An RCD keeps tripping.


Please see attached photo of the board (2 photos attached). I’ll call the breakers:

MCB (1) marked ‘Upstairs lighting’
MCB (2) marked ‘Sockets’
MCB (3) marked ‘Water heater’
MCB (4) marked ‘Sockets’
RCD (5) for MCBs (1-4)
MCB (6) marked ‘Kitchen sockets’
MCB (7) marked ‘Downstairs lighting’
MCB (8) marked ‘Garage’
MCB (9) marked ‘Cooker’
RCD (10) for MCBs (6-9)

No appliances are plugged in to any sockets and all sockets are turned off.

Turning on MCB (4) trips RCD (5) every time.

It is possible to have all MCBs other than (4) on and not trip RCD (5). However, it will trip eventually, around every 30 mins.

Even with all of MCBs (1-4) off, RCD (5) occasionally trips.

Kitchen sockets are on a different circuit MCB (6) and RCD (10). Using high powered appliances in the kitchen (e.g. kettle) will also trip RCD (5). However, the appliance, MCBs (6-9) and RCD (10) all stay on.

RCD (5) is not faulty: it has been replaced.

I can’t use a socket tester other than in the kitchen as as turning on MCB (4) will trip RCD (5).

Any ideas much appreciated.

Tom
 

Attachments

  • 84375CB6-0D19-4F9F-87F0-AFECBA9A5DF0.JPG
    335.6 KB · Views: 30
  • IMG_6394-converted.jpg
    266.4 KB · Views: 31
Why on earth did you shoehorn a BG RCD into a Wylex board?
There’s a fault, the RCD is telling you that. It’s not the RCD. Put the right one back.

You need an Insulation Resistance tester and someone who knows how to use it.
A competent electrician is your best bet.

Just changing things isn’t gonna fix anything. Sorry.
 
Turning on MCB (4) trips RCD (5) every time.
Kitchen sockets are on a different circuit MCB (6) and RCD (10). Using high powered appliances in the kitchen (e.g. kettle) will also trip RCD (5)
These two together suggest a rather complicated specific fault scenario (a large load driving current through a fault on a different circuit).
As already said, there is no hope of finding this fault without testing every circuit with specialised (expensive) gear that only electricians are likely to have.
It won't take long for an electrician to do this (usually around an hour).
I normally tell people that if the fault is persistent I can usually find the reason within two hours. (Intermittent faults are a different kettle of fish but this doesn't sound like that)
 
It has all the hallmarks of a N-E fault somewhere, but finding it needs a systematic approach and the correct test gear (insulation tester) to disconnect each circuit in turn and check for a fault, then when you identified the circuit(s) with a fault, to further divide-and-conquer it until the fault location (cable, accessory, junction box, etc) has been located.
 
These two together suggest a rather complicated specific fault scenario (a large load driving current through a fault on a different circuit).
As already said, there is no hope of finding this fault without testing every circuit with specialised (expensive) gear that only electricians are likely to have.
It won't take long for an electrician to do this (usually around an hour).
I normally tell people that if the fault is persistent I can usually find the reason within two hours. (Intermittent faults are a different kettle of fish but this doesn't sound like that)
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
 

Reply to RCD tripping. Not appliance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This for an apprentice 32 amp mcb /63amp RCD 1) no power to the sockets 2) installation resistance all good. 3) contunuty good. 4) no loses...
Replies
13
Views
733
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
636
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
623
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
404
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top