Hello all,
Just wondering if my en-suite is wired correctly .
There is a timed extraction fan and bathroom light in there .
There is an isolator switch outside the door. When you turn off the isolator the light stops working too.
Is this correct?
Should the isolator not stop the fan only and allow the light to still come on?
Any help appreciated
 
I don’t know the Irish building regulations, but this is extracted from the Electricians Guide to the Building Regs. I would imagine the applicable Irish regs are similar, Scottish building standards certainly have a similar statement.

“An extractor fan supplied from a lighting circuit for a bathroom without a window should have its own means of isolation; if it does not, the replacement or maintenance of the fan would have to be carried out in the dark.”

No window in the room, the fan needs to be isolated independently from the light. With a window do what you like ?

Changing the operation so the fan isolator doesn’t isolate the light is possible but without knowing how it is wired now I would be guessing on the safest and easiest way of doing it.
 
I don’t know the Irish building regulations, but this is extracted from the Electricians Guide to the Building Regs. I would imagine the applicable Irish regs are similar, Scottish building standards certainly have a similar statement.

“An extractor fan supplied from a lighting circuit for a bathroom without a window should have its own means of isolation; if it does not, the replacement or maintenance of the fan would have to be carried out in the dark.”

No window in the room, the fan needs to be isolated independently from the light. With a window do what you like ?

Changing the operation so the fan isolator doesn’t isolate the light is possible but without knowing how it is wired now I would be guessing on the safest and easiest way of doing it.
Thanks for reply, that makes sense. My en-suite has no windows so I think perhaps it’s not set up correctly.
The isolator has a permanent live going to the fan, then two twin and earths ( one going to light and fan and then one to the shaver outlet)
 

Reply to Fan isolator turns off light too? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock