Mark Coles wrote an article on the introduction of RCD protection to additions & alterations to final circuits.

Thanks Lenny,

That article has confirmed that the RCD S/O and the FCU RCD options that have been suggested are not compliant.

Just what I needed to know.

Thanks also to Richard and Spin, for taking the time with their longish (Long in Spin's case) responses. I was already aware of the main reasons behind RCDs but somehow, the requirement because of concealed cables <50mm had evaporated from my mind, even though I now remember learning it. I guess I'm just getting old :sad:

Cheers
 
I think I will rely on the testing complying with BS7671 rather than fully upgrading an entire ring circuit to BS7671 for a socket addition, that could be a bit expensive. Though I would normally protect the entire circuit with an RCD (if required).
 
Long gone thread maybe , but where do we stand then on replacement of say a broken external back box or broken socket , with regards to RCD protection and or even testing . ????? . Or shall i just put the Gas Safe sticky tape back on , thank her for the cuppa and bugger off .
 
Gas safe sticky tape by the way that was on it when i arrived , whilst she was happily working on her lap top from said socket which happened to suddenly be void of neutral on minor wobble of said skt . ooooh scary , poor Danish student .
 
… It has also been determined that ordinary persons are quite thick, and will now indulge in DIY (especially when there is a bank holiday).
These people will insist on drilling and nailing where any reasonable person would not.

An amusing, informative, and well-written post. Thanks.

I wonder if the inspector would have accepted an RCD spur? I suspect not: even if it might (just) be within the letter of the regulations, surely it isn’t within the spirit. It smacks of a ‘jobsworth’ interpretation: there you go, MY single additional socket complies, but stuff the other twenty sockets on the same RFC.

It does (sort of) make sense that if you have to RCD-protect new or additional work, then you should protect the whole circuit which feeds that work. It could be argued that ALL the final circuit cabling supplying your new socket is now adopted by you and hence falls under current regulations.

But what about existing cabling which is not installed in the ‘safe zones’. It would clearly be absurd to have to tell a client that in order to add a single new socket somewhere you have to change all the cabling in the walls of maybe many rooms, because it doesn’t run in just exactly the right places. Apologies if this is specifically excluded and I’ve missed it.
 
Last edited:
This thread is beginning to remind me of the thread about whether a circuit feeding an a garage/shed should have rcd protection to include the feed to the garage/shed, or just at the garage/shed part of th instaallation.

I think it was generally agreed that the whole circuit including the feed shoulf have rcd protection.
 
An interesting thread and as usual its obvious that we sparkies don't have a consistent view on the regs.

How for gods sake do the people who write the regs expect Joe Public to understand them if they make NO attempt to market and advertise these MOST COMMON situations. Its left to us to try and get things done to the regs and then the bloke down the pub comes and does what the client wants ignoring the regs all together.

Rant over.

exactly murdoch, the regulations are written in a law way and the only way us sparks can understand them properly is to go to university and get a degree in law!, surely the regs has to start being written in plain language for all sparks to understand if all sparks new the regs they wouldnt want to be jumping on forum sites explaining things to other sparks to give them the correct terminology.
 
This thread is beginning to remind me of the thread about whether a circuit feeding an a garage/shed should have rcd protection to include the feed to the garage/shed, or just at the garage/shed part of th instaallation.

I think it was generally agreed that the whole circuit including the feed shoulf have rcd protection.

that depends!!. lol (only joking or there again?)
 
In the 1st amendment to the regs there are proposals that on a MEIWC the use of RCD can be omitted when the designer deems it is not neccessary to fit one, but that is in the future, if it is included, which it still may not.

just out of curiousity i remember reading about this when the 1st ammendment draft was written, but it may sound like a daft question, i take it that this part of the 1st amendament draft never be came part of the of the new ammendment ? as i cannot see anything relation to this in the regs


thanks
 
Last edited by a moderator:
no.. the idea was scrapped because somebody at the IET suggested that it was common sense.
 
This thread is beginning to remind me of the thread about whether a circuit feeding an a garage/shed should have rcd protection to include the feed to the garage/shed, or just at the garage/shed part of th instaallation.

I think it was generally agreed that the whole circuit including the feed shoulf have rcd protection.
Rather unlikely, as that would not strictly comply with the Regulations requiring minimum inconvenience.
 
Yes it is so why resurrect it?

Try using the search facility and read first before asking questions that have been answered ad nauseam.

You have a valid point Tony but had this member not posted in this thread then I probably wouldn't have had the pleasure of reading it. Very interesting points raised throughout :thumbsup
 

Reply to Minor Works Certificate – Details of Departures from BS7671? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
1K
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
671
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
962
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
905
Hi everyone, I’m brand new to the site and hope everyone is doing well. My question is this: I have a 2365 level 2 diploma and have been doing...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock