Discuss Adding another circuit ! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to a 6.5KW heater that is used prob once a month for 10 min intervals max.

Question: I have a spare 63A RCB + 20A MCB box, Can I take another feed from the input of the 63A isolator to feed that, then that would feed into the next building to feed a compressor, some sockets etc via 4mm2 T&E ?.

cheers
Spike
 

Attachments

  • Heater wiring v1 21.04.24.jpg
    74.7 KB · Views: 31
Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to a 6.5KW heater that is used prob once a month for 10 min intervals max.

Question: I have a spare 63A RCB + 20A MCB box, Can I take another feed from the input of the 63A isolator to feed that, then that would feed into the next building to feed a compressor, some sockets etc via 4mm2 T&E ?.

cheers
Spike
Lots of pictures may help of each item and where the 16mm tails originates along with what else it feeds.
 
Lots of pictures may help of each item and where the 16mm tails originates along with what else it .
To be honest I'm doubting we will reach the threshold of information required to say for certain "yes, this is safe, go ahead". It's not changing a light fitting, it's a very general question about adding distribution circuits, and I don't think we should be signing off the design over the internet.
 
To be honest I'm doubting we will reach the threshold of information required to say for certain "yes, this is safe, go ahead". It's not changing a light fitting, it's a very general question about adding distribution circuits, and I don't think we should be signing off the design over the internet.
Very true, but I wouldn't mind seeing the pics
Previous posts of the OP related to a 3ph TT farm.
:)
 
Last edited:
What I can understand is he wants to come off the supply side of a cu mainswitch, run an swa to another building to feed another cu.

If there is no space to give it an mcb within the board, I would suggest splitting before the first cu with Henley’s, an isolator and fusing the swa down.

The “5 way rcd box” is irrelevant. It only suggests the entire circuit is rcd protected at source and is on a 45A OCPD.
 
I know what you mean, but the 16mm tails could mean 60A supplier fuse, and max demand of the whole lot might be a consideration.
Indeed.

Sounds as though the only extra load is a 20 and a 6 breaker… could just be a light and a socket… or could just as likely be a dozen lights and any number of sockets… but max 26A

The only issue might be during the 10 minutes that the big heater is on.


Reading it again, it also seems like he’s running this new part in t&e…. Which is wholly unsuitable.
 

Reply to Adding another circuit ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
899
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and...
Replies
23
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
The ongoing kitchen refit..... I have chased and fitted 10mm T&E from the cooker outlet to the isolator switch and up into the loft. I have 4...
Replies
4
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock