Currently reading:
IR testing steel conduit on 1st fix?

Discuss IR testing steel conduit on 1st fix? in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi everyone,
I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking.

I recently came across this note about IR testing PRIOR to connection? Can someone just explain how you would test if there was steel conduit and the earthing arrangement being on the other end of a building!?

"It is essential that, when performing an insulation resistance test between live and protective conductors, the protective conductors are connected to the earthing arrangement – that is, to the general mass of the Earth (Regulation 612.3.1 refers).

The connection to Earth is typically achieved by the protective conductor being connected to the main earthing terminal (MET) of the installation, to which the earthing and main protective bonding conductors are also connected, with the MET connected to the earthing arrangement (the distributor’s earthing facility (TN system) or the installation earth electrode (TT system), as applicable)."

Thanks everyone
 
I recently came across this note about IR testing PRIOR to connection? Can someone just explain how you would test if there was steel conduit and the earthing arrangement being on the other end of a building!?
I think there are two things being muddled:
1 - testing when using conductive containment, or MICC cable
2 - final IR testing prior to energising.

For the final testing, the containment would need be fully installed and earthed before you tested.
Then you would test the conductors in turn against the CPC bar or MET, whichever is nearer.

For the intermediate testing, it's a matter of testing all conductors against the containment (or MICC copper outer)

I can't remember what you have to do to pass the exam, but it just seems common sense to me to make sure that any containment that is conductive isn't in contact with any of the conductors.
 

Reply to IR testing steel conduit on 1st fix? in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top