OK I've got 2 contactors where the coils are wired in parallel.
They are sitting right next to each other,
One pulls in and holds perfectly well. The other pulls in and drops out. Pulls in again drops out. Ect. Ect. For as long as you are trying to keep the contacts closed.

I've tried swapping out contactors, I've tried swapping the wiring around,

Same thing.

This is an established system that's been working fine for probably as long as I've been alive. :D

Any clues on what to try.


Cheers
 
Have you proven that the coils are indeed wired in parallel and that the voltage at the coil terminals is what you expect it to be, correct for the coil and constantly energised?

What is the voltage? AC or DC? What type of contactor? How rapidly does it operate & release?
 
I have seen contactors that were originally 2 no + 2nc
changed for 3no +1nc or 4no etc, you get the idea.
can have some very strange effects on machine opperation
 
maybe the first coil contactor is providing current to a latching contact which brings in the second coil has developed a fault
 
there are so many ways the 2 contactors could interact with each other it can only be speculation or suggestions of what "may be wrong" some more info from the op would be great.
 
The OP does say specifically at the beginning that the coils are wired in parallel, i.e they should both energise and release at the same time regardless of anything else. This then suggests one coil is faulty or the wrong type, but he claims to have substituted them.

I recently had a head-scratcher where I had made a similar assumption that two relay coils were paralleled. They looked like it and tested like it, but when I picked the wiring loom apart it turned out they were not, there was a contact elsewhere in series with one of them that sometimes opened when I was not looking.
 
New posts

Reply to Problem with contactors wired in parallel in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
601
Having to wire around a messed up output for a month or so. Some sort of program corruption is keeping the central lubrication system from...
Replies
3
Views
877
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
876
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
625
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top