Search the forum,

Discuss Mains electric shock from plastic light switch - no fault found by electrician - what next? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch outside a bathroom today.

I turned the switch off with my left hand and got what felt like a mains electric shock through the switch into my left arm. It had the distinctive "throbbing" feel of mains electricity and I felt it mainly through my left arm and left torso. I pulled my arm away and my rib cage still feels a little sore this evening. It was definitely not a static shock. The apartment has an RCD box which didn't trip.

The light switch itself is plastic but has metal screws (although I don't think I touched them). I was wearing slightly damp socks on a thin carpeted floor and my hand was possibly a bit damp from washing my hands in the toilet so my resistance was probably relatively low.

An electrician has now been to visit and said he couldn't find anything wrong and he seemed to suggest I couldn't have had a shock. He very happily touched the switch and it was fine. The wires in the switch appeared to be screwed in properly and the same in the light. The switch is mounted in a metal frame but he couldn't find any live voltage where there shouldn't be with his two-pronged multi meter. He did suggest that a more thorough check of the property and this is being scheduled.

This may be unrelated but in the morning before the shock my wife had noticed that the light in the bathroom controlled by the switch (which is a ceiling mounted multi-LED type) was pulsing on and off approximately once a second when switched off. When turned back on it was working fine but then still pulsing when switched off. The light then started working normally again so we thought it had cleared up.

Any ideas as to what can possibly have caused this? I didn't imagine it but with the electrician not finding anything wrong, I am flummoxed! Note I am handy with a multimeter but only a hobbyist and I normally steer well clear of working on mains electricity.

Pics of the light switch are below:

IMG_20220606_190906570.jpg



IMG_20220606_172154665.jpg
 
Last edited:
There doesn't appear to be a Neutral in the switch box so did the electrician test from the switch screw to another known earth, if not how did he /she establish the metal switch box was not live, other than touching it?

And did he / she investigate whether there's a nail or screw through a live cable in the floor, which you may have made contact with and with earth on the switch screw?

The current required to trip an RCD is at a "painfull level" so there may not have been enough current passing through you to trip it.
 
Not saying this is what has happened, but sometimes the top and bottom lug of the backbox can touch the middle terminal of the screw and make the box, and the fixing screws live.... Taking the switch off has stopped them touching. The lugs can be bent back, or broken off.

This does raise the question of why the RCD didnt trip, and the electrician should have checked its operation. Although, looking at the age of the switches... the lights may not actually be on the RCD.

It may be that the earth wire in the lighting circuit isn't connected to earth anywhere, and this really needs investigated. Hopefully a more in depth check will find out.

A photograph of the circuit breakers in your consumer unit might help there.
 
I hate it when i see bend back lugs top/bottom. I wont ever fit them and given the chance will tear them out. And this also answers why the screw covers can be a good thing !
 
the light in the bathroom controlled by the switch (which is a ceiling mounted multi-LED type) was pulsing on and off approximately once a second when switched off. When turned back on it was working fine but then still pulsing when switched off.

This seems highly significant. Some lights do flash annoyingly when off because they are hyper-sensitive to cable leakage but I assume yours doesn't normally do this. It strongly suggests electrical leakage across the switch for which a likely cause, being outside a bathroom, would be water entering the switch and forming a partially conductive path between the contacts. By the time you touched the switch, the moisture path causing the leakage through to the light seems to have been driven off, but a conductive path might still have existed between at least one contact and the exposed surface of the switch rocker.

As to why the RCD didn't trip during a shock to earth, I can only suggest that if the RCD tested good (did the electrician carry out tests on it?) then the current was probably below the trip threshold. You can still get quite a nasty belt at 20mA, unlikely to affect your heart but it does hurt. The current would have been limited both by the resistance of the moisture track in the switch and by that of the damp-but-not-wet socks / carpet path between you and earth.

Had I been the electrician, I would have immediately carried out a 500V insulation test between all permutations of switch contacts in an attempt to locate any remaining sign of leakage paths within. MK switches of that era can easily be taken apart and reassembled so I would also have inspected internally with the same objective. Obviously as time went on, if moisture was the culprit, all evidence would disappear without trace.
 
A photograph of the circuit breakers in your consumer unit might help there.

Thanks for the reply! A photo of the (ancient) RCD box is below. I can't test it until tomorrow (wife is working late on office VPN and has forbidden me from disconnecting her...) but I will check it out as it's clearly an old unit and has not been tested by me before - although it has tripped a few times in the past.

Is that a metal trim on the floor across the doorway and were you standing on that?

It is indeed a metal trim! Well spotted and perhaps my foot was on it while I touched the switch (not certain) but if so, it could be the answer as to what my feet were conducting into! I will get my multimeter out and do some (careful) tests tomorrow on that strip. Is it worth covering it in something like gaffa tape as a temporary precaution or is that not going to help?

The RCB:

IMG_20220606_200749385.jpg


IMG_20220606_200729369.jpg
 
There doesn't appear to be a Neutral in the switch box so did the electrician test from the switch screw to another known earth, if not how did he /she establish the metal switch box was not live, other than touching it?

The guy was in a bit of a hurry (emergency call out at 5pm probably at the end of a busy day) so he only used a simple multi-meter inside the switch box and also tested by putting his hand in (this made me slightly nervous...). I'm not sure how (if) he checked to another known earth but perhaps he just didn't.

His testing unit was a basic looking multimeter device with two fixed prongs on the end and a series of lights showing live voltage at different marked levels. It beeped to show continuity when he poked it into the switch box (not sure exactly what continuity he was checking) and none of the voltage lights lit up when he touched it onto the switch box. He didn't do any other tests that I could see.

And did he / she investigate whether there's a nail or screw through a live cable in the floor, which you may have made contact with and with earth on the switch screw?

No he didn't check that but it's a good suggestion and I'll have a check to make sure nothing is peeking through. His only comment was that because it was carpet it was impossible for electricity to travel through it. Someone else has suggested perhaps my foot was touching the metal strip between the bathroom and hall carpets - that also sounds like a possibility.

This seems highly significant. Some lights do flash annoyingly when off because they are hyper-sensitive to cable leakage but I assume yours doesn't normally do this. It strongly suggests electrical leakage across the switch for which a likely cause, being outside a bathroom, would be water entering the switch and forming a partially conductive path between the contacts. By the time you touched the switch, the moisture path causing the leakage through to the light seems to have been driven off, but a conductive path might still have existed between at least one contact and the exposed surface of the switch rocker.

As to why the RCD didn't trip during a shock to earth, I can only suggest that if the RCD tested good (did the electrician carry out tests on it?) then the current was probably below the trip threshold. You can still get quite a nasty belt at 20mA, unlikely to affect your heart but it does hurt. The current would have been limited both by the resistance of the moisture track in the switch and by that of the damp-but-not-wet socks / carpet path between you and earth.

Had I been the electrician, I would have immediately carried out a 500V insulation test between all permutations of switch contacts in an attempt to locate any remaining sign of leakage paths within. MK switches of that era can easily be taken apart and reassembled so I would also have inspected internally with the same objective. Obviously as time went on, if moisture was the culprit, all evidence would disappear without trace.
Thanks - this is really helpful. The light does not flash normally. It was so unusual that I filmed it. The RCD wasn't tested but I will check it myself tomorrow. There was no 500v insulation test carried out - I will see if this is possible.

I'm nervous about leaving this unsolved for any period of time. If it is moisture getting inside the switch, what's a good approach to prevent this in future - replace the switch? Or get a full thorough check up carried out?
 
By all means check the RCD with its test button, but I would have expected the electrician to have run a series of tests using his test instrument to analyse its performance. To me that is a no-brainer after a shock-to-earth that did not cause a trip.
 
Sounds like he used a two prong voltage tester, rather than a multimeter…
He still should have had his proper test kit.

It’s a lot of circuits through one RCD, and over time, it can get a little sensitive.
You may want to consider a new consumer unit which will separate the circuits to one RCBO each…. But you’re looking at high hundreds of pounds.

A new switch to eliminate moisture creep, and bend back the top and bottom lugs on the box. Check earth continuity back to board.

And dry your hands before using the switch.
 
I have a customer who had a similar problem. Occasionally, perhaps once or twice a year, the lights controlled by the problem switch would strobe brightly when off, disco style. This would last for maybe a couple of hours, during which time he claimed that touching the switch would give little shocks, which seemed to be from the switch rather than the (metal) switch plate. Eventually the problem would disappear without trace, and the shocks would stop.

They had previously had another electrician come and look at it, and he couldn't find anything wrong. When the problem happened again, the customer called me. By the time I arrived at their house a few hours later, the problem had disappeared again, but he showed me footage on his phone of the strobing.

I tested everything I could think of that could be affecting the lights, but could find nothing wrong. External loop impedances were fine, Zs fine, earthing to the metal switch plates was fine, no loose connections etc, IR for the circuit was fine, IR between switch terminals and the plate was fine, RCD trip times as expected. A total mystery.

Couple of notes: the switch, at the bottom of the stairs, was 2 gang, both being 2 way with other switches. Both sets of lights were affected by the strobing. Property about 20yrs old.
 
Just curious about the led light. Is it in a loft ceiling or is there another floor above this?
If it is in a loft do you have tanks up there?
Did the electrician look inside the light?




Any chance of a picture with the bulbs OP?
 
Last edited:
Just curious about the led light. Is it in a loft ceiling or is there another floor above this?
If it is in a loft do you have tanks up there?
Did the electrician look inside the light?
Any chance of a picture with the bulbs OP?

The bathroom is in a low-rise block of apartments, on the first of four floors. So there are two more floors above it. I don't think there's a leaking boiler above it (the boilers are in a cupboard next to the bathroom). The electrician did look inside the lamp, picture below! I've also had the switch changed, so hopefully that resolves it (picture of the new switch below for completeness :) ).

The lamp:

1654692799646.JPEG


1654692809230.JPEG


The new switch:

1654692811276.JPEG
 
If you feel confident and only if you do please turn off the main switches on your consumer unit and all the circuit breakers. Then take the cover off the lamp and then take the lid off the white terminal box I have pointed to with green arrows. Take a photo of the terminal block inside and post it. You should see the two white wires connected to the blue and brown ones and the green yellow going in connected to the green yellow coming out to the screw terminal. One cannot be sure but it it may be from studying the order of the wires that one white ( the neutral) has been connected to the green yellow coming out and the green yellow going in has been connected to the blue coming out. Such a fault could cause a voltage on the green yellow wires ( the earths/ circuit protection conductors) at the switch and its screws which is high enough to cause an electric shock especially when the light is turned off as you reported. ( The L to E current may be too low to cause the rcd to trip). If you do find the crossed wires I mentioned then do not use the light or its switch. Others will advise you what to do next.

After taking photo replace lid, cover and finally turn main switches and then circuit breakers on again.
 

Attachments

  • 1654692799646.JPEG
    77.5 KB · Views: 60
This leaves me baffled as well.But there will be a logical explanation (When it's eventually found).So if I may ,I,d like to add my twupence worth.

Neither you nor the investigating electrician found any evidence of moisture?That's peculiar because without it ,it's extremely difficult for you to make any kind of contact with switch terminals.The physical gap between a standard light switch terminal and the part of the switch you touch is a minimum of one centimetre.Its impossible to get any kind of shock unless there is a clear moisture pathway.Secondly moisture does,nt appear and disappear in the space of a few hours.Thirdly If any kind of arcing had taken place it would leave visable marks.

I am leaning towards 2 possibilities.
My first step would be to have your earthing checked.A high earth resistance will cause shocks to be felt in any earthed metalwork when certain appliances or plugged in.A fault loop impedance test will quickly establish this.

The second possibility is static from the carpet you stood on.I know you have ruled it out but static can be very unpleasant.Experiencing it while wearing damp socks and having damp hands can can be extremely unpleasant

As regards your strobing lights....I would 't even begin to speculate
 
If you search through the forums, you’ll find stories of not so good LAP or BG products, but usually followed by a positive example of another product by the same.

It’s like a lot of other things… sometimes you get a good design, sometimes not.

I really don’t think this threads issues are down to the choice of fitting, but either installation mistake, or breakdown of much older equipment..
 
T
Good getting a new switch, but did he bend back the unused screw lugs?

Was there any further testing done? There is still the issue that you got a shock, and the RCD didn’t trip.
This is far from resolved.
Thanks for the follow up!! :) He did not bend the unused screw lugs back, should I do this myself? I feel confident that I can safely disconnect the circuit via the RCD/fuse box prior to doing this. He did do a 500v insulation test (as you suggested!) and found no problems. It was about a 1 hour visit in total. He didn't check the RCD (said it would take too long and require dismantling the box...).

I see there are some additional comments including to dismantle the light (which I feel confident enough to do). I really appreciate the feedback on this very friendly and helpful forum. I will take a look at those later today and post back!
 
Neither you nor the investigating electrician found any evidence of moisture?

Re: moisture, there was no sign of moisture inside the switch found by me or the electrician. There was also no sign of arcing damage.

Although now I think about it I do remember seeing a few droplets on the wall high above the switch when the shock happened, which I remember thinking was odd because I don't know where they could have came from - possibly after I washed my hands I might have shaken them before touching the switch leaving drops on the wall and the moisture on my hands itself was sufficient to conduct? Although it's outside the bathroom there's no possible way water could splash off the shower or sink and into the switch because of the angles. The switch is in a cavity wall insulation and we did also have a heavy thunderstorm over the weekend in London so I wondered whether perhaps some moisture might possibly have come in through the roof (although seems unlikely given we are on the first of four floors). I have never seen any other signs of damp or water leaks.
The second possibility is static from the carpet you stood on.I know you have ruled it out but static can be very unpleasant.Experiencing it while wearing damp socks and having damp hands can can be extremely unpleasant

Re: the possiblity of it being static, I am certain it was an AC mains electric shock. I have had a mains shock once years ago from (ironically) the screw on a faulty light switch on a bathroom in a hotel in the middle east, and it has a distinctive throbbing feel and causes throbbing muscle contractions down your arm into your body and is very frightening/unpleasant/painful. This was the same. Static is (in my experience) a much sharper single shock with no throbbing and that only hurts at the contact point - I've played with e.g. a van de graff generator so I do know what a bad static shock feels like :) I would love for it to be a simple static shock explanation but I just don't think it is.
My first step would be to have your earthing checked.A high earth resistance will cause shocks to be felt in any earthed metalwork when certain appliances or plugged in.A fault loop impedance test will quickly establish this.

Thanks! I will check if the electrician did this test and if not will arrange to have it done (I assume I can't do it myself with a simple consumer multimeter unit)?
 
Last edited:
. He did do a 500v insulation test (as you suggested!) and found no problems. It was about a 1 hour visit in total. He didn't check the RCD (said it would take too long and require dismantling the box...).

Odd. Carrying out an insulation test on the circuit (as distinct from the switch) requires taking the front off the board to disconnect the neutral. In which case an RCD test can be done at the same time, taking less than a minute. If he did not test the circuit insulation and did not open the board, then it is still possible to do the RCD test from the switch position albeit with a bit of legwork to visit the board a few times to reset the RCD.
 
What you experienced was not due to static electricity because you were wearing slightly damp socks which would have discharged you.
Good point.That effectively rules static out .I personally would be very confident that "dampness" is also not the issue so looking forward to hearing what results from testing the earthing.
 
jimster99. Good evening Sir.

We are a nosy crowd and really like to know about how problems which have been presented are resolved especially when we have 'skin in the game'.

I noticed that the light fitting has been replaced some time which may be significant. We will not ask by whom. What we really want to know is whether this problem has been first explained and second resolved so that it is safe for all. Unless one understands how you received the shock ie explained by careful investigation it is uncertain whether it could happen again.
 
jimster99. Good evening Sir.

We are a nosy crowd and really like to know about how problems which have been presented are resolved especially when we have 'skin in the game'.

I noticed that the light fitting has been replaced some time which may be significant. We will not ask by whom. What we really want to know is whether this problem has been first explained and second resolved so that it is safe for all. Unless one understands how you received the shock ie explained by careful investigation it is uncertain whether it could happen again.
Hello Marconi! Thanks for the reply (and for your earlier very helpful comment that damp socks = no static!) and don't worry, I have not forgotten about this - I am very keen to avoid future shocks! :)

The light itself had been replaced by somebody before we moved into the property. We don't know who!

The outstanding points appear to be:

(i) checking the RCBO: why didn't it trip? I suspect because I got less than the 30ma trip level. It's worth noting that we had a faulty metal electric kettle a few months ago that DID trip the RCBO a few times, although I suppose it could have been a short circuit tripping the fuse rather than a voltage leak. But this should be checked (which requires taking the front of the RCBO box off).

(ii) Is the internal wiring of the LED itself correct? You asked for a photo of the inside of the light and I will do this when I get a moment (hopefully today). I have the VED screwdrivers ready to go!

(iii) should the internal lugs of the switch be bent back to avoid any future risks of electric shocks? EDIT - yes - and I will do this myself (since the electrician didn't) after cutting the power to the entire property.

(iv) check earth continuity back to board.

(v) The earthing resistance needs to be checked which requires a fault loop impedance test. Is this the same thing as (iv)?

(vi) an insulation test needs to be carried out on the circuit (rather than just the switch) which requires taking the front cover off the RCBO.

Odd. Carrying out an insulation test on the circuit (as distinct from the switch) requires taking the front off the board to disconnect the neutral. In which case an RCD test can be done at the same time, taking less than a minute. If he did not test the circuit insulation and did not open the board, then it is still possible to do the RCD test from the switch position albeit with a bit of legwork to visit the board a few times to reset the RCD.
Hmm, he only checked the switch insulation, not the circuit insulation. Shall i get him to come back and check the circuit as well? He didn't seem to think it was a necessary check but better safe than sorry I think!

There's a remote possibility that it's the floor that is 'live' as a result of a nearby fault, and that the shock came from touching correctly earthed metal in the switch.
I hope this can be ruled out because of the fact that the light itself was intermittlently pulsing when switched off shortly before the shock - too much of a coincidence otherwise.
 
Last edited:
OP…. My suggestion of bending the top and bottom lugs off aren’t a regulation or anything.
Some makes of switches have terminals very close… and are only a problem if you’re taking a switch off the wall without isolating first.. very easy to brush against, then bang. Or click… if it’s on an rcd.

Does your rcd work at all by using the test button?
If it’s been going off with a big enough fault, it maybe not working properly.

Your electrician should have checked this as a matter of course with the right equipment.
It would tell him how fast it trips… has to be under 40ms, and how sensitive it is.
 
If you feel confident and only if you do please turn off the main switches on your consumer unit and all the circuit breakers. Then take the cover off the lamp and then take the lid off the white terminal box I have pointed to with green arrows. Take a photo of the terminal block inside and post it.
I've checked inside the chocolate box, I think it looks like the wires are correctly connected (especially the earth!) Photos attached as requested. Thanks!! :)

1655224312281.JPEG


1655224313473.JPEG


1655224320015.JPEG


1655224322022.JPEG
 
Oh well… the light fitting has been connected properly. It did look like there was a swapped over conductor from the earlier pictures when it still had the lid on the connector.

Make sure you put that lid back on
 
There's something a bit odd about that set up. Live and neutral come from one direction, cable sheath barely entering the fitting, and the cpc comes from a different direction.
 
There's something a bit odd about that set up. Live and neutral come from one direction, cable sheath barely entering the fitting, and the cpc comes from a different direction.

I think L, N and E all come in through the grommet at the bottom side of the connector block don't they?
 
Now I would take the fitting down and examine the wiring underneath.

Jimster99 - if you feel confident first turn off both red main switches and all the circuit breakers and then remove the fitting securing screws while taking the weight of the fitting. Then take a photo of what you see of the wiring above the fitting especially of any connectors. Then carefully put everything back in place, turn on mains switches and the circuit breakers.
 
Now I would take the fitting down and examine the wiring underneath.

Jimster99 - if you feel confident first turn off both red main switches and all the circuit breakers and then remove the fitting securing screws while taking the weight of the fitting. Then take a photo of what you see of the wiring above the fitting especially of any connectors. Then carefully put everything back in place, turn on mains switches and the circuit breakers.
Thanks again Marconi, will do this during the course of the current week!
 
Returning to the possibility that the shock was received from the switch mounting screws, which indicates that the CPC (Earth) conductor of the circuit is not earthed, I was thinking about the severity of the shock received. The most likely cause in that case would seem to me to be loss of connectivity at the consumer unit, rather than a local problem to the bathroom light.

If the CPC is disconnected locally it will float, but absent another fault would not collect enough leakage current from the nearby cables to give a heavy shock. To do that it would likely have been connected to the earth bar in the CU, while the CU was disconnected from main earth and any bonding due to an intermittent connection. Just possibly, loss of connectivity between all or most of the lighting circuit CPC and CU earth bar (which would leave the entire circuit's capacitive leakage accessible at all points) would be enough to deliver a heavy shock.

The above scenarios of intermittent earth connections should be fairly easy to locate by inspection and testing, unless one is very unlucky and there is a concealed intermittent e.g. where a cable is partially cut through, that is at the moment making very good contact and not detectable by unusually high resistance.
 

Reply to Mains electric shock from plastic light switch - no fault found by electrician - what next? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
Replies
46
Views
4K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
931
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock