Discuss Non type-tested parts in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,156
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion.


My particular situation on a job, all I’m doing is adding to an rfc. Moving a couple of sockets off the skirting board, adding a fcu up to a switch, then wall lights.
The present board is a Memera 2000. Mainswitch and circuit breakers. No rcd on any circuit. Have advised and priced for a replacement full RCBO board as a future job….

But in the meantime, I’ve got to add rcd protection to the circuit I’m working on.
Why are Eaton (MEM) rcbo’s so much more expensive than anyone else?

Other manufactures will physically fit the space and busbar shape… whether Hager, proteus, whatever… I haven’t tried any because I am fitting the Eaton one…. But if it can be done without cutting the front cover to make it fit, or it creating a IP issue…. surely fitting any make of rcbo is better than none at all?
 
I see your financial pain here:
At that sort of price a garage CU style of DIN box for an RCD added to a single RFC's MCB would be my solution, not pretty but if a stop-gap prior to new CU then quite OK.
 
Can you not still get the RCD pods that fit onto those mcb's?
They were available but about £50 ish, better than the kempston prices for a new rcbo!

Edit. Yup here

Or new ouch!
 
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion.


My particular situation on a job, all I’m doing is adding to an rfc. Moving a couple of sockets off the skirting board, adding a fcu up to a switch, then wall lights.
The present board is a Memera 2000. Mainswitch and circuit breakers. No rcd on any circuit. Have advised and priced for a replacement full RCBO board as a future job….

But in the meantime, I’ve got to add rcd protection to the circuit I’m working on.
Why are Eaton (MEM) rcbo’s so much more expensive than anyone else?

Other manufactures will physically fit the space and busbar shape… whether Hager, proteus, whatever… I haven’t tried any because I am fitting the Eaton one…. But if it can be done without cutting the front cover to make it fit, or it creating a IP issue…. surely fitting any make of rcbo is better than none at all?
The problem I found is that the fingers of the busbar on some of those memera boards are too wide for other MCBs, so you have to grind it down to fit. If you do that, then IIRC, Wylex NHX MCBs are the closest fit that I found, so I would expect the equivalent wylex RCBO would go in okay. All of the other brand MCBs I've seen shoe-horned into memera 2000 boards have not been a good fit, with the cover cut out to make way.

I avoid doing this sort of thing these days, except occasionally for emergency call outs, where there's no other way of restoring power at the time.
 
I’ve told the customer the price of a new Eaton RCBO, and the benefits of changing the entire board.
Wholesalers around me don’t even have one in stock.

Space is limited to cram in another make of rcd in a small enclosure, just for this one circuit.
Even the board that is there is on its side.

IMG_5368.jpeg

Weird thing is, If another customer accepts my price, I’ll be taking out an MEM split board in a week or two. With a mainswitch rcd that I feasibly could put into this board.

But that’s another issue. One rcd for 9 circuits.
 

Reply to Non type-tested parts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
4K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
There are 2 inverters feeding into a dorman smith C16 rcbo , every time I visit this site (communal area power) it has tripped. it switches on...
Replies
13
Views
2K
Hi all. This is my first post on here so hopefully some of you will be able to suggest something other than my ideas. Worked as a spark for 19...
Replies
16
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock