Search the forum,

Discuss First little job on own house - advice in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi,

I am currently studying/training to start a career as an electrician and i have recently finished my C&G Level 2 and currently studying for my Level 3.

In the meantime i want to do a few minor works to my house to keep my practice my practical knowledge/keep things in my head.

My MFT and other bits arrived today, so the first little job is that i want to replace a junction box outside with an outdoor double socket. The set up is:

-New build only 2 years old so everything should be new/up to code (one can hope!)
-A fused connection unit takes a spur in the kitchen of from the downstairs ring final (this ring feeds all downstairs sockets and the central heating), feeds the power to a standalone garage (which has a double socket and a light (on a fused switch)).
-Where the cable comes out of the wall on the back of the house from the fused spur it goes into a junction box attached to the wall, to link to SWA which then runs down the wall and underground, then back up to the standalone garage.

Essentially, i just want to turn this connection on the wall of the house into a double socket.

I want to do it all properly and imagine i am doing it for a customer and issue myself a minor works certificate so i wanted to know how one would go about testing this sort of small job in the real world.

Would you do all applicable tests (continuity, IR, ZS and RCD)? If so, would you do them on the whole circuit or would you do them from the fused spur , with the fuse removed (assuming it would have to be double pole to do this without touching anything in the DB?).

So far my studies haven't really covered specifically what you would do on just a small modification on a spur such as this. I am guessing that to be absolutely sure, it may be better to do the tests involving the whole circuit (though with the IR test i will have to be mindful of anything that might get damaged at 500v so will have to remove thermostats/turn off the isolation switched to the boiler and kitchen applicances etc).

Any advice would be much appreciated as it would be good to know how in the real world an electrician would go about doing the tests on something like this, as i dont want to unnecessarily risk fiddling with more stuff than i really have to.

Many thanks
 
testing wise. I'd only do IR testing Land E joined and then IR test to E. A Zs reading and polarity test, together with RCD test for the RFC would suffice.
 
For the purposes of the MWC, @telectrix has covered anything you might need to do. The only additional would be to check that the fuse in the Fused spur was appropriate (13A in the this case, presumably). You could then put that as the source OPCD for the circuit you are working on.

If you wanted to be particularly thorough, you may want to test the RFC is complete at the fused spur, though that's not essential in this case since you are working only on the cabling after the reduction in fusing.

For the purposes of your work in this case, you could do all testing from the Fused Spur onwards - though RCD and Zs would obviously be testing the existing cabling from the CU.

Not sure if the existing junction box is metal, but if you're replacing it with a plastic external socket you'll need to make sure that the armour of the SWA is correct earthed with banjo clip or suitable earth nut.
 
For the purposes of the MWC, @telectrix has covered anything you might need to do. The only additional would be to check that the fuse in the Fused spur was appropriate (13A in the this case, presumably). You could then put that as the source OPCD for the circuit you are working on.

If you wanted to be particularly thorough, you may want to test the RFC is complete at the fused spur, though that's not essential in this case since you are working only on the cabling after the reduction in fusing.

For the purposes of your work in this case, you could do all testing from the Fused Spur onwards - though RCD and Zs would obviously be testing the existing cabling from the CU.

Not sure if the existing junction box is metal, but if you're replacing it with a plastic external socket you'll need to make sure that the armour of the SWA is correct earthed with banjo clip or suitable earth nut.

Thanks. So it would be acceptable to IR and R1 + R2 continuity on the load side of the fused spur (with fuse out), then do a ZS and RCD with everything reconnected at the new socket? I have all the intial verification figures from the installation certificate etc to use as a reference as well. That would make sense to me, as i would not be changing any of the wiring before the junction box on the spur.

The existing Junction box is plastic and the socket will be plastic, so already as the suitable connection.
 
So, I started to do this today and have hit a stumbling block already. I had assumed that with the house being only 2 years old, that everything would be done properly and up to code. However, upon opening the junction box outside, I found that there is no connection from the swa armour/nut to the CPC. That surely is not correct? I thought that the armour must be linked by a bango/piranha nut etc to the rest of the cpc (at least that is what I was taught during my level 2 unless I have misunderstood something)

Here is a picture.

20210625-150555.jpg


I am therefore assuming that to do this properly, I will need to get a piranha nut, some crimps and a bit of green and yellow cable so I can link the armour properly (I assumed that would all already be there for me to just link it all up in the earth terminal on the socket!)?
 
yous correctin that the steel armour needs to be earthedusing a fly lead ( i would fit a bit of 6.0mm).also, looking at that connector block, there's enough exposed copper conductor to short a bus out.sure you can rectify that. personally I'd use wagos.
 
I come across a lot of swa nowadays with no bango or earthing nut on the armour

are the new breed no longer bothering earthing the armour
 
yous correctin that the steel armour needs to be earthedusing a fly lead ( i would fit a bit of 6.0mm).also, looking at that connector block, there's enough exposed copper conductor to short a bus out.sure you can rectify that. personally I'd use wagos.

Thanks

Any particular reason why the fly lead csa would have to be so large? The csa of the line conductors to the supply of the junction box is 2.5mm, and then the swa from that is 1.5mm.

I was going to use 2.5mm for the fly.
 
I come across a lot of swa nowadays with no bango or earthing nut on the armour

are the new breed no longer bothering earthing the armour

I'm surprised that something like that would have got passed initial verification on something only two years old. I thought that was a pretty big requirement for swa that goes out and underground (ie for the armour to have continuity back to the MET).
 
Thanks

Any particular reason why the fly lead csa would have to be so large? The csa of the line conductors to the supply of the junction box is 2.5mm, and then the swa from that is 1.5mm.

I was going to use 2.5mm for the fly.
you're right. it's just that i always have 6mm Gn/Y on the van but not always 2.5.
 
SWA is only required to have the armour connected at one end (if the armour is not being used as a CPC), as already mentioned, so it may well comply.
However, I always connect the armour at both ends and at every joint, where applicable, just to be sure. I believe most sparks would do the same.
 
SWA is only required to have the armour connected at one end (if the armour is not being used as a CPC), as already mentioned, so it may well comply.
However, I always connect the armour at both ends and at every joint, where applicable, just to be sure. I believe most sparks would do the same.
If it is going to be earthed at one end I would always say it must be the supply end, lower Zs on the armour and less risk of something stupid being done at the load/accessory end.

Like the above example! If the armour is earthed, it is fortuitous by means of the back box and not by any acceptable connection.

To add: I would agree that it should be earthed at both ends if practical, exception usually is a feed to a TT'd building/caravan where the cable is TN and the end is a plastic gland as you are using only L & N and putting in a local rod for the RCD/onwards installation.
 
Last edited:
I think what your 1st home exercise has shown is a Golden Rule you should apply on jobs - test and inspect first before you make any changes.

It might well be the installation broken/unsafe to begin with, and that is a whole extra set of donkey balls to suck when you go to test your own work and find something amiss.
 
I tend to only earth (bango) the supply end , just how I do it…

sometimes I banjo both ends but only when the wind is blowing east
 
Yeh, it is a bit poor isnt it. I thought my criticism may have been unjustified as i thought both ends had to be connected to the cpc. However, then i check the termination at the other end and A. it isnt connected there either and B. the metal back box isnt connected either.


I think what your 1st home exercise has shown is a Golden Rule you should apply on jobs - test and inspect first before you make any changes.

It might well be the installation broken/unsafe to begin with, and that is a whole extra set of donkey balls to suck when you go to test your own work and find something amiss.

You are absolutely right. I shouldn't have assumed that just because it was almost brand new/done a few years ago by a big firm that it was done correctly.

I am glad i took the time to inspect it/ask these questions first.
 
Yeh, it is a bit poor isnt it. I thought my criticism may have been unjustified as i thought both ends had to be connected to the cpc. However, then i check the termination at the other end and A. it isnt connected there either and B. the metal back box isnt connected either.




You are absolutely right. I shouldn't have assumed that just because it was almost brand new/done a few years ago by a big firm that it was done correctly.

I am glad i took the time to inspect it/ask these questions first.
ask questions, you learn. always best. that's what makes a good electrician.
 
You are absolutely right. I shouldn't have assumed that just because it was almost brand new/done a few years ago by a big firm that it was done correctly.
I bought a new build house just over 20 years ago and despite insisting on a test certificate which they seemed reluctant to do, a number of issues where found shortly after moving in that they were called back to sort out and I'm still finding some issues with the electrics now. Over the years I've found taped up cables where they have been damaged most likely by other trades under the floor ,faults in the central heating wiring to name a few
Even doing my own test at the time of moving in I wouldn't have identified some of the issues I've found over the years but you do rely on an assumed quality of workmanship when a lot of the installation is always hidden from view
 
New builds have notoriously sloppy bad wiring , years ago I rented a brand new flat with my girlfriend. It was brand new when we moved in very first occupier. I found about 6 bare connector block joints under the kitchen kickboard when cleaning. I found broken cpcs. I found 1.5mm cable on a 32a mcb. The immersion was wired wrong. The lighting was fed from 2 circuits but both circuits were cross linked so you had to kill both mcbs to actually turn off the power. The test sheets left by the consumer unit were bogus as the number of points served was totally inaccurte.

and so on

these flats were completed in 2008 ish so no excuse for such terrible wiring imo
 
What would generally be the correct way to make sure the opening where the wire from the wall goes into the back of the socket? There isnt a big enough hole for a whole gland and it might be awkward to make one.

Are there any specific fittings for this sort of thing or would simply siliconing the top and sides of the socket once it is done be acceptable (as that means no water could realistically get behind the socket)?

I mean, the junction box there at the moment doesnt have anything extra done to it. The wire literally just comes out of the wall and through a whole in the back of it with no further waterproofing etc. However, judging by their other emissions, i doubt the original installers have done it correctly!
 
To the OP - I don't suppose you have a label on your CU with the company that has the initials 'CE' on it. Your pictures look suspiciously like their 'workmanship' ?
 
What would generally be the correct way to make sure the opening where the wire from the wall goes into the back of the socket? There isnt a big enough hole for a whole gland and it might be awkward to make one.

Are there any specific fittings for this sort of thing or would simply siliconing the top and sides of the socket once it is done be acceptable (as that means no water could realistically get behind the socket)?

I mean, the junction box there at the moment doesnt have anything extra done to it. The wire literally just comes out of the wall and through a whole in the back of it with no further waterproofing etc. However, judging by their other emissions, i doubt the original installers have done it correctly!
The hole on the back looks like it might be a standard cut out 20mm, in which case a standard closed grommet would do the job. Sometimes they come with one.

Otherwise silicone filling that hole would be an acceptable option. Silconing around the socket is also not a bad idea, though not necessary if the hole is correctly sealed.

The box will probably have a space for a drain hole to be drilled on the bottom in one corner, which should also be done - some water may get in whatever you do, so it's best to give it an option to get out.
 
I’d say that once that socket is screwed back, it’s all earthed back through the SWA as it’s a metal back box.
Not something I’d rely on but with two fixed lugs on the back box, would that not technically comply?

If it were my job, I’d add a 2.5mm fly lead on that end though, and for the plastic back box, just swap the lock ring over for one of these and just attach another flylead.
https://www.NoLinkingToThis/p/earth..._WtAJX7X4y5YWR-XzRkaApI9EALw_wcB&gclsrc=aw.ds

Should take you around 10-15 mins.
 
I’d say that once that socket is screwed back, it’s all earthed back through the SWA as it’s a metal back box.
Not something I’d rely on but with two fixed lugs on the back box, would that not technically comply?

If it were my job, I’d add a 2.5mm fly lead on that end though, and for the plastic back box, just swap the lock ring over for one of these and just attach another flylead.
https://www.NoLinkingToThis/p/earth..._WtAJX7X4y5YWR-XzRkaApI9EALw_wcB&gclsrc=aw.ds

Should take you around 10-15 mins.

Yes, i have been thinking about this, and i guess it does just about meet regulations maybe? Obviously it is relying on the bare minimum though.
 
I'm surprised that something like that would have got passed initial verification on something only two years old.
I suspect that for some, initial verification consists of checking the contents of the brown envelope. OK, that's a bit harsh - checking that whoever does it can fill in the paperwork well enough not to arouse suspicion.

FWIW, a few years ago my mother was looking at a new build. I was primed to pick up on the electrics and call the contractor out for fraud, and their scam for being useless. Some of the failings were "sort of understandable" (such as the cables in the kitchen not in a safe zone, because they'd left extra length for after the units were fitted, but the socket ended up several feet to one side), but others weren't (such as meter tails buried in the plaster and not RCD protected). Thankfully my mother decided that it wasn't going to be the right property for her. Nothing was "good" about that house - the electrics were "minimal", the plumbing was 'kin sh**e, it was designed to give her cold feet (solid concrete slab, insulated but not heated), and pretty well everything was "minimum the BRs allowed".
As it is, I'd already phoned the insurance company that was going to be providing the 10 year builders insurance and told them I had reservations about the stairs - 1/4" sag in some treads even after having been bodged underneath with random bits of timber ! I didn't think it a good idea leaving something that might mean ripping out the stairs and re-doiong them, along with all the re-decorating, till after she'd be moving in. Clearly my reservations were correct, it happened that shortly after that, my mother went to tell him she was pulling out (the house was supposed to have been ready at least a year earlier and still wasn't), and she called me to say that the vendor was in tears and saying that I'd caused him a lot of trouble.

And then there was a program on telly a year or two ago that looked at problems with some new builds. Examples included some built by one of the big outfits, who self-certify for BRs, and which had faults such as insulation still being in it's rolled up and bagged state just left in the loft - the builder had to take roofs off to fix that (sloping ceilings).

So no, never assume that because it's new and "signed off" that it isn't a load of sh**e - because some of it is a load of sh**e.
What would generally be the correct way to make sure the opening where the wire from the wall goes into the back of the socket?
And no-one's commented on the other fail there - it doesn't look like the cable has any protection as it passes through the cavity.
 

Reply to First little job on own house - advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
903
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
344
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
445
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
527
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top