Search the forum,

Discuss Flat twin cable with sheathed CPC. in the Electrical Tools and Products area at ElectriciansForums.net

Marvo

-
Staff member
Mod
Mentor
Esteemed
Supporter
Reaction score
10,306
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding conductors and you never see it done. We just install and arrange wiring in enclosures or DB's in such a way that there's no realistic chance of the uninsulated earth wires contacting live components or terminations. To be honest I can't ever recall seeing a fault due to an uninsulated earth having strayed into contact with a live or neutral. The closest thing I have seen is screw damage to wiring or flash damage due to an installer causing accidental contact between a live and chassis ground whilst working live but I'm a firm believer there's no tablet that cures stupid and no amount of insulating things would ever stop that happening.

When was the requirement for sleeved CPC's introduced in the UK? Was there a particular event or accident that prompted the rule or was it just decided it would be a good thing to do? Do you think the rule makes an important contribution to safety or it's just something that had good intentions behind it but actually makes no difference and just adds time and ballache to an installation?
 
AFIK the requirement to sleeve the CPC here goes back to before the 1970s, but I don't have copies of older regs to know when that became the norm.

While the UK T&E style of cable has bare CPC that is typically smaller than the live (but still to meet adiabatic) and expectation of adding some sleeving where stripped for use, in the ROI they have the CPC that is sleeved and I think follows the EU norm of same size as live.

The USA seems to have unsleeved CPC cable (Romex?) similar to the UK and I have never seen sleeving used, even though a lot of their sockets have far more exposed live connections behind the faceplate!
 
Last edited:
The reg requiring sleeving at terminations etc. is in the 1976 edition, but not in the 1966 edition, so was introduced some time in between. I do come across the occasional fault caused by bare CPC to live part, that could have been avoided by use of sleeving, but not often
 
From the info I saw they said it will be the same price as the uninsulated version..... but don't quote me on that.
 
I also heard that it's for helping with identification of the CPC but I think no matter how bad someone's eyesight or how colourblind they may be you couldn't mistake a bare CPC or bonding wire for anything other than what it is.
 
Would probably buy this depending on price. Can get quite annoying trying to put 3mm sleeving on long lengths of stripped earth when making off a 24TP distribution board

6193B (I'm assuming you need LSF) has been available for years. While it doesn't meet any British Standard, I can think of nothing that prohibits its use.

Other cable types are also available with insulated CPC and are widely used in 3ph installations. I do occasionally come across T&E in 3ph boards, but it's a very rare occurrence.
 
I also heard that it's for helping with identification of the CPC but I think no matter how bad someone's eyesight or how colourblind they may be you couldn't mistake a bare CPC or bonding wire for anything other than what it is.

Unlikely cost would be the same considering additional material required in manufacture and that's excluding tooling costs.

6193Y/B used in southern Ireland has CPC sized the same as L&N, which obviously make it quite a bit more expensive.
 
The CPC remains a size smaller than the line conductors although sufficient to fulfil rfequirements of the adibiatic formula and the thin sheath on the CPC doesn't qualify as 'insulation' ie it doesn't carry a 1kv IR spec, it's just a thin sheath designed to prevent accidental contact. The outer cable dimensions will remain unchanged so all stripping tools, glands, fastnenings etc will still work.

They're also making the 3-core and earth version as well which I assume you use mainly for 2-way lighting arrangement cabling.
 
I do occasionally come across T&E in 3ph boards, but it's a very rare occurrence.
I've come across loads of it, mostly for additional circuits to existing DB's, not nice.
I'm not totally against it in some cases. LSF T+E feeding single phase equipment in commercial kitchens, for example. Can be a basic, quick way of wiring through metal trunking and flexible conduit, in some situations.
Better than SY...


'Pie eater' territory
photo 6.JPG
 
Last edited:
I thought the sleaving was for identification as much as insulation. You definatly used to get green sleaving before the green/yellow came in. I think that was about 68.
Interestingly, the reg in the '76 edition specifically mentions the word 'insulating', but doesn't mention the colour green. What I take from it is, that its primary purpose was to insulate, and green was used because any other colour would be inappropriate for an earth-continuity conductor (as it was known as back then)
 
Interestingly, the reg in the '76 edition specifically mentions the word 'insulating', but doesn't mention the colour green. What I take from it is, that its primary purpose was to insulate, and green was used because any other colour would be inappropriate for an earth-continuity conductor (as it was known as back then)
Yes it had to be insulating as opposed to conductive but it wasn't there as an insulator.
 
I was an apprentice in 76 and cant remember what colour the sleaving was, I think it was green/yellow but always referred to as green sleaving.
 
Yes it had to be insulating as opposed to conductive but it wasn't there as an insulator.
Here is the regulation:

D29 (ii)
Where the sheath of earth-continuity conductors complying with reg D28(i) is removed adjacent to joints and terminations, earth continuity conductors of CSA up to and including 6mm2 shall be protected by insulating sleeving complying with bs2848.

D28(i) refers to CPCs within cables (not flex).

Make of it what you will, but to me its main purpose is as an insulator.
 
6193B (I'm assuming you need LSF) has been available for years. While it doesn't meet any British Standard, I can think of nothing that prohibits its use.

Other cable types are also available with insulated CPC and are widely used in 3ph installations. I do occasionally come across T&E in 3ph boards, but it's a very rare occurrence.

What are the alternatives with the sheathed earth?
 

Reply to Flat twin cable with sheathed CPC. in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
688
Correctly closing off a dead twin and earth cable in a loft. My old house used to have radial circuits serving night storage heaters. Those...
Replies
4
Views
2K
Good afternoon, I purchased a 25mtr coil of PRYSMIAN 6242Y 2022 GREY 2.5MM² TWIN & EARTH CABLE in Screwfix at the start of July and found while...
Replies
14
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top