Search the forum,

Discuss Need to upgrade main panel? in the UK Electrical Forum area at ElectriciansForums.net

sjaffa

-
Reaction score
0
I have been meeting with solar system installers to install a grid-tied system at my house. Before I commit I want to verify whether I need to upgrade my main service panel.
I have been reading about the 120% rule and am not sure if my current main service panel is sufficient. Any assistance would be greatly appreciated.

I will be getting a 9.28 kW system with a SolarEdge SE7600H-US Inverter (the model with an EV charger). I built my home 6 years ago and looking at my city permit paid for a 200 Amp service from the utility company. I believe my main service panel has a 150 A main service breaker that feeds my subpanel in my basement along with the majority of my breakers installed there. There are a few extra breakers installed in my main service panel. The labeling on my main service panel states "Mains 250 A max". Attached are pictures of my main service panel with the cover off and the label information.

My understanding is that the formula goes Busbar Rating * 120% - Main Service Breaker = Max Size of Inverter Breaker. So in my case does the label "Mains 250 A max" equal the Busbar rating so would my equation be 250 A * 120% - 150 A = 150 A? Which would be plenty big for a 40 A breaker for my system?

Main service panel label.jpg



Inside main service panel.JPG
 
most of us are UK based so ain't got a scooby. however there are a few US members who may be able to help when they come online.
 
I have been meeting with solar system installers to install a grid-tied system at my house. Before I commit I want to verify whether I need to upgrade my main service panel.
I have been reading about the 120% rule and am not sure if my current main service panel is sufficient. Any assistance would be greatly appreciated.

I will be getting a 9.28 kW system with a SolarEdge SE7600H-US Inverter (the model with an EV charger). I built my home 6 years ago and looking at my city permit paid for a 200 Amp service from the utility company. I believe my main service panel has a 150 A main service breaker that feeds my subpanel in my basement along with the majority of my breakers installed there. There are a few extra breakers installed in my main service panel. The labeling on my main service panel states "Mains 250 A max". Attached are pictures of my main service panel with the cover off and the label information.

My understanding is that the formula goes Busbar Rating * 120% - Main Service Breaker = Max Size of Inverter Breaker. So in my case does the label "Mains 250 A max" equal the Busbar rating so would my equation be 250 A * 120% - 150 A = 150 A? Which would be plenty big for a 40 A breaker for my system?

View attachment 51296


View attachment 51297
Sjaffa the 200 amp panel you have is right where it needs to be so no upgrade is needed and the 150 amp breaker that is fed from your service panel to you sub panel should be fine also. My only concern is the rating of the panel which is being sub fed, normally the breaker should be 100 amps. The reason I say that is according to the NEC you cannot exceed the panel rating but I would think you are going to be fine, let us know how it works out
 
@Megawatt how do you know this is a 200 amp panel? I was confused looking at the label with the 250 amp max language, and the 150 amp main service breaker so wasn't sure exactly what it was.

Also, do you know if the inverter 40 amp breaker would be installed in the top two slots or the two slots below those that look like they are connected to the busbar? The installers I have talked to haven't been able to answer these questions so it hasn't given me much confidence that they will install it correctly.
 
@Megawatt how do you know this is a 200 amp panel? I was confused looking at the label with the 250 amp max language, and the 150 amp main service breaker so wasn't sure exactly what it was.

Also, do you know if the inverter 40 amp breaker would be installed in the top two slots or the two slots below those that look like they are connected to the busbar? The installers I have talked to haven't been able to answer these questions so it hasn't given me much confidence that they will install it correctly.
Yes they will put the 40 amp breaker in the top spaces and don’t pay that 250 max no attention. That is information for the electrician which simply put is that panel can with stand 250 amps. Go outside and look at the writing on the meter and it should have 200 amps, probably on the left side. Trust me you have nothing to worry about.
 
Yes they will put the 40 amp breaker in the top spaces and don’t pay that 250 max no attention. That is information for the electrician which simply put is that panel can with stand 250 amps. Go outside and look at the writing on the meter and it should have 200 amps, probably on the left side. Trust me you have nothing to worry about.

The company doing the install on the solar panels couldn’t answer your questions because they are not electricians, all they do is install panels and they will probably have a an electrician to put the 40 amp breaker in and wire it up
 
I might be missing something obvious here, but why does the 150A breaker appear to be four pole with 4 wires?
Dave I just looked at that breaker and you are right and I’ve never seen this before but look at the schematic for the meter and it appears to be a parallel feeder to the house panel
 

Reply to Need to upgrade main panel? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
943
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
769
Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
972
I need to design an electrical panel, and the main circuit breaker is rated at 250 A. We are implementing a 100% Brum solution for the panel, but...
Replies
3
Views
845
My best mate has been medically retired from the prison service at the young age of 52 and has time on his hands :D He's looking at a 'plug in'...
Replies
7
Views
515

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock