Discuss Overhead 240V Supply - How is Earthing Provided? in the DIY Electrical Advice area at ElectriciansForums.net

aesmith

-
DIY
Reaction score
25
Hi,
Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself".

My late parent's house is supplied by overhead 240V, and I was puzzling over how earthing is provided. As far as I can see following cables it goes ..
  • Two overhead cables to the house
  • Single cable down to meter cabinet (I assume SWA or concentric)
  • Meter cabinet hold main fuse, from which there are L and N meter tails, and an Earth cable

As far as I can see that Earth is the only provision, for example I can't see any sign of an Earth rod.

How is Earth normally provided in these cases?

Thanks, TS
 
The Earth is actually the Neutral. Inside the block of the main fuse is a link.
 
Cheers. Naturally I'm not going look in there, I'll take your word for it. So the earth is actually provided overhead. I did wonder, but then thought that wouldn't be safe, for example if the overhead N failed there'd be no earth. Or maybe far fetched, but if the overhead L came in contact with N.
 
This kind of supply is known as TNC-S Earth (Terra) and neutral (N) combined (C) up to the consumer's supply, and then separate
(S).
You are correct that there is potential danger if the supply neutral fails, and there are regs applicable to TNC-S systems to alleviate that danger.
If overhead live and neutral touch, there's usually a big spark, and a bang somewhere, after which everything is safe because it's not live any more.
 
It is also worth noting that the overhead N will be connected to earth rods at more than one point so Is less likely to fail and become Live.
 

Reply to Overhead 240V Supply - How is Earthing Provided? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
347
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
891
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock