Spotted what’s wrong with the last picture, compression fittings on gas!
Here's mine at home...
TN-S or TN-C-S???
Answers on a postcard :sifone:
Spotted what’s wrong with the last picture, compression fittings on gas!
In pic 1, at the top right hand corner, there's what looks to be a gas Emergency Control Valve & associated pipework which looks to be far too close to the leccy stuff.
(Aye .... aahh knaa it's got nowt to do with earthing etc. aam just showing off)
but if it gives you a good Ra result (Ze for a TT) I would leave unless it causes an issue with the gas incomer. Any thoughts on this?
Good points E54, I also wouldn't pig tail the earth cable. Wonder how long the connection will last exposed to the elements like that?
Just a note: Never pig tail a live conductor, you've basically just made an induction coil.
if in doubt then do a Ze...and a Zpn....if the PFC is the same then you can be pretty certain that you have a TN-C-S....Hi all, since I'm only in my first year of my Level 2 C&G 2365 electrical installations it's always nice to be able to look at different set ups and recognise what they are, I saw the following and wanted to know if this one is a TN-C-S or TN-S install because I was thinking a TN-C-S but it looks like it's connected to the sheath so that makes it a TN-S install???
Thanks all
View attachment 21921
On a TT system an earth electrode (aka earth rod) needs to be installed. The rod needs to be available for inspection and testing, this can be achieved by an earth pit as below.
Any thoughts on this?
like a nest....Just looked back over this thread and should have mentioned that if a rod has an exothermic or brazed welded connection, it doesn't really need or warrant an earth pit enclosure, (but the rod to cable connection should still be protected, say with amalgamating tape) unless it's only for location identification purposes. I would imagine, that in this case it's one of more than one earth rod position, the first having a removable bolted clamp connection for testing purposes.
I'll assume that this rod is a part of an industrial or commercial earthing installation or maybe even a lightning protection system, rather from a domestic installation??
So what do YOU think about them??
What's going on there? It looks like two cables leaving the pole, but three arriving at the house.
Come on Hohmage, what did the DNO say?
Exact wording please!
I found this comment on the IET forum (thanks Archy S): "Up in Scotland as one of the DNOs, CEW or (SEN) is a Continuos earth wire earthing system given to consumers who have an earth loop higher than 0.35 ohms. ie 3 wire single phase system consisting of a phase, neutral and a separate earth. If PME they'd just get a phase and a combined earth/neutral."
How's the earth actually made, and where does it join neutral (if at all).
I'm comparing with our supply, which is the same type of pole mounted 11kV transformer but in our case we're connected by underground split concentric to provide TN-S (DNO called this CEW as well). As explained by the DNO our transformer's neutral on the LV side is connected to an earth cable/rod/spike or something at the foot of the pole.
A previous house, served by overhead 240V, only had L and N overhead with a locally provided earth.
In this case, are they really providing Earth on an overhead cable?
That'd be TNS then. (?)
Further research needed, when I'm totally C[SUB]2[/SUB]H[SUB]5[/SUB]OH free!
"Up in Scotland as one of the DNOs, CEW or (SEN) is a Continuos earth wire earthing system given to consumers who have an earth loop higher than 0.35 ohms."
I'm not sure if it's the same thing he was meaning, but SSE publishes a target of max 0.35 ohms for TNCS, but up to 0.80 for TNS. It doesn't necessarily mean that TNS will be over 0.35 though, ours is 0.29.
You may be misunderstanding me, I'm not an electrician but I have taken a keen interest in our earthing arrangements because of the need to take supplies out to some outbuildings with a lot of extraneous metalwork so I made it my business to get a definitive answer.Hi aesmith, thank you for replies. I am only versed in basic electrics. Can you tell me were I should b looking to answer your question "how's earth made, and whre does it join neutral". I have a basic understanding of the more obvious systems TN-S etc. I could take more pics.