Search the forum,

Discuss why would i get 0.00 on Ring Final for R1+RN? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite r1's+rn's for figure of 8 joined in connector blocks. set up Kewtech KT63 multifunction tester nulled leads and plug adapter and tested at sockets at got a reading of 0.00? Any advice on why this might be would be greatly appreciated and enhance my understanding
 
Should have got 0.4 so one must assume there is a dead short between E-N. Have you tried testing with probes directly onto the terminals in socket? Maybe something plugged in still?
 
Last edited:
Try nulling leads again, or try without nulling.
It’s difficult to null a plug adaptor and I’m wondering if something happened.
Is R1+R2 ok?
 
Thank you for reply I'm going back 2moro to look into it properly when kids at school, so i can take sockets off and carry out a proper test and inspection. will report back if i still have issues or if i resolve problem, thank you again for reply much appreciated
 

Reply to why would i get 0.00 on Ring Final for R1+RN? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top