Search the forum,

Discuss Is this TN-C-S or TN-C, also earth bonding size. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes back up to connect to the outer sheath.
IMG_20231004_191431.jpg


The bonding looks like 6mm^2. And the connection point looks like that's the max it will take. As I understand it, TN-C-S needs 10mm^2 so TN-S?
 
It's impossible to tell from looking at it.

It would have originally been TNS and the original cutout has been replaced with that one.
But those cutouts have a removable N-E link, so it could still be TNS if the link has been removed or it may have been left in place to convert it to TNCS.
 
Thanks, though not the answer i wanted :(

I had a man out to change the meter, should have asked him. If the DNO fuse was 1/4" to the right, he could have changed it. Got to sort out the door for clearance.

There are two issues here. First I need another bond to the gas. From the CU? Or split the CU wire and a terminal block for the additional gas bond. Then we have the size issue. My house is in the process of being renovated, so now would be a good time to pull a wire.

It's an Earth Loop Impedance Tester that'll allow me to measure and find out? Ze reading or or something can be used to work out what I have.

I want to update the CU to 18th with RCBOs at some point so hoped I could sort bonding first.
 

Reply to Is this TN-C-S or TN-C, also earth bonding size. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock