Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen.

I was originally planning on having my washing machine 9.1A, tumble dryer 6.5A, dish washer 8.5A on there own radial circuit. Total current 24.1A, protected by a 25A circuit breaker, on a radial circuit. Then i thought about having them all controlled by grid switches.

This is the part i require feedback.

For wiring them up, is it perfectly acceptable to have them wired up as a radial through the grid switches protected by a 25A breaker. I am aware that the grid switches are only rated at 20A. Which is why i'm wondering if i would be better to split them onto two circuits and i could also fit my cooker hood into a grid switch that would be fused.

Although ive seen videos on youtube of a 4mm cable being split over two grid switches and on the supply side having 2.5mm cable, is this acceptable?
 
24A on a 2.5mm cable is pushing its current capacity which can be a lot lower depending on its installation method. (Through insulation for example)

A separate 16A, 2.5mm radial circuit for the washing machine and dishwasher… as both are over 2kW (or very near it)
Another radial for dryer and hood.

The 20A rating of the switch is only for the individual load connected to each switch. Your maximum is 9.1 so that’s ok.


Grid switches can get tight to work on. Give yourself a 47mm back box for a little extra room.

4mm in a gridswitch would be very hard to work on… trying to get 2 into a terminal.
 
If you want a single radial circuit in 4mm then you might be better to have some 5-way Wagos in the grid box for 3 * 2.5mm out to each switch.

2.5mm for the appliances is OK as they should have 13A fuses anyway so you can't overload the cable, and 25A the RCBO (or MCB+RCD) gives adequate fault protection prior to the socket outlet.
 
24A on a 2.5mm cable is pushing its current capacity which can be a lot lower depending on its installation method. (Through insulation for example)

A separate 16A, 2.5mm radial circuit for the washing machine and dishwasher… as both are over 2kW (or very near it)
Another radial for dryer and hood.

The 20A rating of the switch is only for the individual load connected to each switch. Your maximum is 9.1 so that’s ok.


Grid switches can get tight to work on. Give yourself a 47mm back box for a little extra room.

4mm in a gridswitch would be very hard to work on… trying to get 2 into a terminal.
Thanks for sharing your knowledge mate. If i were to have multiple circuits inside the grid switch station, is this acceptable, i would think so as its an isolation point but just curious.
 
Having multiple circuits in the grid switch should be fine, but I personally would label it inside to that effect. just in case some DIY person in the future fails to realise it.

In the UK with our 13A sockets (or FCU) we have the luxury of allowing any reasonable size current limit to that point as the fuse takes over when it comes to the appliance protection. That is why we can have 32A ring finals or radials, where as EU is limited to what is safe for the appliance flex, etc.

So in places like France they would insist on 3 * 16A radials for this, and there is a logic to it, but it means more RCBOs (they also have much larger CUs and, more importantly, regulations on the space around them!)

You could do the same, but on the assumption they are DP switches you don't need to as if one is faulty (even N-E fault tripping RCD side) you can easily find out with the use of the switches. So you can put in 25A or 32A.

Now if you want to avoid buying both 4mm and 2.5mm (which you might have) you could put in 2*2.5mm to the grid switch and treats it like a ring. Simply paralleling them to some 5-way Wagos (then 3 *2.5mm out) is also an option and perfectly good, but if you want to terminate on just the grid switch terminals doing that means 2 wires at each switch.
 
Look for the deepest back box you can fit in.

A few places sell T&E in short-ish lengths, some by the metre, so you can get what you need without masses of cable left over.
 
I often fit grid switches on site supplied via a ring final with loads to various appliances- cooker hood, washing machine , dishwasher, fridge freezer.
2x 2.5mm for ring and 4x2.5mm to each appliance in a 35mm back box no problem.
 

Reply to Grid Switches radial wiring acceptable or not? in the Electrical Tools and Products area at ElectriciansForums.net

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock