C

claret73

This may be quite hypothetical for now, but can I take a feed out of the incoming side of an FCU (If it was either a radial or Ring Final) to feed a 2nd FCU which would provide a load out to a boiler?

Spoke to the plumber asking if he has power next to the boiler and mentioned the spur. If it's off the Ring originally then I assume no difference to spurring off a Socket outlet?...Good or Bad Practice? Not looked at it yet, just trying to pre-empt anything.
Thanks!
 
You can spur off a FCU as long as its on the ring, or radial circuit.

You can't spur off a spur (even if its 2 FCU's protecting 2 cicuits of, say 3A each) - which IMHO is silly as you can spur off a socket to a double socket and plug in 2 3KW heaters!
 
You can only have one spur from a point on a Ring or Radial (socket, JB or FCU) - If fused you can have as many outlets as you want - so only 13A.no matter how many you fit on it.

So two FCUs from the same point would not comply.

If on a Radial and same csa it wouldn't be a spur.
 
Last edited by a moderator:
Off the incoming side, no. Only one spur allowed. From the outbound side (protected by the fuse) then fine.

I disagree. The load side of an FCU is fused so spurring off the supply side is no different to spurring off a socket as long as the FCU is connected directly to the ring.
 
Last edited by a moderator:
Maybe, but if there were two spurs that would be 39A.<br>
<br>
I'm afraid there's no argument on this one.

Where did you get 39A from???

You have one FCU connected directly to the ring like a socket-outlet would be. This is not the spur, the cable running off the fused LOAD side of it (which is no different to the flex of something plugged into a socket-outlet) is the spur.

Then, just like you would spur off a socket-outlet you run a spur off the SUPPLY side of the FCU.
 
Didn't mean to start a war Lads! I haven't looked at it yet, but Jud that's what I was thinking initially. If the spur is connected to a ring, then taking off the load is only a spur off that like a socket. I guess I'd need to test to see that there aren't already Spurs in existence (which might be highly unlikely...)

GrimySparks, that sounds a useful option. Hopefully I've got this right & maybe is unnecessary?? I could put a new FCU next to the original, Split the legs and bridge between. Both now wired into the ring. Keep the new at 13A & take the load 1x 2.5mm to the 2nd FCU. Then Load out of that to the Boiler. If the original is next to the Boiler in proximity then could just take my flex out of the first FCU & fuse down, marking the FCU as the Boiler.
 
You can spur off a FCU as long as its on the ring, or radial circuit.

You can't spur off a spur (even if its 2 FCU's protecting 2 cicuits of, say 3A each) - which IMHO is silly as you can spur off a socket to a double socket and plug in 2 3KW heaters!

And even worse, the regs allow you to use unfused socket doublers (the small cube things) and essentially double the draw! So this could potentially be 52A/12KW (in practice < 32A or the ring MCB would trip but still more than 2.5mm is allowed) from a double socket off a spur and be compliant but 2 FCUs carrying 26A max is for some reason not ok?
 
Obviously not. Lol


Those cube adapters are always fused… they have to be. If not, then you’re buying unsafe non compliant products.
That's not the case, some are unfused and the regs say only ones with 3 or more sockets need to be fused (unless the regs have changed?)

Here just a couple of examples:
 

Reply to Spuring off a Switched Spur in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock