Discuss RCBO Testing in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB recorded a value of >300ms (test probes connected N&L load side, and E bar), yet when running the same test at a socket-outlet of the same RCBO tripped at <40ms?
 
Make of rcbo? Some (MEM?) were known to not trip when testing at their output terminals but attach even a modest length of conductor and test from that and they behaved.
 
Thanks all for responding to my message.

Make of rcbo? Some (MEM?) were known to not trip when testing at their output terminals but attach even a modest length of conductor and test from that and they behaved.

I can confirm that it was an Eaton RCBO/MEM TP-DB. Out of interest, are there other brands of RCBO that this occurrence is common? - or is Eaton/MEM particularly renowned for not tripping when under test at the breaker?

Grime on the terminal screws not making a good connection?

Fault with the proketbe lead, but not the lead with plug fitted?

Connections looked good to me. Test probes could be a consideration, I have subsequently ordered a new set to err on the side of caution. There were a number of RCBOs within the same DB that were giving me the same >300ms recording when under test at the DB, and a result of <40ms when using the MFT socket adapter on the respective circuit.
 
or is Eaton/MEM particularly renowned for not tripping when under test at the breaker?

It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO does not see the test current.
If you insert the probe where the conductor would normally be it will trip as expected.
 

Reply to RCBO Testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
418
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
762
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
668
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock