Hello everyone I'm Chris. I am taking the 2391 in February. This question is from the c&g main site under 2391 sample questions. Continuity of a ring final circuit has been tested as part of an initial verification of a new primary school. All the socket-outlets are connected directly to the ring. The circuit loop length is 58 m long, wired in 4 mm2 live and 1.5 mm2 cpc flat profile cable. The circuit is protected by a 32 A BS EN 60898 Type B circuit breaker. The installation has a measured Ze of 0.29 Ω. What is the expected value of Zs for this circuit? a) 0.24 Ω b) 0.28 Ω c) 0.53 Ω d) 0.58 Ω The answer is C.
I don't get that answer just wondered if anyone would like to help me as to what i am doing wrong. Many Thanks Chris.
 
approx
58 mts 4mm = 0.25375 ohms
58 mts 1.5mm = 0.67666 ohms
0.25375 + 0.67666 / 4 = 0.232604 then add ZE 0.29 = 0.522 taking 0.53 as the closest

edit just to add the max zs allowed - allowing for 80% and c-diff would calc to 1.09 - approx
Thank you Steve, feel like a total bell now. I was using the 4mm and 1.5mm combined value. 16.71 Makes total sense now. Thank you again.
 
approx
58 mts 4mm = 0.25375 ohms
58 mts 1.5mm = 0.67666 ohms
0.25375 + 0.67666 / 4 = 0.232604 then add ZE 0.29 = 0.522 taking 0.53 as the closest

edit just to add the max zs allowed - allowing for 80% and c-diff would calc to 1.09 - approx
im stuck on this same question how are you working out the ohms for the meterage etc. First time using the regs book and GN3 and completely lost of where to do this calc
 

Reply to Zs C&G 2391 question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
545
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Got a couple of sparkies doing the 2391 exams, now split to make it easier. Seen some of the questions exam sheet… interesting reading for us say...
Replies
5
Views
1K
I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options. Continuity of a ring...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock