One issue I am concerned about with AFDDs is that they are effectively small computers.

That means firmware/software and with that comes issues of maintenance/errors/life expectancy due to heat/electronics.

What happens when/if they develop a new and improved version? Will there be a way to update existing units (I suspect not).

What will happen if a new appliance is released that just by coincidence produces a similar 'fingerprint' to the one looked for?

I know the idea is not new, particularly in the US, but I believe that our ones are rather different and therefore still fairly new and untested in wide usage (Are they widely used in other part of the 230V world?)

I doubt I will be fitting them anywhere other than I have to for some time to come, until the technology has proved its usefulness and the price has dropped significantly.

Surely if the belief is that a lot of the problems this will solve are within appliances, the better solution would be to include some sort of AFDD within every appliance. Wonder why the appliance makers and large companies who sit on the regs committee didn't consider that? 🤨
In America you can actually but a double socket or as they call it a duplex receptacle which has built in AFCI capability.
You are recommended to use the AFCI sockets where white goods appliances , hair dryers , fridge freezers and hoovers etc are to be plugged in...
This way then you don't need AFCI at the board just at the individual socket out-let,
 
One issue I am concerned about with AFDDs is that they are effectively small computers.

That means firmware/software and with that comes issues of maintenance/errors/life expectancy due to heat/electronics.

What happens when/if they develop a new and improved version? Will there be a way to update existing units (I suspect not).

What will happen if a new appliance is released that just by coincidence produces a similar 'fingerprint' to the one looked for?

I know the idea is not new, particularly in the US, but I believe that our ones are rather different and therefore still fairly new and untested in wide usage (Are they widely used in other part of the 230V world?)

I doubt I will be fitting them anywhere other than I have to for some time to come, until the technology has proved its usefulness and the price has dropped significantly.

Surely if the belief is that a lot of the problems this will solve are within appliances, the better solution would be to include some sort of AFDD within every appliance. Wonder why the appliance makers and large companies who sit on the regs committee didn't consider that? 🤨
There can be a fire risk of some white goods having their power removed whilst part way through a program.
 
One issue I am concerned about with AFDDs is that they are effectively small computers.

That means firmware/software and with that comes issues of maintenance/errors/life expectancy due to heat/electronics.
This is one of the points I made in an earlier post
What happens if the firmware / software throws a checksum error do they automatically reset as all the AFDD's I've looked at have no indication for it but how often is anyone going to check anyway
When you look at the evolution of the consumer unit years ago convention was to have the higher rated fuses next to the main switch fast forward a decade or three and it is not recommended and you should spread the higher current using circuits across the CU to prevent a build up of heat affecting the RCBO's, AFDD's now are going to add to the heating effect so are we going to need a ventilated CU to reduce the heat build up or a half module gap separating the the circuit devices
What happens when/if they develop a new and improved version? Will there be a way to update existing units (I suspect not).
I mentioned the programmable Hager AFDD's much earlier in this thread but having thought more about it I'm not sure about them, if you have a nuisance trip because an arc signature is detected then how do you evolve the programmed arc signature to eliminate the nuisance trip without missing a real arc fault but we also have the issue of is there an arc fault and how do we verify we haven't before going down the route of reprogramming the AFDD
What will happen if a new appliance is released that just by coincidence produces a similar 'fingerprint' to the one looked for?
That is anyones guess or is that for the PAT brigade to identify during inspections
I know the idea is not new, particularly in the US, but I believe that our ones are rather different and therefore still fairly new and untested in wide usage (Are they widely used in other part of the 230V world?)
If all the reports from across the pond are to be believed the use of AFCI's is not that widespread with many taken out after installation
I doubt I will be fitting them anywhere other than I have to for some time to come, until the technology has proved its usefulness and the price has dropped significantly.
As with a lot of stats in some circumstances it is difficult to prove, people will tell you the introduction of Part P saved lives but within 2 years the regs brought in RCD's on everything so what saved the lives, move on and how many lives has the RCD saved we will never know the true number as it trips it is reset and no one logs the fact it tripped or the circumstances why it tripped.
So how will the technology prove itself, the coarse analysis of fire causes will not produce sufficient evidence IMO to prove their worth and what would the price need to come down to make them an automatic fit like we do with RCBO's
Surely if the belief is that a lot of the problems this will solve are within appliances, the better solution would be to include some sort of AFDD within every appliance. Wonder why the appliance makers and large companies who sit on the regs committee didn't consider that? 🤨
And we come back around to cost and safety which is something that is lost on the appliance manufacturers
 
Last edited:
My conclusion for now - If 15% of fires are being caused by faulty appliances then maybe our advice should simply be that AFDDs are an attempt to bring down that number. The reality is that we won't know if it works for several years.
The analytical team I managed until I retired from the Scottish Fire and Rescue Service were (and are) responsible amongst other things for publishing comparable fire statistics for Scotland.

The stats you kindly quoted are derived from data completed by all fire and rescue services in England, Scotland and Wales on the National Incident Recording System (IRS). The IRS provides some very detailed questions about the source of ignition, item first ignited, fire location, spread of the fire, proportion of the property affected by fire, and so on, but it cannot and does not have the capability of delving into detailed causes that would not be known to the attending crews.

I mention this because knowing that (say) an electrical appliance was the source of ignition tells you very little other than that there was a fire resulting from the use of some form of white goods. The firefighter who records the details on the IRS is recording which item they believe was responsible for the fire and (based on what they found on scene) how it ignited whatever it ignited. The 'which item ignited' can be straightforward when there is a completely destroyed fridge or tumble drier extinguished by the crew sitting in what remains of a kitchen, but the more detailed causal information on why that appliance caught fire is most likely to be ascertained by specialist fire investigators following fatal or major fires. The Beko fridge recall resulted from fire investigation work undertaken (if I remember correctly) by London Fire Brigade, not from analysis of IRS data.

The Beko fridge-freezer fires related to (as I recall) mains spark-suppression capacitors short-circuiting and setting fire to the surrounding casework. I don't know whether or not an AFDD would in any way have stood a chance of detecting the sudden short of the capacitor - the resulting fire started by the shorted capacitor which then spread to the plastic casing is not arc-related at all.

Similarly, the major fires which resulted in the recall of thousands of Whirlpool tumble driers relate to combustion of materials in the drier, not to arcs in its motors or heaters.

The stats quoted are quite correct - but of the 15% of fires the number which may be arc-related is likely to be a small minority. We simply do not know from what is recorded on the IRS, but in the 12 years in which I was involved in this field I can only say that true arc-related fires in Scotland at least were so few that I can't recall any details. That's not to say that AFDDs won't save some lives - only that the Whirlpool fires amongst others would not have been caught by AFDDs, and those dreadful appliance fires have resulted in fatalities.

-Stewart
 

Reply to AFDDs for single-socket circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
0
Views
271
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
896
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock