Search the forum,

Discuss What is wrong with bonding plastic water pipes and plastic gas pipes ? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal)

Would I be in wrong if I have earthed the plastic gas pipes ?
Can someone point me in right direction in on site guide if it’s wrong and why it’s wrong ?
 
I think you need to elaborate because as above you can't earth something that is all insulated.
 
Last edited:
My best guess is that he's asking if there's any harm been done if he's bonded the internal pipework at a point that is copper even though it enters in plastic.
The simple answer is no, no harm has been done.
 
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal)

Would I be in wrong if I have earthed the plastic gas pipes ?
Can someone point me in right direction in on site guide if it’s wrong and why it’s wrong ?
You'd be wasting your customers time and money.

You also have to be careful as, if you're recommending this work when it is unnecessary, you may be acting fraudulently.
 
My best guess is that he's asking if there's any harm been done if he's bonded the internal pipework at a point that is copper even though it enters in plastic.
The simple answer is no, no harm has been done.
This is exactly what I mean , so there’s no problem with that ?
 
This is what I don’t understand, can you explain this more please

In the event of a fault to earth, the copper pipe would be raised to the same potential.
Agreed. But that rather assumes the copper pipework is completely insulated already. A combi boiler, an immersion heater, a gas hob with electric ignition etc etc will often create a parallel path between the CPC bar and the pipes.
While it shouldn’t be consciously done, IMHO a mistake in this area doesn’t make an installation inherently dangerous. It’s not as if we get called in every time a copper water main is replaced with MPDE.
(Of course one would also hope that ADS /fault protection would clear an earth fault quickly in the first place)
 
It's absolutely pointless. Waste of time and money.
I don't think anyone is arguing that point. The point he was getting at is whether he's made anything excessively dangerous by bonding some copper pipe when there was a plastic incomer.
Many gas fitters like to bond between every single pipe entering a boiler (even though the boiler itself conducts between them all) and what he did is no more dangerous than what they routinely do.
 
Agreed. But that rather assumes the copper pipework is completely insulated already. A combi boiler, an immersion heater, a gas hob with electric ignition etc etc will often create a parallel path between the CPC bar and the pipes.
While it shouldn’t be consciously done, IMHO a mistake in this area doesn’t make an installation inherently dangerous. It’s not as if we get called in every time a copper water main is replaced with MPDE.
(Of course one would also hope that ADS /fault protection would clear an earth fault quickly in the first place)
I just wanna know if I have bonded
Agreed. But that rather assumes the copper pipework is completely insulated already. A combi boiler, an immersion heater, a gas hob with electric ignition etc etc will often create a parallel path between the CPC bar and the pipes.
While it shouldn’t be consciously done, IMHO a mistake in this area doesn’t make an installation inherently dangerous. It’s not as if we get called in every time a copper water main is replaced with MPDE.
(Of course one would also hope that ADS /fault protection would clear an earth fault quickly in the first place)
I just wanna know if I have bonded the internal pipework at a point that is copper even though it enters in plastic is there a problem ? If there is why is there problem ?
Does on site guide mention this ?
 
I just wanna know if I have bonded the internal pipework at a point that is copper even though it enters in plastic is there a problem ? If there is why is there problem ?
I would say don't lose sleep over it. It's the same situation as if the water supplier changed the pipe to plastic.
We don't try and create extra earthed exposed conductive parts within a property, which you may have done. But there are plenty of other things that may have been earthing the pipes anyway, making it unlikely you provided the only earth connection.

A convoluted example of it being a problem would be if the earthing was TT, and for whatever reason the RCD providing fault protection didn't work. Then if (for example) a toaster had a fault where the casing became live, everything connected to earth in the house would also become live. If pipes had been bonded, they would become live too. So in this extreme (and unlikely) set of circumstances bonding the pipes when they didn't need bonding might have increased the number of surfaces in the house that are live.

Does on site guide mention this ?
The on site guide tells you what needs bonding. It doesn't tell you why you shouldn't bond something and the consequences if you do.
I suspect you are over-worrying about this. Maybe better to just focus on not doing it again?
 
Tested internal pipework as a matter of routine on a refurb that had had a new plastic water pipe installed.
Pipe work was found to be very low resistance to earth (MET).
Subsequently found a pipe (iron) had previously been installed below ground to an remote building.
Despite incoming main being plastic and the OSG indicating otherwise the internal pipework required bonding!
Always worth double checking!
 
That’s why it’s worded “extraneous” pipe rather than incoming.
Example there of a metallic outgoing pipe… still extraneous, requires bonding.
Incoming or outgoing. Doesn’t matter.

Plumbers don’t see that… they just assume incoming pipe, needs bonded.
 

Reply to What is wrong with bonding plastic water pipes and plastic gas pipes ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
974
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
344
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top