Search the forum,

Discuss Supply Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable. He wants the DB moved to his garage. It will still supply the two pumps but also a socket circuit in the garage. Having done my cable calcs, 4mm will clearly not be enough as the cable will need to be approximately 10M in length.

I would normally use SWA for this but he is insisting on T&E if possible.

Advice please on what cable to use for this? He wants the smallest size cable and preferably T&E but I'm not sure I can do this as the cable calc I use doesn't account for using T&E for this. Can I use 10mm T&E? How about 6mm? If so, where can I find a decent cable calc and info on this? Thanks
 
What size of protective device is supplying the DB?
Are you completely renewing the supply or just extending it?
 
What size of protective device is supplying the DB?
Are you completely renewing the supply or just extending it?
He wants to see if I can utilise the existing 4mm T&E supply but I'm not really happy with this as my cable calc suggests it's not big enough. He is happy to change the protective device supplying the DB.
 
What is the protective device and the total distance from the supply to the location of where the DB is being moved to.
 
What is the protective device and the total distance from the supply to the location of where the DB is being moved to.
The protective device can be increased in size but currently 40A. The new distance is 10 metres. The sub-DB will supply the air source heat pump, pool pump, garage socket circuit and a lighting circuit.
 
40A is too big for a 4.0 cable so are you replacing the whole run?
I will have to replace the whole run or change the supply protective device. I suggested 10mm T&E as he will have a heat pump, pool pump, socket circuit and lighting. Would that sound reasonable and would T&E be ok? I normally use SWA for this sort of thing.
 
T&E is fine providing it has where necessary suitable protection, it isn't suitable for exposed use outside.
 

Reply to Supply Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
501
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
866
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
712

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top