I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be used to aid with selectivity and avoid potential nuisance tripping, providing the ratio of the rated residual operating current of the upstream S-Type RCD to that of the downstream RCD is at least 3:1. This said I have recently seen a setup where there's been a 30mA RCD within a lodge CU, with a 30mA C32 RCBO at the supply side DB - external to the lodge. When the RCD within the lodge is under test it would almost inevitably cause the 32A RCBO upstream to trip. Is this situation one where an S-Type RCD, or 100mA RCBO, would be better suited in the DB?
 
If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing additional protection. This is because S type RCDs introduce a time delay to help achieve selectivity, which makes it too slow to meet the requirements for additional protection.
 

Reply to S-Type RCD Selection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top