Search the forum,

Discuss Maximum Disconnection Times in the UK Electrical Forum area at ElectriciansForums.net

Cookie

-
Reaction score
118
What is the reasoning behind having a 0.8 disconnection time for up to 120 volts Uo, but it then jumps to 0.4 seconds as soon as you go over it? Wouldn't it be better 0.8 seconds for 150 volts Uo and under, 0.4 seconds 150 volts and over Uo?
 
What is the reasoning behind having a 0.8 disconnection time for up to 120 volts Uo, but it then jumps to 0.4 seconds as soon as you go over it? Wouldn't it be better 0.8 seconds for 150 volts Uo and under, 0.4 seconds 150 volts and over Uo?

We don't use 150V supplies, but we do have 110 and 230 so in reality whether you set the limit at 120 or 150 the real world effect will be the same.

What is your logic behind saying its better at 150V rather than 120V?
 
When using a single phase supply you get 120 volts line to earth, but on a 3 phase supply you get 138 volts to earth which increases the disconnection time requirements (ie faster trip mandated).
 

Attachments

  • autodraw 11_20_2019.jpg
    40.6 KB · Views: 22
Last edited:
When using a single phase supply you get 120 volts line to earth, but on a 3 phase supply you get 138 volts to earth which increases the disconnection time requirements (ie faster trip mandated).
Cookie I got to be the one but are you asking a question or telling us. Nobody really knows how to respond to the 3 post you have made already.
 
When using a single phase supply you get 120 volts line to earth, but on a 3 phase supply you get 138 volts to earth which increases the disconnection time requirements (ie faster trip mandated).

No we don't, standard single phase and three phase supplies in the UK are 230V to earth.

The 120V would only usually be relevant to a reduced low voltage supply on construction sites.
[automerge]1574290644[/automerge]
Well, the NEC does frequently talk about 150 volts to ground over or under. Would be nice to harmonize the IEC with the NEC.

That will be pretty difficult with the big differences between electrical installations in different countries.
 
No we don't, standard single phase and three phase supplies in the UK are 230V to earth.

The 120V would only usually be relevant to a reduced low voltage supply on construction sites.
[automerge]1574290644[/automerge]


Yup

That will be pretty difficult with the big differences between electrical installations in different countries.


Usually, but in places like the Philippines, Saudi Arabia and parts of Latin America one is often left working with both codes. An NEC system with IEC standards applied to them.

See page 8:



120/240 and 138/240Y is found in older installations that have been changed from 120 to 230 volt distribution equipment. Makes for some interesting stuff.
 
What is the reasoning behind having a 0.8 disconnection time for up to 120 volts Uo, but it then jumps to 0.4 seconds as soon as you go over it? Wouldn't it be better 0.8 seconds for 150 volts Uo and under, 0.4 seconds 150 volts and over Uo?
Think of it as Time and "energy Received" , cooking a resistor .
..Where the resistance is a human wishing to survive an electric shock...
Simplify things thinking the first 50V is wasted getting through your skin !
[automerge]1574304597[/automerge]
Think of it as Time and "energy Received" , cooking a resistor .
The reality is we are saving equipment from fire risk , limiting total amount of energy received - is how we stay safe !
 
Last edited:
Center tapped 240 is 120. Line to line 240 produces 138.

Republic of the Philippines uses this system.

Yes, BS7671 and IEC codes on how they would go about dealing with those two voltages.

I'm well aware line-line 240 is rare in Europe.
 
Center tapped 240 is 120. Line to line 240 produces 138.

Republic of the Philippines uses this system.

Yes, BS7671 and IEC codes on how they would go about dealing with those two voltages.

I'm well aware line-line 240 is rare in Europe.

Err OK then.
 
Center tapped 240 is 120. Line to line 240 produces 138.

Republic of the Philippines uses this system.

Yes, BS7671 and IEC codes on how they would go about dealing with those two voltages.

I'm well aware line-line 240 is rare in Europe.
In a star connection phase to phase is 240 vac phase to earth 120vac the voltage you read can be as high as 130vac the same goes with 3 phase. It’s a plus or minus 5% on the voltage in the US
 
Also got a post deleted in another thread for saying the stuff on Amazon made by China is often not safe to install.
Tricky tight rope - Negative opinions ..
( I'm older and just love moaning )
You get what you pay for, (and some local wholesalers risk a big hit , when they have to honour their returns policy)
Need to educate customers to spend more!
 
130 volts would be the highest in a 120/208 system, not a 240 volt wye system.

The drawings are correct for the system being depicted.
On paper is one thing, in the real world it’s a totally different world. Why the emphasis on exactly 138vac
 
710? I had 41.1 in mind. I'm curious how those voltage cutoff values were derived.
Yes I missed table 41.1 maximum disconnection times on page 55 as far as how are the voltages are derived starts with AC and DC theory
[automerge]1574375985[/automerge]
Yes I missed table 41.1 maximum disconnection times on page 55 as far as how are the voltages are derived starts with AC and DC theory

I’m trying to learn the UK ways of doing electrical work
 
UK wiring requires that general socket and lighting circuits trip a breaker in a required amount of time based on the line to earth voltage.
We can test breakers or RCDs but we can’t fix them if there are 1/10th of a second to slow, as far as I go if they trip I’m happy. I read your profile and I applaud you for wanting to learn but don’t just post things you are reading and asking why. I’m here to help anyone that needs it if I can. I’m going to ask you a question are you from the UK or US
[automerge]1574377266[/automerge]
Asking about the code's reasoning. And Megawatt- I fully get you!
If you are looking for reasons why the code wants this or that is something every body wants. You have hundreds of people who make up rules and regulations in the BIS 7671 and they all have different opinions
 
Last edited:
Staff have cleared up some posts in this thread. Please keep threads on topic and don't respond to rubbish, just report it, it saves us time. Cheers. :)
 
Err OK then.


I measured the voltage today and got 122.4 volts slot one to earth, 122.5 volts slot two to earth and 244.5-244.7 volts slot to slot. I can't find or measure any 240 volts to earth. IMO the diagrams are correct.
 

Attachments

  • VV1.jpg
    80.1 KB · Views: 10
  • VV2.jpg
    77.9 KB · Views: 10
  • VV003.jpg
    85.7 KB · Views: 7
  • VV3.jpg
    87 KB · Views: 7
Sorry, my mistake - I thought you had put 'incorrect'.
[automerge]1575140239[/automerge]
I think I need to reread this thread. You posted a table from the UK regs I think, but you are asking about the US voltages? Apologies if I'm confused.
 
My apologies. And to be fair I can understand any confusion this may cause as these systems are not used in the UK.
[automerge]1575140949[/automerge]
120/240 and 138/240Y system, not used in the UK, but designing around IEC standards in regards to human and life safety.
 
Last edited:
Center tapped 240 is 120. Line to line 240 produces 138.

Republic of the Philippines uses this system.

Yes, BS7671 and IEC codes on how they would go about dealing with those two voltages.

I'm well aware line-line 240 is rare in Europe.

BS7671 is primarily intended for use in the UK with our standard voltages.

Using BS7671 in the Philippines with USA standard supplies and voltages is never going to be fully compatible. Its a square peg and round hole situation.
 
BS7671 is primarily intended for use in the UK with our standard voltages.

Using BS7671 in the Philippines with USA standard supplies and voltages is never going to be fully compatible. Its a square peg and round hole situation.


I agree- which, IMO- gives me grounds to question Table 41.1 in BS7671 and IEC60364-4-41. IMO both these codes are 230 volts centric, meaning they give little thought when dealing with systems 150 volts to ground and under. Considering that at one point parts of central Europe were 127/220 (think how schuko sockets came about having no polarity), the IEC/VDE/NFC15-100 may have had incentive to mandate 0.4 seconds disconnection times on 127/220 volts systems since an increase in voltage would not require any re-wiring or recalculating of the circuits once raised to 220 volts to ground.

Both the Phillipines, Mexico, Canada and the US use the NEC or NEC based code- however the NEC has no earth fault loop impedance requirements. Meaning I could legally run 2.08mm2 to a shed 2000 feet away and never trip a breaker during a short circuit. All the earth wires in the shed would be at 60 volts to remote earth. I could plug in something metal, have it sit live at 60 volts to ground, get killed, and absolutely nothing could be done to blame the electrician, authority having jurisdiction or the NFPA. Even better a 277 volt light pole in a parking lot. I could run 3,500 feet of 3.31mm2 to a LED light, have a ground fault in the fixture, energize the pole at 138 volts to ground and have it sit continuously 24/7 live without tripping a breaker where a child could hug or lick the post with their tongue during winter. Child dies, case gets taken to court, lawyers litigate away from the real cause taking advantage of everyone lacking basic electrical theory...

Here are two US sparks having seen the problem in their career:




The thing is people, especially children, get killed all the time in the US from energized pools, fences, light poles, AC units, industrial equipment, doors, ect. The blame gets put on shoddy work or poorly connected earth wires... not the code... Much like in the 70s missing bonding jumpers leading to shocks and electrocutions were blamed on ground rods not driven deep enough in the court of law.


The NFPA's solution is to quietly mandate GFCIs on everything- much like GFCIs took care of all the 2 prong metal framed tools injuring people. I encourage you to read the code making panel's reasoning:

NEC 2020 code new standards in GFCI protection - http://www.p3-inc.com/blog/entry/nec-2020-code-new-standards-in-gfci-protection


Ditto for industrial equipment violating earth fault loop impedance:




Which is why I am so curious about learning BS7671 and establishing a value which can be applied to US systems.

That and the fact the US will eventually one day go to a 230-250 volts utilization voltage. Before (if) 230/400Y becomes the norm 127/220, 133/230 and 138/240Y systems will be common in aiding the conversion process. Its easier to raise a Con Edison 120/208Y network by 10 volts than it is by 110 volts.

But regardless the issue of loop impedance (or lack there of) needs to be addressed first.
 
BS7671 is primarily intended for use in the UK with our standard voltages.

Using BS7671 in the Philippines with USA standard supplies and voltages is never going to be fully compatible. Its a square peg and round hole situation.


I'll ask this: how did loop impedance become a thing in the UK? Was it actual shocking electrics or a theoretical perspective of "what if"?
 

Reply to Maximum Disconnection Times in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
862
Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
97
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock