Hi All

Whilst carrying out some testing today I had the following messages on my Kewtech KT64DL.

L - N >20ohms - this was on the ring on only one socket, all others tested fine. Could this be a faulty socket?
n-pe hiv - this was on the upstairs lighting circuit. Was testing in the loft where I assume the furthest point would be. I got this message so tried at another light on the first floor and it tested fine. I assume this is an issue with a part of the circuit. I believe the issue is a high voltage between N - CPC. I was getting 137V when a tested N - CPC. All the lights on the circuit were working fine.

Can anyone shed some light on what might be the cause of the above.

Tom
 
Hi All

Whilst carrying out some testing today I had the following messages on my Kewtech KT64DL.

L - N >20ohms - this was on the ring on only one socket, all others tested fine. Could this be a faulty socket?
n-pe hiv - this was on the upstairs lighting circuit. Was testing in the loft where I assume the furthest point would be. I got this message so tried at another light on the first floor and it tested fine. I assume this is an issue with a part of the circuit. I believe the issue is a high voltage between N - CPC. I was getting 137V when a tested N - CPC. All the lights on the circuit were working fine.

Can anyone shed some light on what might be the cause of the above.

Tom
Were these both Zs tests, on circuits that have RCD protection. They both seem linked to Kewtech's ATT (Anti Trip technology)

The first one could well be a faulty socket, in which case testing at the terminals to the back of the socket should show that.

The second might be an issue with Neutral to Earth low resistance, in which case the IR test on that circuit should pick it up. Are you sure you had Line and Neutral correctly connected, or that it wasn't reversed at that fitting?
 
What results did you get from dead testing on the lighting circuit? Sounds like you’ve got a broken earth (CPC) somewhere. Time to get the wander lead out, or R1R2 the circuit and see what you find.

WRT the high Zs on the socket, it’s more than likely the socket and needs replacement, can test as has been mentioned above.
 

Reply to Loop testing question in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock