Hey,

I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet.

When re-fitting them I noticed one was a very tight fit (3 cables stuffed in to a shallow 25mm knock box. End of the ring and an extra socket coming off it?). I was a bit wary pushing it in thinking it might damage/loosen a wire but went ahead as it’d been in there previously. Then I switched the ring back on at the consumer unit.
All seemed fine but I noticed every ten or fifteen mins my lights (separate circuit) were dimming temporarily for a split second.
The problem persists even when all sockets are empty and individually turned off at the sockets. The problem only stops when the ring is off at the consumer unit (all RCBOs).

I then pulled the sockets again to check the wiring was all okay and whilst I was at it I chiselled out some more brick to fit a deeper knock box. I also stripped the wires back so they were fresh. This didn’t resolve.

I’ve been round and checked every socket on that ring to make sure all connections are tight and they’re all fine.

I also removed those sockets from the ring and completed it with wagos temporarily to eliminate the prospect of faulty sockets.

Anyway, I’ve got the ring off at the consumer unit now and an electrician potentially coming over the weekend to investigate.

I’m just curious if anybody has any idea what the fault is likely to be. Nothing is tripping at the consumer unit.

I wonder if I’ve damaged a neutral wire further up the cable by stuffing it in to such a shallow knock box.
 
possibly the lighting feed goes up with the socket cables and you have disturbed it, could be a long standing Almost a fault ith the cable/s ad the disturbance has brought it to light. forgive the pun.
 
possibly the lighting feed goes up with the socket cables and you have disturbed it, could be a long standing Almost a fault ith the cable/s ad the disturbance has brought it to light. forgive the pun.

Hey I did think this could be the case but then I can’t figure out why the issue would stop when the ring is off at the consumer unit.
 
I think this is going to need an electrician and test equipment unfortunately.
 
So the only thing you did was unscrew the sockets from the backplates?

Are these backboxes galvanized?
Do they have a rubber grommet where the cable passes through?

If so are these backboxes bonded to the sockets you removed?

A photo might help...
 

Reply to Issue with lighting after lifting sockets to paint in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
692
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
897
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
955
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
783
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top