Has anyone got experience terminating steel conduit from 1935 (so likely imperial measurements) into a new metal enclosure? This was the work of the previous electrician to touch the board and I'd like to get a far better fixing this time around. No chance of a re-wire and the IR readings are all good.
Screenshot 2024-03-21 at 21.45.44.png
 
In those examples, just remove the female Bush and fit a standard BSCon locknut, then refit the Bush.

Just looks like 3/4 and 5/8 BSCon to me, locknuts are available.

(I would either fit extra washers on the 5/8 - or drill a proper size hole and re-locate if at all possible) just knocking out a 20mm and banging a 16mm (5/8") in there really annoys me!
 
As above make the correct sized entries. In those days two locknuts were fitted, internal and external and tightened on each other then a female bush fitted or just the external locknut tightened back onto the female bush. Both gave very good connections.
 
Last edited:

Reply to Connecting 1930s steel conduit to new CU in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
817
I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all...
Replies
10
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock