Search the forum,

Discuss Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

Hi aesmith, yes, my main concern is with the safety of the earthing. I was originally concerned that the system was TT or similar, and so the CU required a 100mA RCD. At present it has no RCDs at all. As someone else said, the earthing arrangement that I do have here could deteriorate underground. Similarly with the outbuildings, I wondered if earthing rods were required and am still unclear on that one, because some folk say you can never have too much earthing. If he system here is TN-S, then I should worry less. SSE is installing a new substation couple of miles away from here right now, so I will ask again for someone more technical to visit. Thank you for your help.
 
The three wire is an old way of N→E connection. It moves the LV earth rod away from the MV earth rod.

Hi Tony, thank you for this. However, being a layman (but really wanting to know more about the subject) I don't understand where the HV would be at the house, let alone the earths. Could you point me in the right direction of a simple explanation please? Many thanks.
 
The three wire is an old way of N→E connection. It moves the LV earth rod away from the MV earth rod.

Come on Tony, please explain what CEW is in simple terms, maybe with one of your infamous drawings! (If you're feeling in a generous mood! :) )
I just can't visualise it.
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
OHearthingzones_zps22959b1b.jpg



DNO drawing for ground mounted
Substation_zpscacb0f7a.jpg
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
OHearthingzones_zps22959b1b.jpg



DNO drawing for ground mounted
Substation_zpscacb0f7a.jpg
and when you think about it Tony...its just common sense isn`t it...

differing potentials n all that lot...
 
and i`ll say this as well Tony..

one of the neighbours up until recently had issues with extranious in his house with voltage sitting on it..

then he said one day the DNO came out and were doing something...
ever since then the extranious in his house has been clear....

hmm.....
 
The DNO’s also have another crafty trick with MV OH earthing. You may have seen section switches on OH lines. If you look there will be an earth running from the switch metalwork to the ground. It isn’t a rod, there will be a mat.
The idea is that the ground the operator is standing on is at the same potential as the switch metalwork. Where it gets tricky is approaching the switch, I was taught “the shuffle”. You don’t go striding up to the switch as there could be a ground voltage gradient, you shuffle towards it not putting one foot fully in front of the other.

PS I don’t like MV OH lines.
 
Cows are more sensitive to the gradient effect because of the distance between their legs (this applies to some TV 'celebrities' as well). Luckily most cows don't need to operate MV switchgear - they normally stick the the LV stuff. Daz
 
PS I don’t like MV OH lines.[/QUOTE]

Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!
 
The advantage of having sheep and cattle in the field is you know there’s a ground voltage gradient around the switch. Dead sheep and cows tend to give it away.
 
Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!

If you know there's a fault, supplies gone off etc. Don't go nosing around the MV gear, simple as. If you're that woried, talk to the DNO. If you're on a farm then it's worth a phone call.

Remember I’m talking of fault conditions, not the everyday life of country folk.
 
I think it's a 60's build council semi near Poole, Dorset. It's no longer council though.
I'm not sure how to proceed. I suppose a call to the dno should be the next step.
 
It's a semi-detached house with a pre-paid meter and cut out within the same enclosure (I think!).
The property is some distance from me so I'll ask the client (a friend) for another picture showing the content of the enclosure and when I get it I'll post it here.
 
Deleted... only I haven't worked out how to delete the photos! Help!!
 

Attachments

  • DSC_0123.jpg
    289.9 KB · Views: 113
  • DSC_0125.jpg
    299.2 KB · Views: 102
  • DSC_0126.jpg
    316.2 KB · Views: 103
Last edited:
The incoming cable looks like a split concentric and so will be TN-S. I assume that the G/Y earth cable is the main earth to the remote CU. If in doubt test for TNC-S!!
 
The incoming cable looks like a split concentric and so will be TN-S. I assume that the G/Y earth cable is the main earth to the remote CU. If in doubt test for TNC-S!!

Thanks Eng. Yep, G/Y is the main earthing conductor. I'm sure determining the pfc will reveal.
 
Though it might be that. Don't assume it's 415V because it says it on the side. In a similar way, don't assume it's a 100 amp fuse because it says 100A on the fuse carrier. Daz
 
Though it might be that. Don't assume it's 415V because it says it on the side. In a similar way, don't assume it's a 100 amp fuse because it says 100A on the fuse carrier. Daz

Yeh, sorry, my system went a bit lala for a few minutes. I don't assume anything. Assumptions bite! But point taken...
 
Though it might be that. Don't assume it's 415V because it says it on the side. In a similar way, don't assume it's a 100 amp fuse because it says 100A on the fuse carrier. Daz

Right you are, not to assume.
After obtaining some temporary seals from the DNO I looked inside the carrier and this is what I found.

Brush
30 Amp
60 LR
Certified
440V AC 4
BS88 - 1952
Class 3
Made in England

The print on the fuse had faded so there may be errors in the above info.

The DNO were contacted again and they're sending an engineer to address the issue.
 
Just shows you how long that service fuse has been in place. My parents house only had a 40A service fuse and a 40A meter for donkeys years. Then got updated out of the blue to 60A fuse and 100A meter. Later still, Mechanical meter replaced with digital meter and fuse/tails uprated to 80A/16mm....
 
Just shows you how long that service fuse has been in place. My parents house only had a 40A service fuse and a 40A meter for donkeys years. Then got updated out of the blue to 60A fuse and 100A meter. Later still, Mechanical meter replaced with digital meter and fuse/tails uprated to 80A/16mm....[/QUOTE]

and it held for all that time....


which begs me to ask what the point in this excercise was?
 
Non of your Chinese rubbish!

What happened to Brush Engineering?

I had the misfortune of installing one of their LV panels. Biggest pile of junk I’ve ever come across. So bad I got division engineering involved and we chucked all the outgoing switches away. Replaced them with System 4 gear.
 
What happened to Brush Engineering?

I had the misfortune of installing one of their LV panels. Biggest pile of junk I’ve ever come across. So bad I got division engineering involved and we chucked all the outgoing switches away. Replaced them with System 4 gear.
hmm..

well heres a famous product out of Brush`s loughborough works:

Class_47_'Prince_William'_NRM_Rail_200.jpg

and something from BR Derby....but with Brush electrical plant & gear:

Class_46_D182_at_Grosmont_10th_May_2008.jpg

each gave 30 years of good service...the only issues were with the Sulzer twin bank diesel engines they used
 
I've got a fantastic book, 'Diesel Traction. Manual for Enginemen', 1962, great book.

Also got one for 'Railway Steam Locomotive Enginemen'. More of Geordie's era. :)
 
I've got a fantastic book, 'Diesel Traction. Manual for Enginemen', 1962, great book.

Also got one for 'Railway Steam Locomotive Enginemen'. More of Geordie's era. :)

I have that one and I have "2750 - Legend Of A Locomotive" which is a fictional story about an A3 Class Gresley Pacific named "Papyrus" that I've seen many times written by H.C. Webster. (I think I have some for diesel as well but let's not go there!)

I first stumbled upon it in the school library and was so impressed with it I wanted to nick it!

It's a very rare book and a couple of years ago the idea popped into my head that I would like to read it again but nobody had ever heard of it. Somehow, by fair means or foul, Tidyboiler managed to find a copy for me.

It's so well written with some great drawings that it's possible to learn to drive a Gresley Pacific class from it and that's how at the tender age of 18 I ended up driving this:

P4165255.jpg
 
Just shows you how long that service fuse has been in place. My parents house only had a 40A service fuse and a 40A meter for donkeys years. Then got updated out of the blue to 60A fuse and 100A meter. Later still, Mechanical meter replaced with digital meter and fuse/tails uprated to 80A/16mm....

and it held for all that time....


which begs me to ask what the point in this excercise was?

No idea, no upgrades were ever asked for/requested. Not just my parants house, but the whole estate, street by street!! lol!! Talking about a period from 1952 through to 2005. It was around final year, they changed the meter for a digital one and upgraded the service fuse and the braided VIR 7/064 tails for 16mm....
 
No idea, no upgrades were ever asked for/requested. Not just my parants house, but the whole estate, street by street!! lol!! Talking about a period from 1952 through to 2005. It was around final year, they changed the meter for a digital one and upgraded the service fuse and the braided VIR 7/064 tails for 16mm....
it would have been interesting to have clamped the tails at full demand back then...

and again recently...

compare the results......
 
I have that one and I have "2750 - Legend Of A Locomotive" which is a fictional story about an A3 Class Gresley Pacific named "Papyrus" that I've seen many times written by H.C. Webster. (I think I have some for diesel as well but let's not go there!)

I first stumbled upon it in the school library and was so impressed with it I wanted to nick it!

It's a very rare book and a couple of years ago the idea popped into my head that I would like to read it again but nobody had ever heard of it. Somehow, by fair means or foul, Tidyboiler managed to find a copy for me.

It's so well written with some great drawings that it's possible to learn to drive a Gresley Pacific class from it and that's how at the tender age of 18 I ended up driving this:

P4165255.jpg
theres six of these in existance:

Mallard....a static display in the national railway museum York

Bittern...in steam at southall railway centre

Union of south africa
...in steam at thornton yard

Dominion of canada...a static display at the canadian railway museum

Dwight D eisenhower...a static display at national rail museum green bay wisconsin

Sir nigel gresley...in steam at north york moors railway
 
it would have been interesting to have clamped the tails at full demand back then...

and again recently...

compare the results......

Well i can tell you that while Mum & Dad where living there, hob cooking was always Gas, as was heating and hot water, eg shower!! Though i did install a power shower pump in the latter years... lol!! So it was never really a high usage property, especially after my sister and myself had left the house
 

Reply to Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
578
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top