Discuss Design current of socket outlets in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
7
I'm doing an design project at college and are onto my cable calcs now and I'm fine with my lighting circuits and the fridge and dishwasher supplys where the load has been stated but I'm confused as what to do about my socket outlets as in the spec there is nothing specified about the socket circuits. How do I work out the design current without knowing the load or do i just leave the box blank or N/A for my socket circuits? I don't know what will be getting plugged in to these circuits at all and there hasn't been anything specified.
 
The thing with sockets is they can all be loaded up under the end user's control, not the circuit designer's control. So when you design the cable and OCPD to feed the sockets you generally have to assume the worst possible case. So whether you go for a RFC in 2.5mm, or radials in 2.5mm or 4mm, etc, you have to make sure the OCPD does not exceed the thermal limit (CCC) of the cable as installed.

However, you also have the end use problem and that is where you have to consider if the available socket are able to power all of what the user can reasonable expect to have fitted. In practice you can allow for a bit of diversity.
 
The thing with sockets is they can all be loaded up under the end user's control, not the circuit designer's control. So when you design the cable and OCPD to feed the sockets you generally have to assume the worst possible case. So whether you go for a RFC in 2.5mm, or radials in 2.5mm or 4mm, etc, you have to make sure the OCPD does not exceed the thermal limit (CCC) of the cable as installed.

However, you also have the end use problem and that is where you have to consider if the available socket are able to power all of what the user can reasonable expect to have fitted. In practice you can allow for a bit of diversity.
ok thanks pal
 

Reply to Design current of socket outlets in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock