Search the forum,

Discuss Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

Not dodgy, but lack of understanding of the requirement for bonding. Plumber was impressed with his work though and even pointed out where he'd scraped off the paint on the pipework!

IMG_1532.jpeg
 
Today's fun. I was only there to change a cracked socket front a quick end of day job, which I did.

As far as I can tell it's TT (found the rod and getting 2 ohms Zs from CPC bar) but can't verify what else is bonded at this point. There's only one earth wire that isn't a CPC coming into the board, so suspect there's a MET somewhere in Narnia.
I didn't want to try a high current test in case there's an upfront RCD in there too!

Also of note is the split load board, so potentially inadequate fault protection for right hand half if parallel paths are removed.
I had to say that I couldn't prove I'd left it in a safe condition and I'd have to return, take the panel off and see what is actually going on.
(The panel is actually about 4 times as tall as shown and extends to the top of the stair well just to help matters)

1684429572723.png


Some photo's pointing my phone in the hole...
1684429747162.png


The earth wire below goes to an old oil pipe not the cut-out btw

1684429784171.png


1684429820980.png
 
As far as I can tell it's TT (found the rod and getting 2 ohms Zs from CPC bar) but can't verify what else is bonded at this point. There's only one earth wire that isn't a CPC coming into the board, so suspect there's a MET somewhere in Narnia.
2 ohms is either a very rubbish TN or a suspiciously good TT result!

Of course if there is a lot of oil pipe or whatever buried in damp ground then 2 ohms is possible, but it feels to me like a lot of buried metal or extraordinarily wet & salty ground.
 
On the theme of plumber. Couple of call outs on Monday.

First one was a tripping boiler. Plumber had the wisdom to put the wireless stat directly under the boiler, which leaked straight into the stat. They’ve also used the earth as a core.

814F7C7D-26D8-45FA-A383-4211A713E924.jpeg


Second one was from a plumber who was trying to wire in a switch for an immersion and also a shower pump. Couldn’t work out why every time they screwed the switch back it tripped.

I politely told them it was their rubbish wiring and they’ve nicked the live so it’s tripping on the back box.

I sorted it all out and tidied it all up.

FFE9BFCC-7721-4DA5-9222-097B637AC7A2.jpeg
 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock