What about medical ? Emergency lighting, Alarms ?.
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
 
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !

If you don't mind my asking - what edition of BS7671 are you referencing?

The problem for electricians is that, while many domestic installations may not benefit much from the addition of surge protection, its omission is no longer a matter that can be settled by a customer simply declining the option and now requires a risk assessment. A comprehensive risk assessment takes a significant amount of time, for which the designer will receive no compensation, whereas inclusion of surge protection adds minimal cost to an installation. If you were designing installations, would you take the time to write up a risk assessment for every individual, in many cases finding yourself unable to remove the requirement of surge protection, or would you include it as part of the specification and save yourself considerable hours of unpaid work?
 
If you don't mind my asking - what edition of BS7671 are you referencing?

The problem for electricians is that, while many domestic installations may not benefit much from the addition of surge protection, its omission is no longer a matter that can be settled by a customer simply declining the option and now requires a risk assessment. A comprehensive risk assessment takes a significant amount of time, for which the designer will receive no compensation, whereas inclusion of surge protection adds minimal cost to an installation. If you were designing installations, would you take the time to write up a risk assessment for every individual, in many cases finding yourself unable to remove the requirement of surge protection, or would you include it as part of the specification and save yourself considerable hours of unpaid work?
Such a risk assessment is super easy and super quick.
 
Such a risk assessment is super easy and super quick.

I can provide a risk assessment for anything within minutes, but producing one tailored to a particular installation that meets regulatory requirements and would stand up to legal scrutiny is another proposition entirely.

You didn't mention which edition of BS7671 you have referenced in previous comments.
 
443.4.1 suggests options still exist, although limited.

It would be easy to take certain regulatory statements at face value and conclude that opinion of homeowner absolves designer of any responsibility, but 534.1 would also need to be considered and homeowner's thoughts on that are of no relevance.

GN1 also provides advice on this matter, but I don't have a current copy of it

I asked specifically what @slartybartfast was using as basis for their opinions as I suspect it is (now superseded) blue book.

I commissioned a board this evening in a newly rewired property and the homeowner expressed no opinion on fitment of SPD as I didn't ask for their thoughts on the matter. Difference in price between a main switch board and this main switch board with SPD (+ additional MCB) was £25+vat. If those few pounds had been a deal breaker, I suspect there were many other aspects of my quote that would have been more of a problem.
 
If, as should be done, a Hazard Analysis is carried out first and concludes that the Hazard does not exist or is of a very low consequence then a Risk Assessment does not have to be carried out.
 
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
Placing a surge suppressor in front of the UPS isolates it and its connected equipment from major surge events. The IEEE Standard Section 9.11 states that networked SPD protection is needed and describes protecting a UPS with SPDs
 
If, as should be done, a Hazard Analysis is carried out first and concludes that the Hazard does not exist or is of a very low consequence then a Risk Assessment does not have to be carried out.
What's the difference between a Hazard analysis and a risk assessment when dealing with this scenario.
 
Last edited:
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
There is no argument it's a requirement.

And even if the owner declares that surge protection isn't required, then the equipment still has to comply with the rated impulse voltage.
And would need to check that the data, signal, and telecom lines require protection to preserve lighting protection Zones LPZ concept 443.1.1, 534.1
 
Last edited:

Reply to Are all EV charge point installers this bad? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top