Search the forum,

Discuss hi everyone , i have a question regarding extra low voltage lighting, in the Lighting Forum area at ElectriciansForums.net

A

Al Capone

the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3 into a 200w driver and 2 x into a 150w driver. all in the same B10 RCBO.
the breaker trips after a few hours.
The 230v armour cable and connections are fine. is that a case of overloading? im confused because if we look in terms of amperes its well over on the 24v side. am I getting my math complety wrong? im sure i migh be sounding very very stupid so i do apologize, but i rather come here for knowledge than die with this question. i hope somebody can help? best wishes
 
Welcome - are you in the UK?
 
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3 into a 200w driver and 2 x into a 150w driver. all in the same B10 RCBO.
the breaker trips after a few hours.
The 230v armour cable and connections are fine. is that a case of overloading? im confused because if we look in terms of amperes its well over on the 24v side. am I getting my math complety wrong? im sure i migh be sounding very very stupid so i do apologize, but i rather come here for knowledge than die with this question. i hope somebody can help? best wishes
8 x 45 watt? then 3 x 45 watt and 2 x 45 watt into 2X 200 watt and 1 X150 watt drivers on a B type MCB? answer this first to confirm load then confirm low voltage fittings, length of run etc and we will be able to chip in
 
Is that 45W & 200W/150W total with every thing on - rather than 45W/channel or 180W total ? I assume the former as 8off 180W would be aot of light !
200 + 200 + 150 is only 550W total, under 3A. It would take something in the order of 20A to maje the B10 trip - and from 3A to 20A would need a really bad power factor.
It's not impossible that the MCB is faulty.
Have you measured the actual current draw ?
 
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3 into a 200w driver and 2 x into a 150w driver. all in the same B10 RCBO.
the breaker trips after a few hours.
The 230v armour cable and connections are fine. is that a case of overloading? im confused because if we look in terms of amperes its well over on the 24v side. am I getting my math complety wrong? im sure i migh be sounding very very stupid so i do apologize, but i rather come here for knowledge than die with this question. i hope somebody can help? best wishes
So you have a total of 550w @ 230v, you shouldn't be challenging a B6 on overload but clamping it can confirm this.

Do you have an earth leakage figure for the floods/drivers? Could it be cumulative working earth leakage.

Failing that it could be a genuine fault causing leakage, a low current clamp meter is a helpful diagnostic tool if not very quantitative.
 

Reply to hi everyone , i have a question regarding extra low voltage lighting, in the Lighting Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top