leebut

-
Reaction score
63
Hi Guys

I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head round, this is going to be in a small supermarket one of these locals etc the existing lighting in the retail area is installed with three banks of three led battens so for ease of description shop left, shop middle and shop right each of these circuits have three LED battens attached to them and each circuit is fed from its own MCB in the DB, I'm guessing these circuits are fed separately at the DB only so that if one bank of lights goes off the retail area is still illuminated by the other two banks of lights.

So my question is how can I wire in an emergency lighting system on to the three circuits so that if any one circuit goes off the emergency lights are activated because the other two circuits would still be live, which would mean the emergency lights wouldn't come on, is there some kind of off the shelf relay system available that would work with this.

Thanks in advance guys


regards


Lee
 
You could use a phase failure relay, they fit on DIN rail and are the size of one module. If any phase goes below a preset value then a contact operates.
 
Do you have BS5266 and experience of emergency lighting design.
Hi

I've done the C&G accredited installer course for fire alarms and emergency lighting with Napit, design of a straight forward single circuit with multiple non maintained lights isn't the issue here, its the three MCB's that are feeding three banks of lights in the retail area.

my initial idea was to connect all three circuits onto one MCB back at the DB the total load for the nine LED battens is no more than three Amps, but the initial designer of the lighting system has set the shop floor area so that if one bank of lights fails then there's two other banks of light so the retails store doesn't have to close.
 
Why would you connect them all to one circuit?
Three circuits with non maintained bulkheads from each through three test facilities.
 

Reply to emergency Lighting installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
678
I've been asked by a client to 'mask off' the green LED charging indictor lamps within several emergency lights fitted within bedrooms on a...
Replies
11
Views
717
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
906
Morning Needing help regarding Ansell AARDRINA/DD1/SM3. I’ve installed 6 in one room, one being an emergency light fitting. All 5 standard...
Replies
15
Views
556
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top