Currently reading:
Is 4mm heat resistant cable okay for 7.5kw range cooker?

Discuss Is 4mm heat resistant cable okay for 7.5kw range cooker? in the UK Electrical Forum area at ElectriciansForums.net

chris140

DIY
Reaction score
10
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind the cooker. He put this size in as I didn't know what size cooker I was going to be getting.

I ended up getting a 7.4kw range cooker and the electrician has connected it with 4mm heat resistant cable instead from the cooker to the back plate, instead of 6mm. Is this okay, and is it okay with the 10mm cable and 32a fuse?

Thanks
 
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind the cooker. He put this size in as I didn't know what size cooker I was going to be getting.

I ended up getting a 7.4kw range cooker and the electrician has connected it with 4mm heat resistant cable instead from the cooker to the back plate, instead of 6mm. Is this okay, and is it okay with the 10mm cable and 32a fuse?

Thanks
At least he used heat-resistant cable, most just use twin and earth.
 
Nothing wrong with T&E for the final connection to a cooker, This is fully compliant with BS7671

I'm yet to see T&E showing signs of deterioration behind an oven, but it's not the ideal cable for pushing back behind an appliance. Flex is inclined to drop easily behind a kitchen unit and naturally forms itself into position.
 
I'm yet to see T&E showing signs of deterioration behind an oven, but it's not the ideal cable for pushing back behind an appliance. Flex is inclined to drop easily behind a kitchen unit and naturally forms itself into position.
Loop of string around the cable, down the back to the space underneath and out the vent that should have been cut in the top of the kickboard. Gently pull on the string as you push the oven back into place.
 
4mm is absolutely fine, some like to use H07 some t&e. MF instructions have the last word.
Thanks very much for replying, been really worried about using cooker as I will be doing baking using both ovens and then may have to put something under the grill for my sons dinner at the same time, so cooker could often be running at full power, that's what I bought that model for.
 
cooker should not pull more than 32A
cable if it is H07RN-F as below is good for 35A
however as said before, it will not draw 32A in use for long, even if you have everything turned on.
Nothing to worry about.
1713549180960.png
 

Reply to Is 4mm heat resistant cable okay for 7.5kw range cooker? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock