Discuss 6 swipe main shut off - overload code? in the DIY Electrical Advice area at ElectriciansForums.net

d64b2024

DIY
Reaction score
0
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6 slots (I guess 12) with 5 double breakers currently. One breaker is 90 amps which feeds our interior panel which has lights, cook top, A/C condensing unit, receptacles, etc - the other 4 are A/C heater (50), pump (20), water heater (30), and double oven (50). There is no master breaker or main service disconnect other than these 5 current breakers on the 200 amp service. The breakers add up to 240 amps - so if they all peaked is there an issue or does an 80% rule follow or does new (current) code allow for this? I looked at a new construction across the street and it had 210 amps worth of breakers and it's brand new. My question is can we add another interior sub panel and occupy the 6th breaker with a 60 or 80 amp breaker (taking the total to 300 or 320 amps)? What is the max amps these breakers can add up to? Is there a requirement in the code? As mentioned it seems as though new construction is going beyond the 200 amp service but I don't know if the acceptable rule is a certain percentage or they're doing a load calc on all the devices, etc.... any help is appreciated!
 
TL;DR
What is max total amps of the 6 breaker master shut off rule on 200 amp service?
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6 slots (I guess 12) with 5 double breakers currently. One breaker is 90 amps which feeds our interior panel which has lights, cook top, A/C condensing unit, receptacles, etc - the other 4 are A/C heater (50), pump (20), water heater (30), and double oven (50). There is no master breaker or main service disconnect other than these 5 current breakers on the 200 amp service. The breakers add up to 240 amps - so if they all peaked is there an issue or does an 80% rule follow or does new (current) code allow for this? I looked at a new construction across the street and it had 210 amps worth of breakers and it's brand new. My question is can we add another interior sub panel and occupy the 6th breaker with a 60 or 80 amp breaker (taking the total to 300 or 320 amps)? What is the max amps these breakers can add up to? Is there a requirement in the code? As mentioned it seems as though new construction is going beyond the 200 amp service but I don't know if the acceptable rule is a certain percentage or they're doing a load calc on all the devices, etc.... any help is appreciated!
To start with you have to understand that you are looking at 2 different calculations with the first one being your calculated load which is the size of the breaker and the second is your actual connected load. Having said that all the breakers you named are probably not being used at the same time. Examples are your heat, double stove, water heater etc. yes you could add a sub panel and to answer your other question is that you are required to have a main breaker outside for the fire department to cut all power off in case of a fire.
 

Reply to 6 swipe main shut off - overload code? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
768
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
712
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
870
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
522
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock