Search the forum,

Discuss Log cabin supplies in the UK Electrical Forum area at ElectriciansForums.net

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V

Load:44.34kW / 80A

Length:190m

Method of Installation direct in ground or in ducting in ground

Cable Size:35mm²
 

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V

Load:44.34kW / 80A

Length:190m

Method of Installation direct in ground or in ducting in ground

Cable Size:35mm²
For volt drop 35.0 in undersized.
 
That calculated from Cleveland cables.
@westward10 point is that is when you have a balanced 3-phase load so only the losses in L1-L3 are a factor as N current is near-zero, if you have just one cabin drawing 80A then you get double the drop (L & N losses) so I'm guessing that is the 8% mention above, but I have not actually checked it.

But as @James points out 80A seems a lot for a wooden cabin! If heater cooker, and shower all on at once maybe, but allowing a bit of diversity, and/or maybe a priority unit cooker/shower would drop the peak load and make the overall drop acceptable.
 
Going up from 35mm to meet drop is going to be expensive. However, it seems 80A draw for a log cabin is quite high, more than many flats have as a supply!

So before sizing the cable to meed VD for 80A on a single phase of the three, are you sure that it really is needing that much?

You don't need to meet VD at the supply OCPD current (though you can find issues with disconnection times if not careful there), nor even at the max permitted by the sum of load OCPDs, but you do need to meet it at all realistic levels of usage. Can you tell us the loads and assumptions you made for the 80A figure?
 

Reply to Log cabin supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
712
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
420
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
534
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
569

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock