- Reaction score
- 389
During an eicr i have discovered a 30 ma (RCD) Residual Current Device feeding a dual RCD consumer unit. The source rcd trips before either in the Consumer Unit .
i would remove the source rcd or replace with a type s but i cant be certain about buried cables in walls, at least some of it is in trunking.
anyone have any ideas?
i would remove the source rcd or replace with a type s but i cant be certain about buried cables in walls, at least some of it is in trunking.
anyone have any ideas?