HELP! commercial socket with type D rated fuse

Discuss HELP! commercial socket with type D rated fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi guys,

Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however stated the company fitting the machine has required a type D breaker, the whole board is RCBOs and the company 'Fusebox' is what I fitted the board with but they don't do type D. I know if I put in a MCB of another brand then it will be a C3 or C2 depending on who you are however I don't see an alternative other than to fit another small CU, but would that be tripping the RCD as its only rated 40A and these type D go 10 to 20 times the amps on start up? Also would I need to run this in some type of SWA or SY cable for the jump in Amps or would normal 2.5 T + E Suffice? I'm generally just Domestic so any help would greatly.be appreciated
 
You are where you are with this and while fusebox might not be the ideal choice for a commercial application, I'm not sure why you wouldn't split the incoming tails to fit another small, suitable board?

I'm guessing the RCD rated at 40A isn't fitted upfront?

Edit: just read op again and see that you've fitted a full rcbo board. Where exactly is the 40A rcd?
 
You are where you are with this and while fusebox might not be the ideal choice for a commercial application, I'm not sure why you wouldn't split the incoming tails to fit another small, suitable board?

I'm guessing the RCD rated at 40A isn't fitted upfront?

Edit: just read op again and see that you've fitted a full rcbo board. Where exactly is the 40A rcd?
I believe the maximum size of device for these boards is 40A, he is considering this to supply another board. I agree though never fit a CU considered domestic in a commercial setting.
 
You will be hard pressed to find anyone who makes D-curve RCBOs, realistically your best bet is a 16A D MCB and then an RCD in either a separate enclosure, or if plenty of spare ways in the CU, it can go in there.

You only need the RCD's current rating to exceed that of the MCB's thermal trip (i.e. 16A here). Under hard fault conditions the RCD typically can break 1-1.5kA so you also need the MCB to be breaking before that point on the magnetic trip (which is almost always the case as 50A * 20 = 1kA, 63A * 20 = 1.26kA)

Same for the cable, it need only be rated for the MCB's rating (i.e. 16A under installed method). With a RCD you have very little to worry about in terms of Zs for disconnection.
 
I would add though that the I2t let-though of a D-curve MCB might be a bit high for something as weedy as 1.5mm T&E (1mm CPC) which meets 16A usually. So you might want to use at least 2.5mm T&E (1.5mm CPC) or look at something with 2.5mm CPC as well, for example NYY-J

Edit: Also note many places will sell you NYY-J by the metre which keeps cost down if you know what you need. And a little extra, the one thing more expensive than buying too much cable is buying too little!
 
Last edited:
the whole board is RCBOs and the company 'Fusebox' is what I fitted the board with but they don't do type D.

I wasn't aware fusebox made any devices suitable for commercial installations, are you sure this is a suitable unit?
I know if I put in a MCB of another brand then it will be a C3 or C2 depending on who you are

It doesn't matter who you are it will not be a C3 or a C2, it will be a non-compliant installation.
The C codes are only used for reporting on an existing installation on an EICR. They are not applicable to new works as new work should fully comply with the regulations (subject to any justifiable departures, which this would not be)
 
Bad news, Fusebox don't make a 16A D-curve MCB.

One option would be to use a Fusebox 32A C-curve RCBO in the main CU and then add a 16A D-curve MCB in a separate DIN box so you avoid the issue of non-matching manufacturers. Not ideal in terms of fault selectivity, but if they are both adjacent to each other and not serving multiple circuits then not too hard to rest both if needed.
 
I believe the maximum size of device for these boards is 40A, he is considering this to supply another board. I agree though never fit a CU considered domestic in a commercial setting.
I too agree but isn't it a bit difficult getting hold of a single phase industrial Con Unit these days, with 10k rated c/b's? Even Schneider are 6k. (and not in the same class as the 10k gear, nor the same price range).
We just used to use metal clad CU's but these days.....
Could get a 3 phase and convert to single but it seems a bit over the top.
Solve the D type problem though.
 
Last edited:
You will be hard pressed to find anyone who makes D-curve RCBOs, realistically your best bet is a 16A D MCB and then an RCD in either a separate enclosure, or if plenty of spare ways in the CU, it can go in there.

You only need the RCD's current rating to exceed that of the MCB's thermal trip (i.e. 16A here). Under hard fault conditions the RCD typically can break 1-1.5kA so you also need the MCB to be breaking before that point on the magnetic trip (which is almost always the case as 50A * 20 = 1kA, 63A * 20 = 1.26kA)

Same for the cable, it need only be rated for the MCB's rating (i.e. 16A under installed method). With a RCD you have very little to worry about in terms of Zs for disconnection.
Many commando sockets have DIN rail for an RCCB (assuming installation method permits of course).
 
Sounds to me that this whole thing needs a rethink and that the results of that thinking is that inappropriate equipment has been used so far and will need replacing. It may also decide that the Zs for a D type radial is un-achievable for standard ADS which may place other considerations on reliance of an RCD for protection.
 
Thanks for everyone's reply, to people/person saying it should be rethought about, it's an office space very very small 40sqm at most! Computers, small kitchen etc. So yes a domestic board was fine it's just that they've decided to put a piece of machinery in after the whole installation that I have no clue about and just been asked by the builder that it needs to be type D 16a with a commando socket. It's very unusual industrial equipment would be put in an office which is why you wouldn't put a industrial board on. But everyone else has been very helpful. I'm still scratching my head through this one. I'm actually going to try a RCBO C CURVE 20A, and see how we get on if needs be then I think I'll go down the route of another board 👍
 
I believe the maximum size of device for these boards is 40A, he is considering this to supply another board. I agree though never fit a CU considered domestic in a commercial setting.
Small office space no more than 40sqm. He has an adjacent unit, other sparks fitted exact same. All it's got is computers, sockets, small kitchen, lights etc. Don't think a commercial board would be necessary do you?
 
I wasn't aware fusebox made any devices suitable for commercial installations, are you sure this is a suitable unit?


It doesn't matter who you are it will not be a C3 or a C2, it will be a non-compliant installation.
The C codes are only used for reporting on an existing installation on an EICR. They are not applicable to new works as new work should fully comply with the regulations (subject to any justifiable departures, which this would not be)
Mate it's a 40 sqm tiny office. Do you really think you need a commercial board In there? Every single other unit has a 4 way board. You could barely swing a cat around in it. It's sockets and lights basically. I didn't know they was putting in a machine at a later date. That was never discussed, just a builder saying it needs this and that as they usually do without knowing its very complicated and that can't be done just like that. But thanks for your help 👍
 
Bad news, Fusebox don't make a 16A D-curve MCB.

One option would be to use a Fusebox 32A C-curve RCBO in the main CU and then add a 16A D-curve MCB in a separate DIN box so you avoid the issue of non-matching manufacturers. Not ideal in terms of fault selectivity, but if they are both adjacent to each other and not serving multiple circuits then not too hard to rest both if needed.
Thanks this has really helped 👍
 
Had a similar problem with some pumps where manufacturer specified D type breakers which for the existing DB were unobtainable so agreed to try C type before upgrading/adding to switchgear. They worked fine without tripping on start so were left in circuit.
You may find C type will satisfy the connected load there without upgrading the installation further?
 

Reply to HELP! commercial socket with type D rated fuse in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock