

Number 4 is nonsense, there is no limit to the number of appliances that can be run from a single circuit.

Number 6 again can be solved by fitting RCBO's to the existing board.
Well seeing as you are throwing in the bombs on page 7 here's the rest of it...
 

Attachments

  • EICR Snapshot3s.png
    84.3 KB · Views: 70
  • EICR Snapshot2s.png
    8.9 KB · Views: 60
  • EICR Snapshot1s.png
    63.9 KB · Views: 58
  • EICR Snapshot4s.png
    115.7 KB · Views: 58
  • EICR Snapshot5s.png
    118.9 KB · Views: 55
  • EICR Snapshot6s.png
    106.4 KB · Views: 53
  • EICR Snapshot7s.png
    102.8 KB · Views: 52
  • EICR Snapshots.png
    81.2 KB · Views: 49
Well seeing as you are throwing in the bombs on page 7 here's the rest of it...

On page 3:
they have recorded the model number where they should have recorded the serial number of the tester.
It is apparently a 3 phase 3 wire supply, yet from your earlier picture it is clearly a single phase 2 wire supply.
The value for U is incorrect
The value for prospective fault current does not correlate with the value of Ze recorded.

And they haven't carried out any insulation resistance testing???

Did they wear a stetson and ride a horse?
 
On page 3:
they have recorded the model number where they should have recorded the serial number of the tester.
It is apparently a 3 phase 3 wire supply, yet from your earlier picture it is clearly a single phase 2 wire supply.
The value for U is incorrect
The value for prospective fault current does not correlate with the value of Ze recorded.

And they haven't carried out any insulation resistance testing???

Did they wear a stetson and ride a horse?
I don't doubt your reckoning at all davesparks, what you have said makes sense. It looks like we have been led a merry dance with this guy. He is such a nice guy too, butter wouldn't melt... I am really peaved off with the Electrician. I paid for this inspection and shoddiness will not do at all!
The first thing I am going to do is contact, 'SELECT', after the holidays. The main body with who he is registered. I will ask them to carry out an investigation.

Dependant on their advise, I will then ask for him to explain himself and request a refund of the costs he charged us for the inspection!

I have made a copy of the advice gathered here on the forum and will present this to, SELECT with my statement. We will see what happens from there...

Thank you for your very good advice and i will update this thread as soon as I have had a response from SELECT.

It is guys like him that are giving you guys a bad name. Now it seems that even though I checked his credentials that still wasn't good enough! What the hell is an ordinary guy got to do to get a proper job done!!!

Thank you very much for pointing out these mistakes...
 
I don't doubt your reckoning at all davesparks, what you have said makes sense. It looks like we have been led a merry dance with this guy. He is such a nice guy too, butter wouldn't melt... I am really peaved off with the Electrician. I paid for this inspection and shoddiness will not do at all!
The first thing I am going to do is contact, 'SELECT', after the holidays. The main body with who he is registered. I will ask them to carry out an investigation.

Dependant on their advise, I will then ask for him to explain himself and request a refund of the costs he charged us for the inspection!

I have made a copy of the advice gathered here on the forum and will present this to, SELECT with my statement. We will see what happens from there...

Thank you for your very good advice and i will update this thread as soon as I have had a response from SELECT.

It is guys like him that are giving you guys a bad name. Now it seems that even though I checked his credentials that still wasn't good enough! What the hell is an ordinary guy got to do to get a proper job done!!!

Thank you very much for pointing out these mistakes...
I think you should speak to the guy before reporting him. He will have a complaints procedure that you should follow.
You have gone from thinking he is wonderful to appalling in a short space of time from taking advice from strangers on a forum. I'm not saying they are wrong, but at least speak to the guy and form your own opinion before possibly damaging his career.
 
....No, I will ask him to do only the remedial work. I'm sure he would be asking a lot more for a 4 bedroom, 1 sitting room, 1 bathroom, 1 cloakroom and a kitchen rewire with a new consumer unit. He said half a days labour of £250 for the remedial work and in my experience over the years with various Electricians in Edinburgh, that is a good price.
It will no doubt be extra for the shower that I don't mind paying. It will probably come in around £1000 that would be fine for me...
I thought Scotsman had a reputation for being careful with money ?

I'm confused now...
 
I think you should speak to the guy before reporting him. He will have a complaints procedure that you should follow.
You have gone from thinking he is wonderful to appalling in a short space of time from taking advice from strangers on a forum. I'm not saying they are wrong, but at least speak to the guy and form your own opinion before possibly damaging his career.
Yes nice to be nice and all that... But the evidence is clear strangers or not!

It seems to me that if they are not wrong and the evidence is clear then what other or own opinion would I need to form

Why should we be put in an embarrassing situation? That's not fair for me and my family yet you expect me to be fair on his behalf. He should not have made these errors plain and simple as that. If he is putting himself forward as a Professional Electrician then he should be able to do his job properly.

It seems pretty straight forward to me with regard to the points that have been raised. As you point out, they are not wrong! I'm a layman and even I can see that these discrepancies are wrong. I'm sure that Select wouldn't want to ruin his career either.

However, what worries me is that maybe he did not carry out a proper inspection in the first place! The evidence seems to point to it all being a little bit uncaring or lacking in knowledge. In either case, this has created doubt in my mind. A person tasked with the responsibility of safety for others should think hard about the consequences of their actions. It would be too late ask about his complaints procedure when something has happened and my family and I may be in danger of electrocution because he failed to observe a fault.

Do you think I should just take a chance?
[automerge]1577317781[/automerge]
I thought Scotsman had a reputation for being careful with money ?

I'm confused now...
Yes indeed, we all make mistakes. It seems that even some registered qualified Electricians reputations can't be trusted either?
 
Last edited:
We have decided to put the whole thing down to bad experience, bare the financial loss and start again. I am still concerned that if something isn't done the Electrician may do harm to someone else. No doubt we are not the only ones who have put our trust in him.

However, I am now tasked with finding an Electrician who can actually do the job and carry out a proper inspection. What do I do? Where can I find such a guy? It seems to me that registration of registered bodies counts for nothing...

Does anyone know of a good Electrician in Edinburgh who is tried, tested and worthy?

Also why would our cooker not be on the RCD protected ways side of the CU anyway and why such a large MCB?

In the mean time we still have no shower! Please can someone advise me what would be a safe Shower to buy in terms of Kw rating for the circuit design. That would be if the circuit was RCD protected when the new Electrician has swapped the 40amp MCB to that side of the CU. Utilising the existing 20-25m of 6mm2 running under the floor, lying loose in the solemn and up a plastered wall for 1m. We have a 45amp double pole switch on the wall outside the bathroom then there is around 6" of cable that goes through a 1½" diameter hole directly to the back of the Shower?

Thanks.
 
Last edited:
However, I am now tasked with finding an Electrician who can actually do the job and carry out a proper inspection. What do I do? Where can I find such a guy? It seems to me that registration of registered bodies counts for nothing


It would be a very big plus if the electrician held the City+Guilds 2391 or its modern equivalent,that would mean he should understand what the results actually mean,
membership of a scheme or size of a company means nothing whatsoever( a large company only one employee needs to be qualified, he can then oversign any of the others efforts)

You could find a company with scheme registrations coming out of their nostrils but the actual guy on the job may have no more idea about test and inspection than your good self

Staying with a one man band but insisting on him having the testing qualification will likely cut the odds of getting the same experience as before
 
However, I am now tasked with finding an Electrician who can actually do the job and carry out a proper inspection. What do I do? Where can I find such a guy? It seems to me that registration of registered bodies counts for nothing


It would be a very big plus if the electrician held the City+Guilds 2391 or its modern equivalent,that would mean he should understand what the results actually mean,
membership of a scheme or size of a company means nothing whatsoever( a large company only one employee needs to be qualified, he can then oversign any of the others efforts)

You could find a company with scheme registrations coming out of their nostrils but the actual guy on the job may have no more idea about test and inspection than your good self

Staying with a one man band but insisting on him having the testing qualification will likely cut the odds of getting the same experience as before
Thank you for that Des 56, sounds like a plan... What is the modern equivalent of the City+Guilds 2391 that I should look for just in case?

I actually got the original guys details from the East Lothian Council Trusted Trader website. That was a waste of time...

Thanks again...
 
I've been reading the thread with interest. Agreed that the EICR is a little lacking but far from the words I have ever seen.

Scotland recognises only 2 registration bodies - SELECT and NICEIC. If your electrician trained in Scotland via an apprenticeship it will have been via SECTT, they are the charity arm of SELECT and both are allied to SJIB. He will have taken and passed the FICA (similar to the AM2 in England). Otherwise if he trained via the C&G route then as said look for the 2391 qualification. As far as I am aware he cant be registered with SELECT unless he has his FICA or 2391 - you certainly cant with the NICEIC.

If someone was unhappy with my work then I'd want them to say and let me make it right for them.

Regarding replacing the MCB's with RCBO's you should check with Schneider that they allow mixing of oldeirand newer devices. I put the same question to Wylex this year and I they said no. I had to replace the customers whole lot of MCB's.

I would have been happy to help but I'm 6 hours north of you! :)
[automerge]1577527589[/automerge]
2 more thoughts.

You could try contacting @JK-Electrical He talks a lot of sense and is only over in Glasgow.

SELECT are the only registration body in the UK that are trying to bring in protected title to be mandatory in Scotland. You might want to browse this Yet Another Dodgy EICR - https://www.electriciansforums.net/threads/yet-another-dodgy-eicr.177066/ The Scottish government are already trying to remove under qualified or unqualified people from the industry for example stipulating that only registered contractors can undertake electrical work in private rented property.
 
Last edited:
Regarding replacing the MCB's with RCBO's you should check with Schneider that they allow mixing of oldeirand newer devices. I put the same question to Wylex this year and I they said no. I had to replace the customers whole lot of MCB's.

Yes it is always best to check, but Schneider are pretty good at keeping the design and backwards comparability going so I doubt it will be a problem.
 
I've been reading the thread with interest. Agreed that the EICR is a little lacking but far from the words I have ever seen.

Scotland recognises only 2 registration bodies - SELECT and NICEIC. If your electrician trained in Scotland via an apprenticeship it will have been via SECTT, they are the charity arm of SELECT and both are allied to SJIB. He will have taken and passed the FICA (similar to the AM2 in England). Otherwise if he trained via the C&G route then as said look for the 2391 qualification. As far as I am aware he cant be registered with SELECT unless he has his FICA or 2391 - you certainly cant with the NICEIC.

If someone was unhappy with my work then I'd want them to say and let me make it right for them.

Regarding replacing the MCB's with RCBO's you should check with Schneider that they allow mixing of oldeirand newer devices. I put the same question to Wylex this year and I they said no. I had to replace the customers whole lot of MCB's.

I would have been happy to help but I'm 6 hours north of you! :)
[automerge]1577527589[/automerge]
2 more thoughts.

You could try contacting @JK-Electrical He talks a lot of sense and is only over in Glasgow.

SELECT are the only registration body in the UK that are trying to bring in protected title to be mandatory in Scotland. You might want to browse this Yet Another Dodgy EICR - https://www.electriciansforums.net/threads/yet-another-dodgy-eicr.177066/ The Scottish government are already trying to remove under qualified or unqualified people from the industry for example stipulating that only registered contractors can undertake electrical work in private rented property.

Thanks for that richy3333, no doubt there are a lot worse...

I also understand what you are saying with regards to being given the opportunity to put it right.

However, to make such a fundamental mistake in failing to complete an important document properly does not fill me with confidence... No, I'm afraid the bottom line is I simply cannot trust the guy! Electricity to me is of the same nature as working at sea. No second chances! Mistakes in marine applications are not forgiving and neither is a serious electric shock!

If I did give him a second chance what would he do? Simply say, oh! sorry me bad, I will issue you a new report and I stand by my good judgement of your inspection?

Nope, can't be trusted!

I feel mugged off, but hey if that's the price for safety then so be it. I have learned lessons from this and admittedly I was a little naive in my approach to the whole thing in the first instance. I realise that there are good and bad in the building trade but it's an awfy job when you can't trust a registered Electrician!

Your man in Glasgow sounds good but probably too far away to justify the extra added costs of travel and the like... I will start a fresh search in the new year when the trades return in earnest. Good advice with regard the CU upgrades, I will contact Schneider in that regard.

Thanks again and all the best...
 
Thanks for that richy3333, no doubt there are a lot worse...

I also understand what you are saying with regards to being given the opportunity to put it right.

However, to make such a fundamental mistake in failing to complete an important document properly does not fill me with confidence... No, I'm afraid the bottom line is I simply cannot trust the guy! Electricity to me is of the same nature as working at sea. No second chances! Mistakes in marine applications are not forgiving and neither is a serious electric shock!

If I did give him a second chance what would he do? Simply say, oh! sorry me bad, I will issue you a new report and I stand by my good judgement of your inspection?

Nope, can't be trusted!

I feel mugged off, but hey if that's the price for safety then so be it. I have learned lessons from this and admittedly I was a little naive in my approach to the whole thing in the first instance. I realise that there are good and bad in the building trade but it's an awfy job when you can't trust a registered Electrician!

Your man in Glasgow sounds good but probably too far away to justify the extra added costs of travel and the like... I will start a fresh search in the new year when the trades return in earnest. Good advice with regard the CU upgrades, I will contact Schneider in that regard.

Thanks again and all the best...
I can’t but help but thinking that ’we’ve’ changed your mind about your original electrician after #19, for other than some poor administration? ‘We’ here can be very very critical at times, and sometimes feed people’s fears.

It seems you ready to accept the advise from strangers on a forum, we can only advise what’s reported to us, other than someone you previously trusted and who has worked in your house. Why not take up the suggestion in #39?
 
I realise that there are good and bad in the building trade but it's an awfy job when you can't trust a registered Electrician!
It's not just electricians... but all trades and professions ! I only ever use people that I know do a good job, or are recommended by someone that I know have the knowledge to discern good from not so good.

It's partly the result of the modern world requiring everyone to have a 'certificate' in whatever it is they do... the obvious intimation from this is that if you have the correct certificate then you must know what you're doing; if not, then you don't.

I once had to have some gas work done and was amazed that I had to explain to the gas safe registered guy how to do it ! (He had all the right certificates and was gas safe registered)

Similarly, I have heard of people finding a solicitor to deal with the conveyance of a new property... by searching online then choosing the cheapest one ! They are clearly happy to trust many tens of thousands of pounds to someone they have never met, never heard of before and is probably hundreds of miles away.
 

Reply to Inspection Report, Electric Shower, Merlin Gerin and Schneider MCBs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
769
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
765
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
916
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock