SiJohn

DIY
Reaction score
0
Hello all,
Just wondering what is involved in changing an existing 2 gang socket to a 4 gang outlet?

Is it a case of using the existing wiring from the 2 gang.

Thanks
 
why not just add another 2 gang alongside? and yes, just spur off existing as long as it's currently on a ring.
 
as long as you only spur off 1 socket (single or double) it complies. more than 1 socket spurred off should be fused down @ 13A.
 
Wiring Rules in the south of Ireland don't permit unfused spurs. That said, rings aren't terribly common there. More likely to be a 20A radial.
 
Wiring Rules in the south of Ireland don't permit unfused spurs. That said, rings aren't terribly common there. More likely to be a 20A radial.
Th
Wiring Rules in the south of Ireland don't permit unfused spurs. That said, rings aren't terribly common there. More likely to be a 20A radial.
Wiring Rules in the south of Ireland don't permit unfused spurs. That said, rings aren't terribly common there. More likely to be a 20A radial.
Thanks everyone for replies. In the end I added a double gang to the circuit and from this I added a spur with 13amp fuse switch . There are two double gang sockets running on this spur. Sobto recap I added three double gangs. Thanks
 

Reply to Changing a 2 gang socket to a 4 gang in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just hoping for a bit of advice. When I travel abroad (Europe, predominantly Spain/Cyprus) I usually take a single travel adaptor and a UK 4...
Replies
2
Views
484
Is there such thing as a 2 Gang flex outlet plate, changing an existing heating system to a nest so no need for the programmer however it is by...
Replies
3
Views
734
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
834
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
692
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock