Discuss Random Voltage Drop from 236v to 120v in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
BIG place OK lots of electrical bits.
but one on a 3 phase Radial is tripping its RCCB
so i check the wiring making sure its tight and it has continuity
even trust the RCCB that it trips. All ok

but i noticed on phase for a short while it dropped to 120v on my meter.. just Random comes and goes.
as soon as it was back to 236v i did a RCD test on it and ok

any thing on that Phase could be drawing it down to that voltage, and because its getting dropped to that, i guess any singal phase motor on that phase would slow down a lot and any three phase motors would poop themselfs!

how do you track down what is doing this and note it is Random.
i am wondering about Electric Fork trucks being put on Charge
 
You’ve two contenders : either a large load kicking in and out but long enough for your meter to resolve - or - a cable fault (and I’d be looking at the neutral).
 
imageedit_1_9119440627.jpg

I've never come across some thing that does this before. I don't have much concept of time so it felt like a minute it was on 120v (and that was with the machine not doing any thing and hooked up), why I think some thing else on the phase is doing it (why isn't any thing else tripping over this)
 
View attachment 115955
I've never come across some thing that does this before. I don't have much concept of time so it felt like a minute it was on 120v (and that was with the machine not doing any thing and hooked up), why I think some thing else on the phase is doing it (why isn't any thing else tripping over this)
What's the earthing system?
 
If your meter is measuring line to earth voltage it is likely to be an earth continuity fault which would have no effect on any equipment. A line drop to 120v is likely to have a significant affect.
 
If your meter is measuring line to earth voltage it is likely to be an earth continuity fault which would have no effect on any equipment. A line drop to 120v is likely to have a significant affect.
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a genuine drop on the L.
 

Reply to Random Voltage Drop from 236v to 120v in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
837
Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
934
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock