Hi, hope someone can help with this, i just bought a new dol starter from my air compressor its a 16 amp starter just need to know what colour wires go where? it has three top connections l1, l2, l3, three lower for supply t1, t2, t3 with a separate pe for yellow/green i take it, so the wires i have left on both supply and to 3 phase motor are brown, blue and red. please help needing to finish a job and cant get an expert out for 2 days!
 
L1, L2, L3 are yor supply. T1,T2,T3 are the load. as long as you connect supply to L's and load to T's. if the motor runs the wrong way, reverse any 2 leads on the load side. ( if tou look closely at the cables i think the brown is actually yellow. so its red to L1, yellow to L2. blue to L3.
 
Supply should be L1 L2 and L3 the load should be T1 T2 and T3

Your supply 3 phase should be Brown L1 Black L2 and Grey L3 if the, does your compressor have a phase failure relay attached for safety?

Most modern compressors for refrigeration and air will have this as it will ensure the motor will not run in reverse.
 
Sorry got the load and supply wrong way round your right, but i only have a brown blue and red wire coming from both supply and load. my old starter was like this l1 = brown l2 = blue l3 = red and same colours going in at the other end. Thanks for your rapid reply by the way.
 
Its an old compressor (1999) its why it has the old uk colours of brown, blue and yellow/green the red was a wire on its own connecting l3 and t3 together
 
I may has confused a few people am i right in thinking i really have a single phase with a protecter on the wall? arghhh sorry probs why i have different colour wires! so would this just wire up s my old starter?
 
Supply should be L1 L2 and L3 the load should be T1 T2 and T3

Your supply 3 phase should be Brown L1 Black L2 and Grey L3 if the, does your compressor have a phase failure relay attached for safety?

Most modern compressors for refrigeration and air will have this as it will ensure the motor will not run in reverse.

Should this not be "will ensure the motor will not run on two phases ?
 
sounds like he's got a single phase motor, now he says L3 is linked to T3!!!!
 
when wiring 1ph dol starters, often the extra poles on the contactor are used by looping the live from the t1 to l2, and you then take your live from t2 and yoyur neautral goes through l3, and t3
 
There might be extraneous wiring as well for off-loader valve etc. Maybe a photo or two would be good.
 

Reply to 3 phase dol starter help in the Australia area at ElectriciansForums.net

Similar Threads

Hi, Trying to wire this 3phase switch as single for a table saw, told I could do this from guy at Haymans, even told 2nd time which wires to...
Replies
2
Views
830
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
524
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top