Search the forum,

Discuss Question help needed - C&G 2391 - 52 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
3
Hi - Just joined the forum as I'm making a career change and am training up.

I've come across some mock papers online and am concerned that either I'm way off or they're wrong, so would love some input. (Exams here)

Given that the resistance per metre of 2.5mm² cable is 7.41mΩ/m at 20°C , what would the approximate R1+R2 reading be at the at the extreme end of a 25m long 20A radial socket outlet circuit?

Possibile answers are

  • 0.27
  • 0.37
  • .074
  • 0.17

I came out with 0.37 using BS7671 and GN3 but the exam confirmed .17 as the answer. Could anyone take a look and tell me what I'm missing/where to find the missing info in either book? Thanks!
 
You would get 0.37 if the line and CPC were both 2.5mm

Are they referring to 2.5mm T&E where CPC is smaller?

Edit, beaten to it by Westie!
And also corrected my own mistake!
 
Last edited:
I concur with you. It is a badly written question but we must assume the cpc is also 2.5, it normally states this. Not sure where they got 0.17.
Thanks for taking the time! It's really disconcerting when I'm trying to revise and the certainties are wrong!

The following question tried to state that polarity is to ensure that "The resistance is low enough to operate the protective device within the specified time"... Not sure how much I should trust this place.
 
Thanks for taking the time! It's really disconcerting when I'm trying to revise and the certainties are wrong!

The following question tried to state that polarity is to ensure that "The resistance is low enough to operate the protective device within the specified time"... Not sure how much I should trust this place.

It's amazing how many bad questions there are out there. Lots badly worded or vague, but some that are just plain wrong unfortunately.
 

Reply to Question help needed - C&G 2391 - 52 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi, I have my 2391-52 coming up. Does anybody have the answer sheet to the mock paper on the C&G website? Exam is ‘1.5 June 2022’. Also if...
Replies
0
Views
2K
Hi, has anyone completed the CG 2391-52 inspection & testing course online with LearnZone Media recently? Just looking for opinions or feedback...
Replies
1
Views
2K
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
949
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hi everyone, Question about 2391-52 (initial verification and periodic testing) A brief background to my situation; I do some in-house wiring...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock