92
hello guys

I have a lighting install at high level outside a house.
I don’t need additional mechanical protection and would like to use a good UV resistant insulated and sheathed cable.
Don’t want to use conduit as it looks ugly.

I normally used white FP 200 which the manufacturers said supports UV light exposure however I have seen a few installs where after 6 years turns to dust.

(I might be getting a phone in from client is a few years time as a result)
 
Nearly all black cable has good uv resistance.
The black is normally created with carbon dust in pellet form as the material is being processed.

Obviously check with the cable spec but black anything is nearly always considerably better uv resistance than the same white cable.
 
I tend to use standard black flex for domestic lighting circuits outside if the installation method allows it.
 

Reply to Good cable to use outside in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In preparation for an EVSE installation, I am running the supply cable from the main CU, via catenary, to a new CU in my garage. The cable is 6mm...
Replies
4
Views
217
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
993
Hi, folks.' I have a carrier 38MGRQ48E '5 zone' mini split system with 4 'heads'/evaporators installed, and one 'channel' still open. Had it...
Replies
0
Views
723

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top