Search the forum,

Discuss Bus bar chamber with no main isolator in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
0
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical services. I.e if you isolate the building to work on the electrical services then the supply to the sprinkler pumps must remain live.

The only way I can see of doing this is to install the tails from the 200A service fuses to a bus bar chamber, feed the building panel board from that and also feed the sprinkler switch fuse from that. However, I am uncomfortable with the bus bar chamber having no isolation other than the service fuses

Is there an alternative way??
 
It is common place for busbar chambers to be connected direct to the main switch fuse supply into the building, usually then all sorts of different rated switch fuses are coupled to the chamber and then submained from there to the equipment they were installed for, I have seen literally hundreds over the years like this. That said in your case why cannot you fit a panel board direct to the supply switch fuse and then use an MCCB for the new sprinkler system and MCCBs for the distribution boards inside the building? this way when you need to shut down you can isolate all the MCCBs at the panel board and keep just the MCCB for the sprinkler system working? Unless I have mis understood your post this doesn/t seem a difficult issue to solve.

Any Pictures of the existing set up?
 
Busbar chambers are often considered what's often termed as 'fault free zones' as per BS EN 61439 where firstly the primary purpose of protection is to prevent the possibility of short circuit faults and physical injury to personel by construction techniques rather than preventing overload of conductors by OCPD's.

See attached quick guide for some basic info.

The type of circuit you refer to for fire sprinkler booster pumps would usually be specified in detail by the electrical engineer responsible for the building electrical reticulation.
 

Attachments

  • BS EN 61439 guide.pdf
    503.3 KB · Views: 8

Reply to Bus bar chamber with no main isolator in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
994
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
1K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
738
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
804
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
319

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock