Discuss RV Park branch circuit feeder size in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I am working on a RV Park and I have a question.

I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and downsizing the wire to 2/0 Quadraplex AL URD cable for the last 4 pedestals. I have calculated voltage drop and everything is below 4%. Table 310.16 says 4/0 AL @75d is only good for 180 amps. But I also found a loophole in annex B table B.2.9 for triplex direct burial cable underground cable. My question is based on this table is the 4/0 AL URD cable sufficient to supply the 10 sites?

Calculated load and VD is attached.
 

Attachments

  • Screenshot 2024-02-26 110609.png
    16.2 KB · Views: 13

Reply to RV Park branch circuit feeder size in the UK Electrical Forum area at ElectriciansForums.net