joining 16mm T&E

Discuss joining 16mm T&E in the Australia area at ElectriciansForums.net

B

BristolSpark

Any ideas on joining a 16mm T&E.

Its fed from a main switch up into a flat. Its mechanical sound just to short to reach new board. it needs to be joined under the floor.

But we are lost on best practice for this.
 
Would a 60A junction box help you? What's the rating of the cables protective device?

click-60a-3-terminal-box-junction-box_549_1_medium.jpg
 
This supply will pop out of the floor by about 6- 8inchs max. so we could put a small enclosure then JB it. Then ininstall the new board. We have not had proper chance to view the switch, from the height we are at we assume at present 63A supply.

Running a new cable was original thought thought, but due to location and being a third floor flat, access is rather bad, the route is not easy.
 
If you've got 6-8 inch to play with and seen as the 16mm t+e is for your main incomer, just wall mount henly tail connectors and run your tails from them to the new board. This way you comply with 543.3.3 for testing as Murdoch pointed out.

images-246.jpg
 
use 16mm cable link, clamp properly and wrap with PVC tape

Welcome to the forum.

Unfortunately the member in question hasn't been active in some time and this discussion dates back to 2011. In the UK we have a few options for joining cables of this type and size, but wrapping with PVC tape would not be permitted as a suitable means of insulation and protection.
 

Reply to joining 16mm T&E in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock