Search the forum,

Discuss When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

Loose connection

IMG_3390.JPG
IMG_3391.JPG
 
I’ve posted it before but this is what happens when you put 230V through a 110V coil. The coil voltage was applied whenever the machine control was on, so it would easily be sitting at the over voltage for 8 to 10 hours a day. I think it lasted three days before failing.

Physically the contactor looked fine, but you couldn’t manually push the contacts together like you should be able to.

Always always always check the coil voltage as well as the contactor rating, don’t just rummage around the parts cupboard for something that looks similar!

DF0AC416-6165-4190-A808-8FD9EB3F736F.jpeg


CFE8ACC6-8B4F-46D2-A96B-0CB9022D4DA5.jpeg
 
That's always worked for me. Mention smoke, and they're on site within the hour.
Only had to call out the DNO once when <whistles innocently> I managed to blow the main fuse. As there was no smoke, I was told "within 3 hours". But they refused to take my number - why would they, after all I'm on site; but they did insist on getting the householder's number (which they checked against their records) - so of course they contacted the householder who was at work.
DNO said "our engineer attended but there was nobody there" - we replied "oh no he didn't". They did manage to get him to go back, and then it was "he's standing outside the front door" - "oh no he isn't !"
Yup, he was at the wrong address. It's one of those places where the address can be confusing if you omit part of it - like "5 Greenfield, Whitegate, Anytown"; he was stood outside 5 Whitegate.
I have never had to play with an electric welder (other than a hour or two training as a student) so I would assume the high current secondary is not earthed to avoid a direct burn-out of the welder's earth. Or is it?

So was it two metal objects linked via conduit/CPC, and the welder's clamp was on one and the electrode arcing to the other?
There are a number of possibilities.
There's a brand of oil filled welders (Pickhill Bantam*) that I recall as being popular with farmers - I recall we had one at a farm I worked on as a lad, and a friend's farm has one - which have bare windings sat in a metal box full of oil. Apparently, if mishandled badly enough, the windings can distort and touch the case or each other. Thinking back, I can recall doing some welding and finding the gate I was working on had a bit of a tingle to it - at least we were wearing rubber wellies ! No RCDs back then.
Some might have the secondary connected to the supply earth as a safety feature if there isn't considered sufficient isolation. Then if someone decides that a big metal table should be earthed (either as a safety feature or just because it's bolted to some structural steelwork) then you've an alternative path separate to the welder earth.

* Dunno why it was called Bantam - it certainly wasn't Bantam in weight, they're 'kin heavy b'stards.
 
They were a bullet proof welder! I learned to run beads on one that my dad still has when I was about 9 years old (ahem 1987?)! Them and the old Oxford units, still plenty about in operation today testament to how good they were/are!
 
Hello, I wanna say that one of the biggest causes of frequent circuit breaker tripping is the overloading of power boards. Most homes and apartments, even newer ones, don’t have enough power points to cater to, for example, a complete home entertainment unit setup. If circuit breakers in your home are tripping frequently, it could be down to circuit overload.

It does make sense that over-current protective devices can be tripped by excess current draw I suppose.
 
But considering a typical setup is one or more ring finals, fed by a 32A MCB - so capable of a continuous (almost) 8kW. Even the most extravagant home entertainment system isn't going to get near 1kW.
I doubt that many homes suffer from frequent over-current trips.
 
I realise these pictures aren't as spectacular as the others but they do show how powerful 230V can be. Plus it's a very real outcome if safe isolation isn't adhered to.

If a L-N or L-E short at 230v can take even a little chunk out of steel alloy, hardened with vanadium, then I hate to think what it would do to a persons hand/arm holding a pair of non VDE pliers.

These are my (now spare) side cutters after I cut through a live cable some years ago (whilst my mind was busy elsewhere, thinking about a difficult relationship with a gorgeous yet crazy woman.). We must keep our minds on the job!

View attachment 84131 View attachment 84132
I have a pair of those wire strippers.

They started life as a £45 PAIR OF Klein side cutters and lasted about an hour and forty-five minutes.

I bought them off a trade counter while I was picking up a length of MT2 to stick an extra socket in an office.

The existing trunking ran just below the ceiling so it was an easy case of pulling a leg out of one socket, dropping it into the new and running a new leg back to the old socket.

What could possibly go wrong?

So pulled out my virgin side cutters out to cut out a notch for the new drop and.....bang.

Yep there was a 1.5 laying flat in the bottom of the trunking that I didn't see on account of not being attentive enough to get my lazy arse up and have a look.

In fairness to myself it was the flattest piece of cable I've ever seen, or not in this case, in trunking. It's like the spark ironed it.

Lessons were learnt and new procedures were put in place.
 
I realise these pictures aren't as spectacular as the others but they do show how powerful 230V can be. Plus it's a very real outcome if safe isolation isn't adhered to.

If a L-N or L-E short at 230v can take even a little chunk out of steel alloy, hardened with vanadium, then I hate to think what it would do to a persons hand/arm holding a pair of non VDE pliers.

These are my (now spare) side cutters after I cut through a live cable some years ago (whilst my mind was busy elsewhere, thinking about a difficult relationship with a gorgeous yet crazy woman.). We must keep our minds on the job!

View attachment 84131 View attachment 84132
Most sparks have or have had cutters to compare, I’d wager.
Regarding the short circuit cutting with uninsulated tools, it’s not the same short circuit current via your body (load). Nasty and dangerous, I know, but it’s not going to blow a hole in you. The arc from the metal tool is a real problem, also.
 
I realise these pictures aren't as spectacular as the others but they do show how powerful 230V can be. Plus it's a very real outcome if safe isolation isn't adhered to.

If a L-N or L-E short at 230v can take even a little chunk out of steel alloy, hardened with vanadium, then I hate to think what it would do to a persons hand/arm holding a pair of non VDE pliers.

These are my (now spare) side cutters after I cut through a live cable some years ago (whilst my mind was busy elsewhere, thinking about a difficult relationship with a gorgeous yet crazy woman.). We must keep our minds on the job!

View attachment 84131 View attachment 84132
I'll wager that all the sparks here have converted side cutters to wire strippers!
Since I did my second ones I've kept a new pair in the bag hoping I'll never have to take them off the card!
 
I'll wager that all the sparks here have converted side cutters to wire strippers!
Since I did my second ones I've kept a new pair in the bag hoping I'll never have to take them off the card!
Most will not admit to it.

personally, of course I have never done it.
especially not whilst up a ladder and subsequently scaring the brown stuff out of my rear end.
Pity that I have NEVER had that learning experience.

now where did I leave my pet unicorn?
 
I have never done it, I especially didn't do it when I was working on a 50a sub main in a gunsmiths, through a 10mm twin and earth with croppers, and it didn't blow the stripping notch clean off them and splatter molten copper all over! No not at all, and I didn't scare myself and half the people who were in there who thought it was a live round going off and all ducked in sync!😁
 
Got a phone call earlier this week. Here is a brief synopsis to explain the pics

Customer - "Hi, occasionally when I use my tumble drier there is a strange smell from near the plug and it sometimes trips the electric"

Me - "Sounds like a faulty drier, if you unplug the drier does anything else cause the electrics to trip?"

Customer - "No, just the drier and it is getting more frequent"

Me - "Ok, unplug the drier and don't use it. I will be with you on Friday morning (4 days from the call)

Turns up on Friday morning to find they had still been using the drier and it had decided to let go. The madness continued when I found they were still using the extension lead it blew in! Not anymore after I cut the plugs off both.

IMG_1929.jpeg
IMG_1930.jpeg
IMG_1931.jpeg
 
unplug the drier and don't use it. I will be with you on Friday morning (4 days from the call)

Turns up on Friday morning to find they had still been using the drier
Had a similar one to this, but with a washing machine. Before the few days were up, they had tried to repair it themselves, and the lady of the house had electrocuted herself.
Made more tragic by the fact that the socket would have been RCD protected within a few weeks, and there was a launderette five doors away in the street.
 
You guys have seen this before, but thought it was worth posting again, the smell in the room was a very distinctive fish smell, it comes from running two 3Kw fires off the same double socket, neither the MCB or RCD reacted to the overload, just got very smelly in the room.


Electrical - 1 of 1.jpeg
 
You guys have seen this before, but thought it was worth posting again, the smell in the room was a very distinctive fish smell, it comes from running two 3Kw fires off the same double socket, neither the MCB or RCD reacted to the overload, just got very smelly in the room.


View attachment 93240
That’s quite concerning that neither protective measure reacted to that. 😳

Then again if nothing created a short then it’s a failure of the socket. Especially if it was connected to a 32a MCB as 26a it would be happy with. Guessing the materials in the socket weren’t rated to withstand 26a for that long.
 
The socket was Legrand, but the MCB and feeding RCD where both Hager and both tested out as per the specifications for them, I can only think that the fan and thermostat's for the heaters did not come on at the same time consistently, so an intermittent accumulative overload over a long period.
 
The socket was Legrand, but the MCB and feeding RCD where both Hager and both tested out as per the specifications for them, I can only think that the fan and thermostat's for the heaters did not come on at the same time consistently, so an intermittent accumulative overload over a long period.
The back plate looks a bit corroded, maybe contacts were a bit tarnished as well?

In any case a 30% overload (26A on 20A rating) is not likely to trip a MCB but would definitely be considered unacceptable design practice. I guess the approval of double sockets was kind of based on the assumption you would not have two max loads on the same one...
 
The corrosion is quite normal on the ground floor of an old French farm house, no DPC or DPM so walls are always damp, if does not seem to bother the French,

Believe it or not they where not on each socket, but supplied off an extension lead onto lefthand outlet, oh can I say receptacle. 😎
 
Got a call out yesterday afternoon. Told electrics had tripped, turned back on and keeps tripping every few minutes so could I come and check as had no power to sockets, kitchen and half the house.

Arrived to find the following:

95F591D5-0ADF-44D3-9260-4482BB9580F2.jpeg
1E579835-39E6-4EA0-8905-E83F0A81DC28.jpeg
6EE183AD-F973-4447-AEC8-6A8E29CF3D32.jpeg


Basically the far right breaker was a 50A supply to a second DB for one half of the house (big old farmhouse) which includes a 10.5kw shower, sockets, immersion and lights. Also 2 x 32a socket circuits (one of which was the kitchen) a 20a socket circuit and 16a second immersion.

All hanging off a 63a RCD and the board had never been checked in the 18yrs since it was installed.

So I managed to give them some power back. But told them they need a new board now asap and a full EICR doing, as I wouldn’t change a board without doing it anyway (especially not on house where I’ve been called to a melted board) and investigation was needed to check why that 50A breaker had obviously also overheating given the melted plastic around the busbar connection.
 
The Berlin Wall fell in ‘89 I think… all thanks to knight Rider himself, David Hasselhoff.
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.
 
One of my regrets was not going to the Pink Floyd concert in Berlin to mark that.

There was a minibus going from Dundee arranged by Groucho's (closed now, was 2nd hand record shop and outlet for local gig tickets) but various friend could'nd be bothered and I gave up on the idea.

You'd need to go for a week just to listen to one Pink Floyd song though!!
 
I remember groucho’s!

The nightlife was varied when I lived up there.
No1’s, Deacon Brodies, O’Neills… student union, of course.
Mardi gras, fat sams, de’stihls….

That all stopped when we moved to the posh end of Carnoustie
 

Reply to When electrics go wrong!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi everyone, Lets get the s#1t stirring out of the way straight up... Yes I'm a sparkie, and a good one, but for all you Brits, I was trained...
Replies
8
Views
5K
V
And the importance of being able to read them. This is a subject that really concerns me with the apprentices where I work and the management...
Replies
36
Views
13K
cranedude
C
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock